Topic: NEC Table 310.20

User: curious101, Location: Atlanta, GA, USA

Asked on: Tuesday, August 6, 2024 at 11:31 am EDT
Answered on: Thursday, March 6, 2025 at 12:47 am EST

Question: Hello,Messenger wire is sized per NEC Table 310.20, but a new project is in a jurisdiction where NEC 2011 is adopted. There is no Table 310.20 in NEC 2011. How should the information be referenced?Thanks!

You're right, the NEC numbering changed significantly between the 2011 and more recent editions. Table 310.20 is a relatively new addition.Here's how to approach the situation with NEC 2011, focusing on how to determine the appropriate conductor size for a messenger wire (even though the direct table reference is absent)

Understanding the Function and Requirements of a Messenger Wire

Before diving into the 2011 code, remember the purpose of the messenger wire: Support

It provides structural support for the cable(s) it carries. This is its
primary function.

Grounding (Potentially)

In some cases, it may also serve as an equipment grounding conductor.

NEC 2011 Sections to Consult


Since there is no sizing table like 310.20, you need to derive the requirements from these sections:1. Article 225: Outside Branch Circuits and Feeders

This article governs wiring extending from one building to another or on the exterior of a building. It will likely apply to your situation if the messenger wire is supporting outside wiring. Pay attention to the sections dealing with overhead spans and clearances.2.

Article 396: Messenger Supported Wiring

This section specifically covers wiring supported by messenger wires. It will likely have crucial requirements for you.3.

Article 250: Grounding and Bonding

If the messenger wire is intended to serve as an equipment grounding conductor (EGC), Article 250 is essential.4.

Chapter 9, Table 8

This table provides data on the properties of conductors, including their physical characteristics (e.g., diameter, area, weight). This is useful in calculating the tensile strength and sag of the messenger wire.5.

Article 310: Conductors for General Wiring

While there's no Table 310.20, this article is still relevant because it covers the general requirements for conductors, including ampacity, insulation, and installation methods. You might need to reference ampacity tables if the messenger wire is used as a conductor.

Steps to Determine Messenger Wire Size (Without Table 310.20)
1. Determine the Load (Physical)

Calculate the total weight of the cable(s) the messenger wire will support, including any anticipated ice or wind loading. This is critical. You need to know the forces the messenger wire will experience.2.

Determine if Grounding Function is Required

Is the messenger wire intended to serve as an equipment grounding conductor (EGC)? If so, proceed to step 3a. If not, skip to step 4.3.

Grounding Conductor Size (If Required)



(a) Equipment Grounding Conductor Sizing (Article 250)

Reference Table 250.122 (in NEC 2011) to determine the
minimum size of the equipment grounding conductor based on the rating of the overcurrent protective device protecting the circuit(s) carried by the cable(s) supported by the messenger wire. The EGC must be large enough to handle fault current.

(b) Corrosion Protection

Grounding conductors directly buried or subject to corrosive conditions must be appropriately protected.4.

Mechanical Strength Calculations (Key!)



Tensile Strength

Consult with a qualified engineer or the messenger wire manufacturer to determine the
required tensile strength of the messenger wire. This must be significantly greater than the calculated load (weight of cables, ice, wind) with a suitable safety factor. A common safety factor is 2.0 or higher. The safety factor is the ratio of the breaking strength to the maximum working load.

Sag

Calculate the expected sag of the messenger wire under load. Excessive sag can violate clearance requirements or create other problems. The messenger wire manufacturer should provide data to assist with sag calculations.

Span Length

Consider the distance between support points (the span). Longer spans require stronger messenger wires.5.

Material Considerations



Type of Messenger Wire

Common materials include galvanized steel (various grades), aluminum-clad steel, and alloys. The choice depends on the environment (corrosion resistance) and the required strength.

Hardware

Select appropriate hardware (clamps, insulators, etc.) that are rated for the chosen messenger wire and the anticipated loads.6.

Code Compliance (Article 396)

Ensure that the installation meets all requirements of Article 396 regarding messenger supported wiring. This may include specific requirements for clearances, support spacing, and grounding (if applicable).

Why You Need Expertise


Sizing a messenger wire properly is
not just about picking a wire gauge from a table. It's an engineering calculation that involves: Understanding structural mechanics Knowing the properties of materials Considering environmental factors* Adhering to code requirementsRecommendations1. Consult with a Qualified Engineer

For anything beyond a very simple installation, engage a licensed electrical engineer. They have the expertise to perform the necessary calculations and ensure a safe and code-compliant installation.2.

Manufacturer's Data

Obtain data sheets and application guides from messenger wire manufacturers. They can provide valuable information on wire properties, allowable loads, and installation recommendations.3.

Local Jurisdiction:
Consult with the local electrical inspector. They may have specific requirements or interpretations of the NEC that you need to follow.In summary, while Table 310.20 might be absent in NEC 2011, the underlying principles of safety and mechanical integrity remain. Focus on calculating the loads, selecting the appropriate material, and adhering to the requirements of Articles 225, 250, 310, and 396. Remember that the mechanical strength of the messenger wire, verified by engineering calculations, is paramount. Flag for review