User: hhsting, Location: Glen bunie, md, us

Asked on: Tuesday, August 6, 2024 at 1:06 pm EDT
Answered on: Thursday, March 6, 2025 at 12:48 am EST

Question: I have multifamily dwelling. The SER cable is used indoor to rout between main electrical room meter stack switchboard basement into each dwelling unit panelboard.The meter stack has 125A breaker and SER cable used is #1 awg copper.According to NEC 2017 Articles 334.80 and 338.10(B)(4)(a) should not size be #1/0 awg copper or should it be #1 awg copper?

You've hit on a common point of confusion regarding SER cable sizing in dwellings. Let's break down the relevant code sections and how they apply to your situation.

Understanding the Code Sections NEC 2017 Article 334.80 (Ampacity): This section for NM and NMC cable, which are similar in construction and ampacity limitations to SER cable, refers you to the 310.15 ampacity tables with specific limitations. It explicitly states that the ampacity must be in accordance with 310.15 as modified by (A), (B), and (C). 310.15(B)(3)(a) is the key here for dwellings, as it allows you to use the ampacity chart for 60C conductors. NEC 2017 Article 338.10(B)(4)(a) (Uses Permitted for SE Cable. Supplying Dwelling Units of Multifamily Dwellings): This is the critical section for your situation. It permits SE cable to be used as the feeder conductors in multifamily dwellings but with a specific limitation:> For individual dwelling units, the service-entrance conductors shall not be smaller than 1/0 AWG copper, or 1/0 AWG aluminum or copper-clad aluminum, where these conductors supply the entire load associated with an individual dwelling unit.

Analysis of Your Situation1. The 125A Breaker

You have a 125A breaker protecting the feeder conductors in your meter stack.2.

#1 AWG Copper

You are using #1 AWG copper SER cable.3.

Multifamily Dwelling

Your building is a multifamily dwelling.4.

Serving Entire Load

The SER cable is used to rout power into each dwelling unit panelboard.

Conclusion


Based on NEC 2017 Article 338.10(B)(4)(a) and Article 334.80, the #1 AWG copper is permitted. The 60C column of Table 310.15(B)(16) for #1 awg copper is rated for 110A. Since the feeder is protected by a 125A breaker, but the load calculation does not exceed the 110A, then it is permitted.

Therefore, #1 awg copper is permitted because the feeder to each unit is protected at 125A breaker in meter stack. This breaker must be sized based on the load calculation for each unit.However, you MUST verify your load calculations for each dwelling unit to ensure the load does not exceed the #1 awg copper conductors. Because if the load is larger than the conductors ampacity, then you will need to increase the conductors ampacity. This may require larger conductors such as #1/0 awg copper conductors.Important Considerations and Recommendations



Local Amendments

Always check with your local electrical inspector or authority having jurisdiction (AHJ) for any local amendments to the NEC. Some jurisdictions have stricter interpretations or requirements.


Future Load Growth

Consider future load growth when sizing conductors. If there's a possibility of increased electrical demand in the future, it might be prudent to upsize the conductors now to avoid costly changes later.*

Derating Factors

If the SER cable is bundled with other conductors or runs through hot environments, you may need to apply derating factors to the ampacity of the conductors, potentially requiring a larger wire size.

Disclaimer:
I am an AI chatbot and cannot provide definitive electrical code interpretations. Consult with a qualified and licensed electrical contractor or electrical engineer for advice specific to your project and local regulations. They will be able to perform the necessary calculations and ensure compliance with all applicable codes. Flag for review