Question: Surface mounted and EMT must be used. Would there be any issued dropping doen one 3/4" pipe and nipple between boxes? I think (3) sepaparte conduits doen from ceiling would be foolish. No derating issues. 6 CCC's conductors.
Okay, let's break this down and consider the issues with dropping down a single 3/4" EMT nipple between surface-mounted boxes, especially with 6 current-carrying conductors (CCCs).
Understanding the Situation
You're running EMT conduit and surface-mounted boxes. You want to transition from a run in the ceiling down to a lower box. Instead of running three separate EMT drops for the conductors to the lower box, you're proposing using a single 3/4" EMT nipple.
Considerations and Potential Issues1. Fill Capacity
This is the most critical issue. 3/4" EMT has a very specific fill capacity based on the type and size of the conductors. You must calculate the conduit fill.
How to calculate conduit fill
You need to know the size (AWG) and insulation type of your conductors. Look up the cross-sectional area of each conductor in Chapter 9, Table 5 of the NEC (National Electrical Code). Multiply each conductor type by the number of its type (in your case all the same, that is 6) Then total all conductor cross section areas, compare against Table 4 for EMT for permitted fill
Important
Remember that a nipple is defined as 24" or less of conduit, or the fill requirements differ (43% instead of 40% for more than 2 conductors of the same wire type.)2.
Ease of Installation
Pulling six conductors, even if the conduit is technically legal to fill capacity, through a short nipple can be a royal pain. If the conductors are large gauge, it's even worse. This can lead to damaged conductors which can cause faults and safety issues.3.
Code Compliance (NEC)
This is absolutely paramount. You must comply with the NEC. Improper conduit fill is a code violation and a safety hazard. The NEC will be based upon the edition that the local AHJ is using.4.
Mechanical Protection
Even a short nipple needs to provide adequate mechanical protection for the conductors. Make sure the fittings are properly tightened and that the nipple is securely connected to the boxes.
When this might be acceptable
Small Conductors
If you're using smaller gauge conductors (e.g., 14 AWG or 12 AWG), and your conduit fill calculation is well within the allowable limits for 3/4" EMT, this might be okay.
Short Run
As a short Nipple of 24" or less.
Why running separate conduits might be better, even if it seems "foolish" Easier Pulling
Spreading the conductors across multiple conduits makes the pulling process much easier. Easier pulling means less stress on the conductors, which means less risk of damage.
Better Fill
Even with larger gauge conductors, running smaller conduits in parallel may be easier to fill within the allowable limits.
Future Expansion
If you think there's any chance you might need to add more conductors in the future, having separate conduits provides more flexibility.
Heat Dissipation (though not a factor here)
While you've said there are no derating issues, spreading conductors across multiple conduits can improve heat dissipation in some cases. (Not a factor for you with only 6 CCCs.)
Code Compliance
It can ensure better compliance with code, especially if the single conduit is pushing the fill limits.
Recommendations
Calculate the Conduit Fill
This is non-negotiable. Get the exact conductor size and insulation type. Use the NEC Chapter 9, Table 5 to find the area of the wires and Table 4 to compare the permitted fill2.
Consider Larger Conduit
If the 3/4" EMT is too tight, go up to 1" EMT. A little extra space makes the pull much easier.3.
Seriously Consider Separate Conduits
Even if the 3/4" EMT is technically within the fill limits, ask yourself if it's practical to pull those conductors through that short nipple without damaging them. If not, running separate conduits is the better option. The extra cost of the conduit and fittings is well worth the time and hassle you'll save.4.
Consult with an Electrician
If you're not 100% confident in your understanding of conduit fill calculations and the NEC, consult with a qualified and licensed electrician.
In summary, while dropping down a single 3/4" EMT nipple might be acceptable, it's crucial to prioritize safety and code compliance. Always* calculate the conduit fill, and seriously consider the practical implications of pulling multiple conductors through a short nipple. When in doubt, consult with a qualified electrician. Remember this is general information, and local and national codes may vary. You are responsible for understanding and following all codes. Flag for review