Question: Have a couple questions about a class 1 division 2 motor and pump.So they changed existing motor and pump seen in picture #1 to the motor and pump in pic#2The existing motor had a ground lead that ran from j box into the sealed motor. The new one did not. I did not notice this until I got the conduits put back together and got ready to terminate….As I was also looking for the wiring diagram the pump guys handed me the outlet box that they removed from the motor.Question 1 - will the rigid conduit be a sufficient means of bonding ? or am I going to need to break everything back apart install the outlet box on the motor and get an egc to the terminal inside the outlet box 3” away from the jbox?Question 2 - when the pump guy removed the the outlet box did he void any type of warranty on the motor?Motor is 240 single phase 2 hp. When I spoke to Baldor the rep said the motor and outlet box are listed separately… he suggested the box go back on if it were to be sent in for warranty, but wouldn’t give direct answer if it being taken off would void it…I have looked over 501.30 a and b and I don’t believe I meet the exceptions…I also looked of 430.12(e) but i don’t beleice that the exception would apply here as well…I am Hoping that this is a compliant install with out the outlet box going back on and running a egc 6” from j box to motor outlet box!?I think installing the outlet box on the motor and running the egc would be a much safer install, and will pry end up being the method I chose to fix this but I wanted to learn something and find out if it was or wasn’t compliant..Thanks in an advance I really appreciate all of you and your help!
Okay, let's break this down step-by-step. This is a common and important question, especially when dealing with hazardous locations.
Understanding the Requirements Class I, Division 2
This means the area could become hazardous due to the presence of flammable gases or vapors. This affects equipment selection and installation practices.
Bonding (Grounding)
Providing a low-impedance path back to the source is crucial for safety. This allows fault current to flow quickly, tripping overcurrent protection (like circuit breakers) and preventing dangerous voltage from appearing on equipment enclosures. In hazardous locations, this is even more important to minimize the risk of sparks.
Rigid Conduit
Rigid Metal Conduit (RMC) is often used in hazardous locations because it provides a robust, mechanically protected raceway and, when properly installed, can serve as an effective equipment grounding conductor (EGC).
Motor Listing
As Baldor mentioned, motors and their terminal boxes (outlet boxes) can be listed separately. The listing determines what the assembly has been tested and approved for.
NEC (National Electrical Code)
Your references to 501.30 and 430.12(E) indicate you're on the right track with your understanding of the NEC requirements.
Addressing Your QuestionsQuestion 1: Will the rigid conduit be a sufficient means of bonding?
This is the key question, and the answer is a qualified "maybe," but leaning heavily towards NO, it is likely NOT sufficient without the additional EGC. Here's why: NEC 501.30(A) and (B) - Equipment Grounding
This section covers the grounding requirements in Class I, Division 2 locations. Rigid conduit can be used as an EGC, but only if the connections are made up wrench-tight and free from corrosion. Even with these things completed the safest approach is to add a supplemental equipment grounding conductor.
The "Weak Link"
The problem isn't necessarily the rigid conduit itself but the connections at each end. Over time, connections can loosen due to vibration, corrosion, or thermal cycling. This increases impedance (resistance) and can compromise the effectiveness of the grounding path. This is why a supplementary ground wire is preferred, especially in hazardous locations.
The "Exception" Trap
You mentioned you don't think you meet the exceptions in 501.30(A) and (B). You're right. The exceptions are very specific and generally apply to situations like short, direct connections where the conduit run is very short and unlikely to have connection issues. This is a motor and pump setup, so vibration is a major concern.
NEC 430.12(E) - Motor Connection
The exception here only applies if the motor is specifically listed and marked for use without an external grounding conductor when connected with rigid conduit. In addition, some inspectors feel that this rule is not applicable in a classified location. Since you removed the listed outlet box, you have voided this exception.
Risk Tolerance
The level of risk is higher in a classified location.
Best Practice
Even if the rigid conduit might meet the minimum requirements, it's best practice to always include a supplementary equipment grounding conductor (EGC) inside the conduit, especially in hazardous locations. This adds an extra layer of safety and ensures a reliable low-impedance ground path.
Therefore, I strongly recommend you install the outlet box and run an EGC from your junction box to the motor's terminal inside the outlet box.Question 2: When the pump guy removed the outlet box, did he void any type of warranty on the motor? The Likely Answer: Yes, POSSIBLY. The Baldor rep's answer is telling. Here's the reasoning: Listed Assembly
The motor and outlet box, together, are a listed assembly. Removing a component changes the configuration from what was originally tested and approved.
Warranty Terms
Motor warranties typically state that any modification or alteration of the motor voids the warranty. Removing the outlet box could be considered a modification.
Burden of Proof
If the motor fails and a warranty claim is filed, Baldor could argue that the removal of the outlet box contributed to the failure, thus voiding the warranty. They might not automatically* deny the claim, but it gives them grounds to do so.
In summary, yes, removing the outlet box likely jeopardizes the warranty.Recommendations1. Reinstall the Outlet Box
This is the safest and most compliant option. It puts the motor back in its originally listed configuration.2.
Run an EGC
Run an appropriately sized equipment grounding conductor (EGC) inside the rigid conduit from the junction box to the motor's terminal inside the outlet box. The EGC size must comply with NEC 250.122, based on the rating of the overcurrent protective device (circuit breaker).
3.
Check all connections
Ensure that all threaded conduit connections are tight and free of corrosion. Use an anti-seize compound on the threads if necessary.4.
Document Everything
Take photos before, during, and after the work is completed. This documentation can be helpful if there are any questions or issues later.5.
Consult with a Qualified Professional
This is a critical situation. If you are unsure about any aspect of this installation, consult with a qualified electrical engineer or master electrician with experience in hazardous locations.6.
Confirm with Baldor
Get something in writing from Baldor regarding the warranty. Ask them specifically if removing and reinstalling the outlet box voids the warranty.
Why This Matters
In hazardous locations, even a small spark can have catastrophic consequences. Proper grounding and bonding are essential for safety. Don't take shortcuts or assume that the rigid conduit is sufficient. The cost of doing it right the first time is far less than the cost of an accident. Flag for review