Question: How do I calculate the overall load for a 100,000 sq.ft. school, using T 220.86, assuming that the initial calculated load was 2,500,000 VA
Okay, let's break down how to calculate the overall load for a 100,000 sq. ft. school using NEC 220.86, starting with an initial calculated load of 2,500,000 VA. This process involves determining the Actual Demand Factor (ADF) from the previous 12 months of billing data and applying it to the initial calculated load.
Understanding NEC 220.86 (Optional Method)
NEC 220.86 provides an optional method for calculating the service or feeder load for existing schools. It relies on historical energy consumption data to potentially reduce the calculated load if the actual usage is lower than what the standard calculation methods would suggest. Here's a summary of the key elements: Purpose
To allow for a lower calculated load based on actual past performance.
Applicability
Primarily for existing schools with at least one year of billing history.
Basis
Utilizes the highest 12-month billing demand to determine an Actual Demand Factor (ADF).
Limitation
the calculated load cannot be less than the load that will serve the school.
Steps to Calculate the Overall Load Using 220.861. Gather Billing Data
Crucial
Obtain the actual kilowatt (kW) billing demand data for the most recent 12 consecutive months. This is the key input. It's usually available from the utility company. The billing demand is the highest average kW usage over a specific time interval (e.g., 15 minutes, 30 minutes, or 1 hour) during the billing period (usually a month).2.
Convert kW to kVA
If the billing data is in kW, convert it to kVA by dividing each month's kW demand by the school's average monthly power factor. If the power factor isn't known, you can conservatively assume a power factor of 0.80 (although a better estimate is always preferred). `kVA = kW / Power Factor` If your billing data is already provided in kVA, you may skip this step.3.
Determine the Maximum kVA Demand
Identify the highest kVA demand among the 12 months of data. This is your "Maximum kVA Demand." Let's say, for example, the highest monthly kVA demand you find is 1,200 kVA.4.
Calculate the Actual Demand Factor (ADF)
Divide the Maximum kVA Demand (from Step 3) by the initial calculated load. This is your ADF. `ADF = Maximum kVA Demand / Initial Calculated Load` In our example: `ADF = 1,200 kVA / 2,500 kVA = 0.48` ADF cannot exceed 1.0. In other words, if your highest kVA demand were 3,000, your ADF would still be 1.
0.5.
Calculate the Adjusted Load
Multiply the Initial Calculated Load by the ADF. This is your Adjusted Load per 220.86. `Adjusted Load = Initial Calculated Load ADF` In our example: `Adjusted Load = 2,500 kVA 0.48 = 1,200 kVA`
Important Considerations and Caveats
Accuracy of Data
The accuracy of this method hinges entirely on the accuracy and completeness of the billing data.
Future Load Growth
Consider potential future load increases (e.g., new classrooms, technology upgrades, HVAC systems). The 220.86 calculation is based on past usage, and the electrical system must be adequate for future needs. Don't shortchange the school. You might need to add additional capacity.
Professional Judgment
It's essential to exercise professional judgment. If the historical data seems unusually low (e.g., due to extended school closures or unusual energy-saving measures), a more conservative approach might be warranted.
Local Codes and Regulations
Always consult with the local electrical inspector or authority having jurisdiction (AHJ) to ensure compliance with all applicable codes and regulations. They may have specific requirements or interpretations regarding 220.86.
Documentation
Thoroughly document your calculations and the data sources used. This will be essential for the inspector.
Minimum Load
Ensure that the calculated load is not lower than that required to serve the connected load.
Example Summary School Size: 100,000 sq. ft. Initial Calculated Load (from other methods): 2,500,000 VA (2,500 kVA) Highest Monthly kVA Demand (from 12 months of billing data): 1,200 kVA Actual Demand Factor (ADF): 1,200 kVA / 2,500 kVA = 0.48 Adjusted Load (using 220.86): 2,500 kVA 0.48 = 1,200 kVAIn this example, the overall load calculated using 220.86 would be 1,200 kVA. Remember to carefully consider future load growth and consult with the AHJ. Flag for review