User: Cberr, Location: NJ
Asked on: Tuesday, August 6, 2024 at 4:48 pm EDT
Answered on: Thursday, March 6, 2025 at 12:49 am EST
Question: Helping a neighbor with her pond fountain. It’s a 220v pump (oasi) pretty much a well pump…that is hooked up to a fountain for a large pond. There is a main panel with a normal 30 a breaker. From there a wire runs underground about 100 feet to a sub panel close to pond. the sub panel was original to original oasi pump. The panel has circuits for lighting and timer which is no longer in use or hooked up. so basically if you were to follow the power it goes into panel to a 30a gfci breaker then to the motor control box and out to pump fountain. the only other thing hooked up to the circuit is a lightning arrest or. Which ties into the two hots before breaker and the neutral bar.so recently pump started tripping breaker. I systematically elimintated all draws off breaker to troubleshoot. Finally removed everything and breaker was still tripping. So basically removed 2 hots coming out of breaker and still would not reset. Tried a new gfci breaker thinking bad breaker and still tripping. So had electrician come and he determined the underground wire Between panel and sub panel was bad. So I dug a trench and electrician came and ran a new wire. When I was able to get back to try it out (wasn’t there when electrician came to do work) all he did was hook up the wire from main panel to the 30 a gfci. I hooked everything back up it was still tripping? When I looked at the wiring he had used UF wire (I think #10) with 3 wires black white and ground. He hooked up the black and white to hots on breaker but the ground he hooked up to the ground lug on the motor, starter box. Nothing,going to the neutral bar. Except the curly wire from the gfci. Is that right? It raised a few questions if he did it right. Then i wonder3d if the wire he used was wrong. Should it have been 10-3 with a ground wire as well as the 2 hots and a neutral? I dug trench about 18“ and told homeowner to make sure he used conduit. But he told her this was correct? But i thought the only way is to code is if it’s 20a or under and gfci protected and also only 110v at that depth. Otherwise,it,would have to be 24” deep, right? If one were to start from scratch from the main panel, just curious how this would be done correctly and to code, as well as safely. Did this electrician do it correctly? I’m not looking to prove anyone wrong. Just want it to be safe as it’s in a pond and worried about it being properly grounded. Thanks.
Okay, this is a complex situation with several potential issues, and it's good you're being thorough and concerned about safety. Let's break it down step-by-step
1. The Grounding Issue & UF Cable
The Problem
The biggest immediate concern is the incorrect grounding. In a subpanel situation, you MUST have a separate neutral and ground. Bonding the ground wire to the neutral only at the main panel is crucial for safety. This prevents neutral current from flowing through the grounding path, which is a shock hazard.
Why it's Tripping the GFCI
GFCIs work by detecting an imbalance between the current flowing on the hot and neutral conductors. If any current is leaking to ground (through faulty insulation, a loose connection, or a damaged component), the GFCI will trip. By improperly connecting the ground, you are likely creating a path for current to leak, causing the GFCI to trip. The GFCI sees the ground wire, potentially with some stray current on it, and interprets that as a ground fault.
The Correct Wiring
You absolutely need a 4-wire feed to the subpanel (2 hots, neutral, ground). That means using a cable like 10/3 with ground (or larger depending on the pump's amperage draw)
Main Panel
Connect the two hot wires (typically black and red, or black and black) to the 30A breaker. Connect the neutral wire to the neutral bar in the main panel. Connect the ground wire to the ground bar in the main panel.
Subpanel
Connect the two hot wires to the 30A GFCI breaker in the subpanel. Connect the neutral wire to the
neutral bar in the subpanel. Crucially, ensure the neutral bar is isolated from the subpanel enclosure. There should be no bonding screw or strap connecting the neutral bar to the metal of the subpanel. Connect the ground wire to the ground bar in the subpanel. The ground bar should be bonded to the subpanel enclosure. The "curly wire" from the GFCI breaker (the neutral pigtail) connects to the neutral bar in the subpanel.2. UF Cable and Depth of Burial UF Cable
UF (Underground Feeder) cable is designed for direct burial. However, even though it's rated for direct burial, conduit is highly recommended. Conduit protects the cable from physical damage (rocks, shovels, rodents, etc.) and makes future replacement easier.
Depth
National Electrical Code (NEC) Requirements (General Guidelines - Always check local codes)
These are general guidelines. Local codes always supersede the NEC.
24 inches
This is the standard depth for direct burial of UF cable for 240V circuits.
18 inches
With GFCI protection, 240V circuits may be buried at 18 inches. This is where the electrician may be coming from.
6 inches
If the entire run is in rigid metal conduit (RMC) or intermediate metal conduit (IMC).
Inside Conduit
When using PVC conduit, the depth depends on the voltage and whether it's under a driveway or not. Generally, it would still need to be buried at a reasonable depth (18-24 inches is a safe bet).
Important
Local codes always take precedence over the NEC. Contact your local building inspector or electrical inspector to confirm the required burial depth for your specific situation. The electrician should have known this and obtained a permit.
Recommendation
Insist on conduit. It's a small investment for significant protection and future serviceability.
Permitting
This type of electrical work almost certainly requires a permit and inspection. Having it inspected ensures it meets code and is safe.
3. Lightning Arrestor The connection of the lightning arrestor sounds generally correct, but double-check the manufacturer's instructions for proper installation. It should be connected to both hots (before the GFCI breaker in the subpanel) and to the ground bar in the subpanel.4. The Pump and Motor Control Box Once the grounding issues are resolved, you'll need to carefully inspect the pump and motor control box for any signs of damage, water intrusion, or faulty wiring. It's possible the original short circuit that damaged the underground cable also damaged the pump or control box. Have the pump professionally tested to ensure it's not drawing excessive current or has internal shorts.5. Starting from Scratch (Hypothetical - but good to know) If you were starting from scratch, the best approach would be:1.
Determine the Pump's Amperage
Find the pump's nameplate and determine its full-load amperage (FLA) at 220V. This dictates the proper wire size and breaker size.2.
Calculate Voltage Drop
For a 100-foot run, calculate the voltage drop to ensure the wire size is adequate. Online voltage drop calculators can help. You want to keep voltage drop below 3%.3.
Select Wire Size and Cable
Based on the amperage and voltage drop calculation, choose the appropriate wire size (e.g., #10, #8, etc.). Use 10/3 with ground UF cable (or larger) or individual THWN wires inside conduit.4.
Choose Conduit
Use PVC conduit (Schedule 40 is common) or rigid metal conduit (RMC) for maximum protection.5.
Install Conduit
Dig the trench to the required depth (check local codes), install the conduit, and ensure it's properly assembled and glued (if PVC). Use sweeps (long-radius bends) instead of sharp elbows.6.
Pull Wires
Carefully pull the wires through the conduit, being careful not to damage them.7.
Connect at Main Panel
As described above, connect the wires to the breaker in the main panel.8.
Connect at Subpanel
As described above, connect the wires to the GFCI breaker and the neutral and ground bars in the subpanel. Absolutely ensure the neutral bar is isolated from the subpanel enclosure.9.
Test
Once everything is connected, test the system to ensure it's working properly and the GFCI is functioning correctly.10.
Have it Inspected
This is critical.
Summary and Recommendations1.
Stop using the system until the grounding issues are corrected. It is a safety hazard.2.
Consult with a different licensed electrician. The current setup is not safe or to code. You need someone who understands proper subpanel wiring and grounding. Show them this detailed explanation.3.
Correct the Wiring
Insist on a 4-wire feed to the subpanel, with the neutral and ground properly separated and connected as described above.4.
Install Conduit
Strongly consider installing conduit for added protection.5.
Check Burial Depth
Verify the required burial depth with your local building or electrical inspector.6.
Inspect Pump and Motor Control Box
Have the pump and control box professionally inspected.7.
Obtain a Permit:* Make sure a permit is pulled for the electrical work and that it's properly inspected.Electricity and water are a dangerous combination. Prioritizing safety and following proper code is absolutely essential in this situation. Good luck! Flag for review