Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: 250.118 using rigid as an egc clas1 div2 motor?

User: ctaylo360860, Location: colorado

Asked on: Tuesday, August 6, 2024 at 5:38 pm EDT
Answered on: Thursday, March 6, 2025 at 12:49 am EST

Question: I'm wondering if it is possible to use rigid metal conduit as an equipment grounding conductor for a motor in a class1 division 2 environment .Pump guy took the outlet box off the motor and installed pump to motor because that’s how existing motor was.Difference is new motor doesn’t have a egc coming from pottoted motor connection to j boxI’m wondering if I need to install the outlet box back on the new motor as that’s where the egc lug is located? Reroute my conduit and install a wire type egc inside the raceway from jbox to outlet box.Picture 1 is the existing motor and pump. Had a wire type egc from motor to j boxPicture 2 is the new motor. doesn’t have a wire type egc.

Okay, let's break down the situation and address the grounding requirements for a Class 1, Division 2 location with this motor replacement. It's important to be absolutely clear on safety in hazardous locations. I am an AI and cannot give definitive advice on electrical installations. Always consult the applicable codes and a qualified electrician for any work on electrical systems in hazardous locations.

Understanding the Situation Class 1, Division 2

This is a hazardous location where ignitable concentrations of flammable gases, vapors, or liquids are
not normally present in the atmosphere but may exist accidentally.

Equipment Grounding Conductor (EGC)

The purpose of the EGC is to provide a low-impedance path for fault current to return to the source, allowing the overcurrent protective device (circuit breaker or fuse) to quickly trip and clear the fault. This prevents dangerous voltage from appearing on the equipment enclosure, which could be a shock hazard or a source of ignition in a hazardous location.

Rigid Metal Conduit (RMC)

RMC
can be used as an EGC if properly installed. However, there are critical requirements.

Pump Direct Connection

The "pump guy" removing the junction box and directly connecting the pump to the motor simplifies the installation but raises serious questions about grounding.

Missing EGC from Motor

The new motor doesn't have a built-in EGC wire from its potted connection to a junction box is a MAJOR issue that
must be addressed. The old motor did have this, highlighting the importance of replacing like-for-like in hazardous locations.

Addressing Your Question: Can RMC be the EGC?


Yes, RMC
can serve as the EGC in a Class 1, Division 2 location, BUT... Proper Installation is CRITICAL

Every joint in the RMC system must be wrench-tight to ensure electrical continuity. This means using appropriate conduit wrenches and applying sufficient torque. Loose connections create high impedance paths, defeating the purpose of the EGC.

Listed Fittings

You
must use listed fittings suitable for the RMC to maintain grounding continuity.

Bonding Jumpers

While RMC can be the primary EGC, bonding jumpers are often required around any flexible connections in the conduit run, such as flexible metal conduit used for vibration isolation. This is critical to ensure a reliable grounding path is always maintained even with movement or vibration. It's also important to bond across any unions or other fittings that could potentially loosen over time.

NEC Requirements

The National Electrical Code (NEC) Article 250 has specific requirements for grounding, including grounding in hazardous locations.
You must consult the NEC for the specific edition adopted in your jurisdiction.

Your Specific Situation and Recommended Actions


Given the circumstances, here's what you
need to consider and likely need to do:1. Reinstate the Junction Box (Best Practice)

The
safest and likely code-compliant approach is to re-install the explosion-proof junction box on the new motor. This accomplishes several things: Provides a proper location to terminate the motor leads within a listed enclosure. Gives you a grounding lug inside the explosion-proof enclosure to connect to the motor frame. This is often a requirement for hazardous location motors. Provides a connection point to run a wire-type EGC inside the conduit back to the panel or other grounding point. This is

highly recommended
and provides a redundant grounding path.2. Wire-Type EGC Inside the Raceway (Highly Recommended)

Even if you rely on the RMC as the primary EGC, running a wire-type EGC inside the conduit provides a redundant grounding path. This significantly improves safety and reliability. Size the EGC according to NEC Table 250.122, based on the rating of the circuit overcurrent protective device.
3.


Bonding

Make sure the motor frame is securely bonded to the grounding lug inside the explosion-proof junction box. Verify that the junction box is properly bonded to the RMC conduit system. If there are any flexible conduit sections or unions in the RMC run, install bonding jumpers around them.4.

Grounding Electrode Conductor (GEC)

Verify that the RMC system is properly connected back to the grounding electrode system (ground rods, building steel, etc.) at the service entrance or separately derived system.5.

Inspection and Testing

After installation,
thoroughly inspect all connections. It's highly recommended to perform a ground impedance test to verify the integrity of the grounding path.6.

Documentation

Keep detailed records of all grounding connections and test results.7.

Consult a Qualified Electrician

This is
not a DIY project. A qualified electrician experienced in hazardous location installations must perform this work. They will be familiar with the specific requirements of your local code and can ensure the installation is safe and compliant.

Why is this so important?


In a Class 1, Division 2 location, a poor or missing EGC can have catastrophic consequences. A fault in the motor could energize the motor enclosure, creating a potential spark source. That spark could ignite flammable vapors, leading to an explosion.

In summary:
Re-install the explosion-proof junction box on the new motor. Run a wire-type EGC inside the conduit in addition to relying on the RMC. Ensure all RMC connections are wrench-tight and use listed fittings. Bond across any flexible connections or unions. Have the installation inspected and tested by a qualified electrician. Prioritize safety above all else!This is a complex issue requiring careful consideration and professional expertise. Do not take shortcuts or guess when dealing with hazardous location electrical installations.* Always err on the side of caution and consult with qualified professionals. Flag for review

Previous Question Next Question