User: Kishore25, Location: New Jersey, USA
Asked on: Tuesday, August 6, 2024 at 5:42 pm EDT
Answered on: Thursday, March 6, 2025 at 12:49 am EST
Question: For voltage drop calculation, do we take resistance value from Table 8 or from Table 9.Online southwire uses, resistance value from table 8 and reactance value from table 9 of the NEC to calculate the voltage drop
You're right to notice the different resistance values in Tables 8 and 9 of the NEC (National Electrical Code). The choice between using values from Table 8 or Table 9 for voltage drop calculations depends on the situation and the type of conductor
Table 8: Conductor Properties
This table provides DC resistance values (ohms per 1000 ft at 75°C) for various conductor sizes and materials. DC resistance is the opposition to current flow when the current is constant and unidirectional, like in a battery circuit.
Table 9: AC Resistance and Reactance This table provides AC resistance and reactance values (ohms to neutral per 1000 ft at 75°C) for conductors in a raceway or cable. AC resistance is the effective resistance to current flow when the current is alternating (AC). It includes the DC resistance plus additional resistance caused by skin effect and proximity effect. Reactance is the opposition to current flow due to the inductance and capacitance of the conductors and surrounding materials.
Why Southwire (and others) Use Table 8 for Resistance and Table 9 for Reactance
For accurate voltage drop calculations in AC circuits, you should ideally consider both resistance and reactance. The impedance (total opposition to AC current) is calculated using both. Here's the general approach:1. Resistance
For calculating the resistance portion of voltage drop, Southwire and many others prefer to use the
DC resistance values from Table 8. While Table 9 provides AC resistance, the increase in resistance due to skin effect and proximity effect is relatively small for smaller conductors (AWG 8 and smaller). For larger conductors, you may want to consider using the AC resistance value from Table 9 for more accuracy.2. Reactance
The
reactance values are almost always taken from Table 9. Reactance is a significant factor in AC circuits, especially over longer distances. The reactance represents the inductive reactance of the conductors.3. Impedance
Combine resistance and reactance. You'll often see the following formula or a variation of it used:Z = √(R² + X²)Where: Z = Impedance R = Resistance (from Table 8 or Table 9) X = Reactance (from Table 9)4.
Voltage Drop Calculation
You then use the calculated impedance in the voltage drop formula.
Simplified Voltage Drop Formula (Common but Less Accurate)
A common simplified voltage drop formula that you might encounter is:VD = (2 L I R) / 1000 (for single-phase)VD = (1.732 L I R) / 1000 (for three-phase)Where: VD = Voltage Drop (in volts) L = Length of the conductor (one-way, in feet) I = Current (in amps) R = Resistance (from Table 8 - often used in this simplified version)Important Considerations and When to Use Table 9 Resistance Accuracy
Using only DC resistance from Table 8 is a simplification. It's generally acceptable for shorter runs and smaller conductor sizes where reactance is minimal. For longer runs or larger conductor sizes, the impedance calculation including both resistance (preferably AC resistance from Table 9 for large conductors) and reactance from Table 9 is much more accurate.
Larger Conductors
For larger conductors (typically larger than AWG 8), the skin effect and proximity effect become more significant. Using the AC resistance values from Table 9 is recommended for more accurate voltage drop calculations in these cases.
Conduit Type and Spacing
The reactance values in Table 9 are based on typical conduit installations. If your installation has unusual conduit spacing or arrangements, it can affect reactance.
Software and Calculators
Many online voltage drop calculators (like the one from Southwire) have built-in logic to select the appropriate values from Tables 8 and 9 based on conductor size and other parameters. They often use the impedance method (R and X).
Manufacturer's Data
Some cable manufacturers provide specific impedance data for their products. This data is often more accurate than relying solely on NEC tables.
In summary
Table 8 (DC resistance)
Suitable for simpler voltage drop calculations, especially for shorter runs and smaller conductors where reactance is less significant. Often used in simplified voltage drop formulas.
Table 9 (AC resistance and reactance)
Provides the data needed for more accurate impedance-based voltage drop calculations, especially for longer runs, larger conductors, and situations where reactance is a significant factor. Use AC resistance from Table 9 for larger conductors.
Best Practice: The most accurate method involves calculating impedance using resistance (from Table 8 or* Table 9, depending on conductor size) and reactance (from Table 9) and using that impedance in the voltage drop calculation.Always check the specific assumptions and methodologies used by any voltage drop calculator or software you are using. Understanding the basis for the calculations ensures you are getting the most accurate results for your application. If in doubt, it is always safer to use the more conservative (higher voltage drop) result. Flag for review