User: makoester12, Location: Indiana
Asked on: Tuesday, August 6, 2024 at 6:07 pm EDT
Answered on: Thursday, March 6, 2025 at 12:49 am EST
Question: Good Afternoon,I am working on an application that strictly contains (2) above ground diesel fuel tanks with motor operated pumps mounted on top. The area has been considered unclassified since only diesel (combustible liquid) is in the area and the flash point of particular blend is ~140 degrees F. My question deals with whether the circuit disconnect requirements within 514.11 still apply or not? Essentially, if the area is considered unclassified, can the remainder of Article 514 be ignored? Within the handbook commentary, it is stated that "Article 514 encompasses all locations where volatile flammable liquids or gases are dispensed into the fuel tanks of self-propelled vehicles or other approved fuel tanks." While this is only commentary, does this provide indication of the intent of Article 514? Additionally, 514.11 seems to indicate that the area surrounding the dispenser is deemed classified ("and to all other electrical equipment in the hazardous (classified) locations surrounding the fuel dispensing devices").Thanks for your input.
Good afternoon! Your question highlights a common point of confusion when applying the NEC. Let's break down Article 514 and its applicability to your situation
Key Considerations and Analysis:
1. Combustible vs. Flammable Liquids
The distinction is crucial. Diesel fuel, with a flashpoint of ~140°F, is classified as a
combustible liquid under NFPA 30 (Flammable and Combustible Liquids Code). Flammable liquids have flashpoints below 100°F.2. Hazardous (Classified) Locations and the Diesel Exception
NFPA 30 (and, consequently, the NEC) recognizes that diesel fuel generally doesn't create a hazardous atmosphere under normal operating conditions. This is why you've deemed the area unclassified.3.
Scope of Article 514
Here's where it gets nuanced. Article 514 primarily addresses locations where
flammable liquids (like gasoline) are dispensed. However, this is not to say that article 514 is strictly limited to these applications.4. NEC 514.3 Scope. “The provisions of this article shall apply to electrical wiring and electrical equipment located in areas made hazardous by the presence of flammable liquids, or combustible liquids as defined in 514.3(B), where such liquids are used as fuels”. “Class I liquids shall be as defined in NFPA 30, Flammable and Combustible Liquids Code. Combustible liquids shall be as defined in NFPA 30B, Code for the Manufacture and Storage of Aerosol Products, and shall include Class II and Class IIIA liquids.”5. NEC 514.3(B) Application of Other Articles. “The general rules of this Code shall apply unless modified by this article.”6. NEC 514.11 Circuit Disconnects. “Each circuit leading to or through dispensing equipment, including equipment for remote pumping, shall have a switch or circuit breaker that simultaneously disconnects all conductors of the circuit, including the grounded conductor, if any…Such disconnecting means shall be readily accessible and conspicuously marked as to its purpose.”7. Interpreting 514.11 and the "Surrounding" Area
This is the core of your question. Even if the overall area is unclassified due to the diesel fuel's characteristics, 514.11 seems to imply a localized classification around the dispensing equipment, or dispensers. In particular, it seems that the requirement for readily accessible circuit disconnects remains regardless of area classification as noted within 514.3(B).
Your Question Answered
In your specific scenario, if the entire area is designated as unclassified based on the properties of the diesel fuel and relevant codes (NFPA 30), you might argue that Article 514 doesn't apply in its entirety. This is dependent on your AHJ and specific code interpretation. However, because NEC 514.3(B) states “The general rules of this Code shall apply unless modified by this article,” AND there are no explicit modifications regarding combustible liquids, then 514.11 likely applies. Therefore, the requirement for a readily accessible disconnect means on all circuit conductors remains despite the area being deemed unclassified. A Conservative Approach
Even if not strictly required, installing a readily accessible disconnect for the pump motors is a best practice for safety and maintenance. It aligns with the spirit of the NEC and provides a clear means to de-energize the equipment in an emergency or for servicing.
AHJ is the Final Authority
Ultimately, the Authority Having Jurisdiction (AHJ) has the final say. Discuss your design with them, present your reasoning for the unclassified designation, and get their feedback on the applicability of 514.11. This discussion should be documented.
Recommendations
Document Everything
Thoroughly document your hazard assessment, the diesel fuel's specifications, and the rationale for classifying the area as unclassified.
Consult NFPA 30
Refer to NFPA 30 for the specific requirements related to the storage and handling of combustible liquids.
Engage with the AHJ
This is the most important step. Early communication with the AHJ can prevent costly rework later.
Err on the Side of Safety: When in doubt, implement best practices, such as readily accessible disconnects.I hope this breakdown is helpful. Good luck with your project! Flag for review