Question: Sorry for a stupid question but I discovered this floating run of EMT while troubleshooting a unrelated circuit, it was near by and I figured it would be a ground reference. I am now attempting to find where it says EMT *shall* be grounded. I see it can be the EGC but not that it must be one or be connected to one, I see 300.10 requires metallic raceways to joined together but it stops short of saying it *shall* be grounded:Electrical Continuity of Metal Raceways and Enclosures.Metal raceways, cable armor, and other metal enclosures for conductors electrical shall be metallically joined together info a continuous electrical conductor ...
You're right, the NEC doesn't explicitly say "EMT shall be grounded" in a single, easily digestible sentence. It's more of a combination of requirements that leads to that conclusion. Here's the breakdown: 300.10 Electrical Continuity of Metal Raceways and Enclosures
This section requires metal raceways to be "metallically joined together into a continuous electrical conductor." This is the foundation. If it wasn't continuous, grounding wouldn't be effective.
250.4(A)(3) Bonding of Electrically Conductive Materials and Other Equipment
This is a key section. It states that "Normally non-current-carrying conductive materials enclosing electrical conductors or equipment, or forming part of such equipment, shall be connected together and to the electrical supply source in a manner that establishes an effective ground-fault current path."
250.4(A)(5) Effective Ground-Fault Current Path
A continuous, low-impedance ground-fault current path is essential for clearing faults quickly and safely.
250.118 Types of Equipment Grounding Conductors
This section lists acceptable types of EGCs, and EMT is among them.
250.96 Bonding Other Enclosures
Addresses bonding of enclosures.
Putting it Together
Think of it like this:1.
Continuity (300.10)
You need a continuous metallic path.2.
Bonding (250.4(A)(3))
That continuous metallic path must* be connected to the electrical supply source to create a low-impedance ground fault current path.3.
EGC (250.118)
EMT is an approved method for establishing that ground-fault current path (when properly installed).4.
Ground-Fault Current Path (250.4(A)(5))
The purpose of all of this is to ensure that a fault current can quickly and safely return to the source, tripping a breaker or blowing a fuse.
Why It Matters
The purpose of grounding is to protect people and equipment from electrical shock. If a fault occurs (e.g., a live wire comes into contact with the EMT), the grounded EMT provides a low-resistance path for the fault current to flow back to the source. This high current causes the overcurrent protective device (breaker or fuse) to trip, quickly de-energizing the circuit and preventing a dangerous voltage from appearing on the EMT.
In your situation, a floating EMT is a safety hazard. It could become energized in a fault condition without tripping a breaker, posing a shock risk.
Recommendations
Identify the Source
Determine where the EMT runs to and from.2.
Ground it Properly
Connect the EMT to a known grounding point (e.g., a grounding busbar in a panelboard, a grounding electrode conductor). Use appropriate bonding jumpers if needed to ensure good electrical continuity. A listed fitting is required.3.
Verify Grounding
Use a multimeter to verify that the EMT is properly grounded and has a low resistance to ground.
In Summary:
While the NEC doesn't say "EMT SHALL be grounded" in those exact words, the combination of requirements related to continuity, bonding, and ground-fault current paths effectively mandates that EMT (when used as a raceway) must be connected to a grounding system. Failing to do so creates a significant electrical safety hazard. Consult with a qualified electrician to address this issue. Flag for review