Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Voltage drop in 3 phase.

User: mylk100, Location: Philadelphia

Asked on: Tuesday, August 6, 2024 at 9:47 pm EDT
Answered on: Thursday, March 6, 2025 at 12:50 am EST

Question: HiI am running a circuit about 220 feet for a motor. If I upsize the wiring should I also upsize the breaker or does the breaker stay the same size as what was the initial breaker called for on the job? For instance. I have a 80 amp breaker 3 pole. I installed a 1 gauge wire instead of a 3 gauge which the job called for on the spec sheet. Do I need to change the breaker to a 100 amp breaker. Or should I just upsize the wire and leave the breaker at 80?

Okay, let's break down the situation regarding upsizing wire for a motor circuit and whether you need to change the breaker size.

The Core Principle: Motor Protection vs. Conductor Protection Breaker/Overload Protection

Primarily protects the
motor from overload and short circuits. Its size is based on the motor's Full Load Amps (FLA) and the applicable codes (mainly the National Electrical Code, or NEC).

Conductor Sizing

The conductor (wire) must be sized to carry the motor's current, plus any safety factors required by code (usually 125% of the motor's FLA), AND account for voltage drop over the distance.

The NEC is what you should follow.
Your Scenario (80A breaker, 1 AWG wire instead of 3 AWG, 220 ft run)


Conductor Sizing (Upsizing Wire)

You've correctly identified that longer runs need larger conductors to minimize voltage drop. Voltage drop can cause the motor to run inefficiently, overheat, and even fail prematurely. Upsizing the wire is a good practice in this case. Using 1 AWG instead of 3 AWG definitely reduces voltage drop and increases the ampacity of the wire.2.

Breaker Size



Crucially, upsizing the wire DOES NOT automatically mean you need to upsize the breaker.
The breaker's primary function is to protect the motor, not the wire. The breaker size is based on the motor's nameplate data (FLA, Service Factor, Temperature Rise) and the NEC tables/calculations. The original 80A breaker was likely sized based on those factors. If the 80A breaker was correctly sized for the motor initially, based on the motor's FLA, you should generally leave it at 80A.When Might You Consider a Larger Breaker?

There are some limited situations where a slightly larger breaker
could be considered after careful analysis, but always consult a qualified electrician for these scenarios



Motor Starting Issues

If the motor is tripping the 80A breaker frequently during startup due to inrush current, and if the NEC allows, you might be able to increase the breaker size slightly to accommodate the inrush.

This is the most common reason to consider a slight increase, but it MUST be done according to code and with careful consideration.
Code limits the amount you can increase. Specific Motor Characteristics

Some motors with specific service factors or temperature rise ratings might allow for slightly different overload protection settings. Again, refer to the NEC and motor documentation.

Important Considerations and Steps


Verify Motor Nameplate Data

Double-check the motor's nameplate to confirm the FLA, service factor, and other relevant information.2.

Calculate Minimum Conductor Size

Ensure the 1 AWG wire you've used meets the NEC requirements for the motor's current (125% of FLA)
and accounts for the voltage drop over the 220-foot run. Use a voltage drop calculator.3.

Consult the NEC (Article 430)

Article 430 of the NEC is the definitive guide for motor circuits. Understand the rules for motor overload protection, short-circuit protection, and conductor sizing.4.

Consider Motor Overload Protection (Heaters or Electronic Overloads)

Many motor starters include separate overload protection (heaters or electronic overloads) that are specifically designed to protect the motor from sustained overloads. These devices are sized based on the motor's FLA and are more sensitive to overloads than the breaker. The breaker provides short-circuit protection.5.

Voltage Drop Calculation

The most important reason you used larger wire was to reduce voltage drop. Check to make sure the voltage drop meets the NEC requirements with the larger wire installed.6.

Engage a Qualified Electrician

This is
crucial. Motor circuits are complex, and improper wiring or protection can be dangerous and damage equipment. A licensed electrician can perform the necessary calculations, verify the installation, and ensure it meets all applicable codes.

In summary, in your case, generally leave the 80A breaker in place.
Unless you are experiencing motor starting issues. Do not* increase the breaker size simply because you upsized the wire. The wire is upsized to reduce voltage drop, and the breaker size is designed to protect the motor. ALWAYS consult a qualified electrician to confirm. Flag for review

Previous Question Next Question