Question: We are working on 5MWac community solar and have submitted IC drawing. Utility is asking us to show configuration on the 10kVA auxiliary transformer and specify if transformer configuration Delta : WYE G. We currently take two lines (L1 and L2, 600V) from three phase panelboard with 30A, 2P breaker for auxiliary transformer.I am attaching the utility concern for your reference. FYI, utility is AEP Ohio. Secondary is 120/240VWhat is best configuration for auxiliary transformer when service transformer configuration is WYE G: WYE G, 600V:12.47kV, 5MVAOriginally no winding configuration symbols was shown for the aux transformer on drawings.Utility commentwhat is required for each of the projects to avoid the loss of phase testing.The main issue that arose from the drawing set was a lack of clarity surrounding how the auxiliary transformers were shown in the drawings. What our engineers wanted clarity on is if the auxiliary transformer is taking more than a single phase on the primary side, then how is the transformer wired? The use three phase transformers that are not configured as WYE-grounded : WYE-grounded is problematic due to the noted effect it has on the inverters to detect a utility loss of phase-it has been observed that if a delta transformer is wired in series or in parallel with the inverter systems, then the delta transformer has made it difficult for the inverters to fully detect a utility side loss of phase event, so they will continue operations when they should cease to energize. So if the auxiliary transformers are three phase, then our engineering team wants to ensure that they are wired in a way that will not cause an issue with the inverters to detect a loss of phase on the utility side and will cease to energize. The preferred configuration is WYE-grounded : WYE-grounded.If the transformers are not 3 phase, then the engineering team wants to ensure that the proper primary side voltage of the auxiliary transformer is shown on the system. If the transformers are single phase, then please show the primary side voltage as 347 V (L-N voltage).
Okay, this is a common issue in community solar projects, especially with AEP Ohio's concerns about loss-of-phase detection. Let's break down the problem and the best solution.
Understanding the Issue
The utility is concerned that a Delta-configured transformer, especially if supplying auxiliary loads crucial to the inverter's operation (like control power), can mask a loss-of-phase condition on the utility grid. Here's why: Delta-Wye Transformer and Phase Isolation
A Delta-Wye transformer can maintain voltage on its secondary side even if one phase on the primary (utility) side is lost. This is because the Delta winding provides a circulating current path that can partially compensate for the missing phase.
Inverter Loss-of-Phase Detection
Inverters are designed to detect a loss-of-phase on the grid and immediately disconnect to prevent backfeeding and potential safety hazards. If the auxiliary power is maintained by a Delta-Wye transformer masking the loss of phase, the inverter might not detect the fault and could continue to operate unsafely.
Wye-Grounded:Wye-Grounded is Preferred
A Wye-Grounded:Wye-Grounded transformer doesn't have this masking effect. If a phase is lost on the primary, the voltage on the secondary will also drop significantly, allowing the inverter to detect the fault.
Analyzing Your Current Configuration
You're currently taking two lines (L1 and L2, 600V) from a three-phase panelboard for a single-phase 10kVA auxiliary transformer. This simplifies the configuration.
The Solution: Single-Phase Transformer and Clear Voltage Specification
Given your current setup using a single-phase transformer, the key is to clearly specify the primary voltage and transformer configuration. Here's what you need to do:1. Specify Primary Voltage
Since you're taking 600V L-L voltage for single phase transformer. It is very important to clearly show primary voltage of transformer as 600V and specify it is single phase transformer.2.
Transformer Configuration
Since you are using single phase transformer, there is no need to specify transformer configuration as WYE or Delta.3.
Update Your Drawings
Make the following changes to your IC drawings:
Clearly label the auxiliary transformer as "Single-Phase Transformer". Specify the primary voltage as 600V. Include the kVA rating (10kVA). Specify the secondary voltage as 120/240V. Show the transformer connection clearly (L1 and L2 from the three-phase panelboard). No need to specify WYE or DELTA connection for single phase transformer.
Why This Works No Masking Effect
A single-phase transformer doesn't have the phase-masking characteristic of a Delta-Wye three-phase transformer. If the 600V feed to the transformer is lost, the secondary voltage will also drop, allowing the inverters to detect the fault.
Meets Utility Requirements
By clearly showing that you're using a single-phase transformer with the correct primary voltage, you address the utility's concern about potentially masking a loss-of-phase condition.
Example Drawing Update Snippet
Instead of showing a generic transformer symbol, add something like this to your single-line diagram:L1 ---|| Single-Phase TransformerL2 ---| 10 kVA| Pri: 600V (L-L)| Sec: 120/240V|N ---|
Response to the Utility
When you resubmit the drawings, include a brief explanation in your transmittal letter. Here's an example:"Regarding the auxiliary transformers, please note that these are single-phase transformers. The primary voltage is 600V (L-L), connected to L1 and L2 of the three-phase panelboard. We have updated the drawings to clearly reflect this configuration. This configuration will not impact the inverter's ability to detect a loss-of-phase condition on the utility grid, as a single phase transformer does not exhibit the masking effect associated with three-phase Delta-Wye transformers."Important Considerations
Breaker Coordination
Double-check that the 30A, 2P breaker is properly sized and coordinated for the 10kVA transformer and the loads it will supply.
Grounding
Ensure proper grounding of the transformer and the loads it supplies, according to NEC and AEP Ohio requirements.
Future Expansion: If you anticipate needing more auxiliary power in the future, consider whether a single-phase transformer will still be adequate or if you might need to explore a three-phase option later. If a three-phase option is in the future, WYE-Grounded:WYE-Grounded will be required.By clarifying your use of single-phase transformers and providing accurate voltage information, you should be able to address AEP Ohio's concerns and move forward with your project. Remember to always consult with a qualified electrical engineer to ensure compliance with all applicable codes and regulations. Flag for review