Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Connector

User: Alwayslearningelec, Location: NJ

Asked on: Wednesday, August 7, 2024 at 8:09 am EDT
Answered on: Thursday, March 6, 2025 at 12:50 am EST

Question: If you have insulated throat EMT connector do you need a bushing,? If non insulated you would not need a bushing obviously. Question is really about needing bushing for insulated throat.

Okay, let's clarify the bushing requirement with insulated throat EMT connectors.

The general answer is: No, if the EMT connector has an insulated throat, you do NOT need a separate bushing for conductors #4 AWG and larger.Here's why



Purpose of Insulated Throat Connectors

Insulated throat connectors are specifically designed to protect conductors from abrasion against the sharp edge of the cut end of the EMT conduit. The integral insulation (usually a smooth, rounded plastic or rubber) provides a smooth surface for the conductors to be pulled through, preventing damage to the insulation.


Bushing Requirement (NEC 300.4(G))

NEC 300.4(G) states that where conductors #4 AWG or larger enter a raceway or enclosure, they must be protected from abrasion during and after installation. This is normally accomplished by using a bushing or connector with a smoothly rounded or flared entry.

Insulated Throat Meets the Requirement

The insulated throat on the connector
already provides this smooth, rounded entry. Therefore, a separate bushing is redundant and not required.

Important Considerations



Verify Insulation

Make sure that the insulated throat is actually present and in good condition. If the insulation is damaged or missing, you would need to add a bushing or replace the connector.*

If #6 AWG or smaller.
You would not need a bushing on standard connectors due to the wire size.

In summary: You are correct. Because the insulated throat already protects against abrasion, you would not need an additional bushing when using an insulated throat EMT connector for conductors #4 AWG and larger. Flag for review

Previous Question Next Question