Question: I had inspector turn me down. Said I can't use a sealing washer above live parts. I used a TA adapter with the sealing washer. What code section are sealing washers and Myers hubs in
Okay, let's break down why your inspector likely turned down your installation and where you can find the relevant code information.
The Core Issue: Sealing Washers and Live Parts
The inspector's concern is valid. Sealing washers are generally not permitted to be placed between a live electrical conductor (like a wire termination) and the enclosure itself. The reason is that they are typically made of non-conductive materials (rubber or fiber) and are designed to provide a seal against water and other ingress, not to act as an insulator for live parts.Think of it this way: Insulation
Insulates live conductors from accidental contact. Think of the plastic or rubber coating on wires.
Sealing
Prevents water, dust, or other contaminants from entering an enclosure.You need proper insulation between live parts and any conductive enclosure. A sealing washer isn't designed for that purpose.
Why the TA Adapter with Sealing Washer Matters
The TA adapter (threaded adapter) with a sealing washer is typically used to:1. Connect a conduit to an enclosure (like a junction box, panel, or motor housing).2. Provide a weatherproof seal where the conduit enters the enclosure.
The problem is that you mentioned "above live parts." This suggests you may have placed the sealing washer in a way that it's potentially acting as the primary insulation between the live conductors within the enclosure and the enclosure itself.
Code Sections and Related Information
The National Electrical Code (NEC) is the primary reference for electrical installations in the US. Here's where you'll find relevant information: Article 300: Wiring Methods This article covers the general requirements for wiring methods and materials. Pay attention to sections covering: 300.6 Protection Against Corrosion
This is important when dealing with outdoor or wet locations, but also relates to the materials you're using.
300.12 Mechanical Continuity - Raceways and Cables
Ensuring that your wiring system has proper mechanical strength and continuity is important for safety.
300.4(F) Insulated Fittings
This section specifically covers the requirements for using insulated fittings to protect conductors where they enter enclosures or raceways. This is relevant because it addresses how to properly protect conductors that pass through metal.
Article 314: Outlet, Device, Pull, and Junction Boxes; Conduit Bodies; Fittings; and Handhole Enclosures 314.17(B) Conductors Entering Boxes, Conduit Bodies, or Fittings. This is critical. It outlines how conductors must be protected when entering boxes/enclosures. It generally requires a fitting (like a connector) that securely clamps the cable or conduit to the box, protecting the conductors from abrasion. This is where the inspector will likely be focused.
Article 314.40 Covering Boxes Boxes must be closed and any openings must be closed off properly.
Article 312: Cabinets, Cutout Boxes, and Meter Socket Enclosures 312.5 Deflection of Conductors. If the conductors are bent or deflected inside the cabinet, it must be done in a way that doesn't damage the insulation.
Article 430: Motors, Motor Circuits, and Controllers (if applicable) If this is related to motor wiring, Article 430 will have additional requirements.
Article 110: Requirements for Electrical Installations This covers general requirements, including: 110.3 Examination, Identification, Installation, and Use of Equipment
Electrical equipment must be installed and used according to its listing and labeling. This is key. The TA adapter and any other components you use must be listed for the intended purpose.
Myers HubsMyers hubs are specifically designed to provide a raintight connection between a conduit and an enclosure. They typically include an insulated throat which protects conductors from abrasion when entering the enclosure.
Listing and Labeling (110.3)
Myers hubs, like all electrical equipment, must be listed by a recognized testing laboratory (like UL or ETL). The listing will specify the intended use (e.g., raintight connection). Using a hub not listed for raintight applications in a wet location is a violation.
Why the Inspector is Right (Probably)Based on your description, the inspector likely interpreted your installation as using the sealing washer in place of proper insulation between the live conductors and the enclosure. This would violate the code because a sealing washer isn't designed to provide the necessary insulation to prevent electrical shock or short circuits.
What to Do Now1.
Clarify the Installation
Talk to the inspector again and carefully explain exactly how you installed the TA adapter and sealing washer. A picture or diagram might help. Understand specifically what the inspector believes is the code violation.2.
Review the Equipment Listings
Carefully review the listings and instructions for the TA adapter and the sealing washer. Make sure they are approved for the way you are using them.3.
Correct the Installation
The following are common fixes:
Use an Insulated Bushing or Connector
These are designed to protect conductors as they pass through a knockout in an enclosure. An insulated bushing will provide the required insulation between the conductors and the enclosure.
Use a Myers Hub (Properly Installed)
If you need a raintight connection, ensure you're using a listed Myers hub with its insulated throat. Follow the manufacturer's instructions.
Ensure Proper Wire Termination
Make sure the wire terminations inside the box are properly insulated with wire connectors or tape, according to code.
Double-Check Grounding
Verify that the enclosure is properly grounded according to NEC requirements (Article 250).
Example of a Correct Installation (General Guidance)
1. Conduit enters the enclosure through a knockout.
2. A listed Myers hub (or a TA adapter with an insulated bushing) is used to connect the conduit to the enclosure. The insulated throat protects the conductors.3. The sealing washer is used outside the enclosure, between the hub and the enclosure wall, to create a raintight seal.4. Inside the enclosure, the conductors are properly terminated with insulated connectors.
Important Note:* Electrical work can be dangerous. If you're not completely confident in your ability to perform the work safely and according to code, hire a qualified and licensed electrician. This is especially true when dealing with live circuits. Flag for review