Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Water heater breaker sizing

User: hhsting, Location: Glen bunie, md, us

Asked on: Wednesday, August 7, 2024 at 10:41 am EDT
Answered on: Thursday, March 6, 2025 at 12:51 am EST

Question: I have water heater 277V single phase 2kW. Engineer has provided 20A breaker. Says in manufacturer install instruction there is no breaker size listed and breaker size of 20A is compliant.Should not the breaker size be 15A? Is the engineer correct or incorrect?

The engineer is likely correct, but let's break down the reasoning and considerations

1. Calculating Current Draw:
Watts = Volts x Amps (P = V x I) Amps = Watts / Volts (I = P / V) Amps = 2000 Watts / 277 Volts Amps = 7.22 Amps2. NEC (National Electrical Code) Considerations



125% Rule for Continuous Loads

Water heaters are generally considered continuous loads because they can operate for 3 hours or more at a time. The NEC requires that the circuit conductors and overcurrent protection device (breaker) be sized for 125% of the continuous load.


Calculation for 125%

7.22 Amps x 1.25 = 9.03 Amps

3. Standard Breaker Sizes and Conductor Ampacity

Common breaker sizes are 15A, 20A, 30A, etc. The conductors (wires) must be rated to handle at least the 125% continuous load calculation (9.03 Amps in this case). Typically, #12 AWG copper wire would be suitable for a 20A breaker, but you should verify with your local code requirements and the wire's insulation type. #14 AWG copper wire would be adequate for a 15A breaker.

4. Why the 20A Breaker is Likely Acceptable



NEC allows for the next standard size

The 125% calculation yields 9.03 Amps. The NEC allows you to use the
next higher standard breaker size if the calculated value doesn't perfectly match a standard breaker size, provided the wire size is appropriate.

Manufacturer's Instructions

Since the manufacturer doesn't specify a minimum breaker size, they are likely comfortable with a 20A breaker.

Wire Size

If the engineer specified #12 AWG wire (or larger), then a 20A breaker is acceptable.

5. Why a 15A Breaker Might
Not Be Ideal

While a 15A breaker could technically work based on the 7.22 amp draw, it leaves very little headroom. It could potentially nuisance trip, especially as the heating element ages or if there are voltage fluctuations. It would be less compliant with the 125% rule.

Important Considerations and Things to Verify



Wire Size



This is the most critical factor.
Confirm with the engineer or electrician exactly what size wire is being used for the circuit. If it's #14 AWG copper, then a 20A breaker is too large and could create a fire hazard. If it's #12 AWG copper, then the 20A breaker is fine. Local Codes

Local electrical codes may have stricter requirements than the NEC. Make sure your installation complies with all local regulations.


Voltage Drop

While less likely with a short run, a long wire run to the water heater could experience significant voltage drop. This would increase the current draw and could potentially cause the 15A breaker to trip.

Manufacturer Clarification

While the engineer stated there is no breaker listed, it would be best to contact the water heater manufacturer if possible and ask directly about their recommended breaker size, given your voltage (277V).

In summary:


The engineer's recommendation of a 20A breaker is
likely correct, provided the wiring is appropriately sized for a 20A circuit*. You MUST verify the wire size. If #14 AWG wire is used, you must change the breaker to 15A. If #12 AWG (or larger) is used, then the 20A breaker is acceptable and might be preferable to avoid nuisance tripping.It's always best to err on the side of caution and ensure that the installation is safe and compliant with all applicable codes and regulations. If you are still unsure, consult with a qualified electrician. Flag for review

Previous Question Next Question