Question: Hi,How do I determine if I have to go by 30C or 40C ambient temperature table (tables in the thread line) if I have 37C ambient temperature?For an outdoor installation of photovoltaic DC conductors, how do I determine the ambient temperature? Do I take the average of year-around temperatures in the specific city?Thank you!
Let's break down how to handle ambient temperature calculations for your photovoltaic DC conductors, especially when dealing with temperatures between standard table values and outdoor installations.1. Interpolation Between 30°C and 40°C Tables Understanding the Tables
The 30°C and 40°C tables are used to determine the ampacity (current carrying capacity) of conductors based on their insulation type and the surrounding ambient temperature. A higher ambient temperature means the conductor will operate hotter, requiring a lower ampacity to prevent overheating and insulation degradation.
Interpolation for 37°C
Since your ambient temperature of 37°C falls between 30°C and 40°C, the most accurate method is to
interpolate between the ampacity values in the two tables. Here's how:1. Find Ampacities
For the specific conductor you're using (gauge, insulation type, installation method), look up the ampacity in both the 30°C and 40°C tables.2.
Calculate the Difference
Subtract the 40°C ampacity from the 30°C ampacity. This gives you the ampacity reduction over a 10°C range.3.
Determine Proportion
You are 7°C above 30°C (37°C - 30°C = 7°C). Divide this difference by 10°C (7°C / 10°C = 0.7). This means you're 70% of the way between the two temperatures.
4.
Calculate Adjustment
Multiply the ampacity difference (from step 2) by the proportion (from step 3). This is the amount you need to subtract from the 30°C ampacity.5.
Final Ampacity
Subtract the adjustment (from step 4) from the 30°C ampacity. The result is your interpolated ampacity for 37°C.
Formula
Here's a consolidated formula:Ampacity @ 37°C = Ampacity @ 30°C - [(Ampacity @ 30°C - Ampacity @ 40°C) (37°C - 30°C) / (40°C - 30°C)]
Example
Let's say a specific conductor has an ampacity of 50A at 30°C and 45A at 40°C. Difference: 50A - 45A = 5A Proportion: 7°C / 10°C = 0.7 Adjustment: 5A 0.7 = 3.5A Ampacity @ 37°C: 50A - 3.5A = 46.5A Therefore, you would use 46.5A as the ampacity for this conductor in your calculations.
Conservative Approach
If you want to be extra conservative (and it's often a good idea for safety), you could just use the 40°C ampacity. This will ensure the conductor never exceeds its temperature rating, but it may lead to using a larger gauge wire than strictly necessary.
2. Determining Ambient Temperature for Outdoor PV Installations
This is a crucial and sometimes complex aspect. You cannot simply use the average annual temperature. Here's why and what to do instead: Why Average Temperature is Insufficient
The average temperature doesn't account for the peak temperatures that the conductors will experience. Conductors need to be sized for the highest temperatures they'll encounter.
NEC Requirements and Considerations
The NEC (National Electrical Code) provides guidance. Look at:
NEC 690.8(A)(1)(a) and (b)
This section addresses the calculation of maximum circuit current for PV systems, which is related to temperature.
NEC 310.15
This covers ampacity calculations in general, including ambient temperature corrections.
Methods for Determining Ambient Temperature
Historical Weather Data (Most Accurate)
Obtain historical temperature data for the specific location of your installation. This data should ideally cover several years (e.g., 10 years or more). Look for the maximum recorded temperature during the warmest months. Reliable sources include:
National Weather Service (NWS)
In the US, the NWS provides detailed historical weather data.
Local Weather Stations
Often, local airports or universities maintain weather records.
ASHRAE (American Society of Heating, Refrigerating and Air-Conditioning Engineers)
ASHRAE provides detailed climate design data for many locations, useful for engineering applications. Use this maximum recorded temperature (or a value slightly above it, as a safety factor) as your ambient temperature.2.
Temperature Adders Based on Installation Method (NEC Table 310.15(B)(3)(c) etc.)
The NEC provides a table with adders to the measured ambient temperature if your wiring is installed on or above a roof. The temperatures can rise drastically above the ambient temperature on the roof. These temperature adders must be accounted for.
Important
These adders are added to the ambient temperature you determined in step 1.
Example
If you measured 45C in Step 1 as the peak ambient temperature, and Table 310.15(B)(3)(c) recommends a 30C adder, you would use 75C.
3.
Engineering Judgement (Use with Caution)
In some cases, you might need to use engineering judgment if precise historical data is unavailable. Consider the following:
Location
Is the site near a large body of water (moderating effect) or in a desert (extreme temperatures)?
Elevation
Higher elevations tend to have lower temperatures.
Surface Reflectivity
Light-colored surfaces reflect more sunlight, reducing the heat absorbed. Dark surfaces absorb more heat.
Ventilation
How well-ventilated is the area where the conductors are located? Good ventilation will help dissipate heat. Document your reasoning carefully if you use engineering judgment. It's always best to err on the side of caution.
Practical Considerations
Conductor Placement
Where are the conductors run?
Exposed to Direct Sunlight
Expect higher temperatures. Consider using conductors with a higher temperature rating (e.g., THHN/THWN-2 rated for 90°C).
Conduit on Roof
This is a very harsh environment. Use the NEC temperature adders.
Underneath PV Modules
Temperatures can be high here as well, due to heat radiating from the modules.
Shaded Areas
Temperatures will be lower.
Derating for Multiple Conductors in a Raceway or Bundle
If you have multiple conductors grouped together, they will generate more heat, and you'll need to further reduce their ampacity (derate them) according to NEC tables (e.g., Table 310.15(C)(1)).
Voltage Drop
While not directly related to ambient temperature, voltage drop is another important factor to consider in PV system design. Excessive voltage drop can reduce the system's efficiency. Larger gauge conductors will reduce voltage drop.
In summary
Interpolate between the 30°C and 40°C ampacity values to get a more accurate ampacity for a 37°C ambient.2. Never use average annual temperature for outdoor PV conductor sizing.3. Obtain historical maximum temperature data for your location.4. Consider installation method (NEC Tables for adders).5. Account for derating if you have multiple conductors bundled together.6. Prioritize safety by erring on the side of caution when estimating ambient temperatures. Consult with a qualified electrical engineer or PV system designer for complex installations.Always consult the latest edition of the NEC and local electrical codes for specific requirements and interpretations. Flag for review