Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Reactance Questions on Conductors

User: wwhitney, Location: Berkeley, CA

Asked on: Wednesday, August 7, 2024 at 12:36 pm EDT
Answered on: Thursday, March 6, 2025 at 12:51 am EST

Question: NEC Chapter 9 Table gives reactances for "3-Phase, 60 Hz . . . Three Single Conductors in Conduit." The notes say "capacitive reactance is ignored," so this is an inductive reactance. A few questions:1) For PVC conduit, I take it this is the impedance attributable to the current in one of the 3 conductors inducing an opposing current in the other two conductors (in aggregate, for all pairs of conductors). How would these values change for a single phase 2-wire circuit, or the case of a 3P4W wye supply, or a 3P3W supply plus a wire type EGC, or 6 conductors for 2 parallel sets on a 3P3W supply?2) For steel conduit we get a higher reactance than PVC. If we have a wire type EGC as a 4th conductor in the conduit, how will the 60 Hz reactance change if that steel conduit is bonded to the wire type EGC at 0 ends, 1 end, or 2 ends? [0 ends, of course, is usually an NEC violation.]Thanks,Wayne

Let's break down the inductive reactance values in NEC Chapter 9 and address your excellent questions.

Understanding Inductive Reactance in this Context

The inductive reactance values in NEC Chapter 9, Table 9 (and similar tables) primarily account for the external inductance of the conductors. This inductance arises from the magnetic field created by the current flowing in each conductor. When multiple conductors are grouped together, their magnetic fields interact, affecting the overall inductance and, therefore, the inductive reactance. It's NOT primarily due to inducing an opposing current within the other conductors, although that's a component of the overall effect. Think of it as the magnetic field produced by one wire influencing the magnetic field around the other wires.1) Reactance Variation with Different Circuit Configurations in PVC Conduit Single-Phase, 2-Wire Circuit

The inductive reactance will be
significantly lower than the values listed for 3-phase. The NEC table is specifically for 3-phase systems where the interaction of the three phase currents significantly contributes to the magnetic field interaction. With only two conductors, the magnetic field interaction is reduced. You would need to recalculate the inductive reactance based on the geometry and conductor spacing. Empirical formulas or specialized calculators (often from conductor manufacturers) are the best way to get these values. Ignoring this reactance (which is often done in short runs) will typically be conservative in the design.

3-Phase, 4-Wire Wye

This is closer to the conditions in the NEC table, but not identical. The neutral conductor carries the unbalanced current. The inductive reactance will be slightly different than the 3-phase, 3-wire case. The neutral conductor's current will contribute to the overall magnetic field. Again, a detailed calculation would be needed for precise values. In practice, the difference is often small enough to be ignored for most standard installations. If you're dealing with very long runs or critical voltage drop calculations, more precise modeling is necessary.

3-Phase, 3-Wire with Wire-Type EGC

The EGC
should not be carrying current under normal conditions. Therefore, the inductive reactance will be very similar to the 3-phase, 3-wire case. Any slight differences would arise from the presence of the EGC within the conduit affecting the overall geometry and magnetic field distribution. The EGC's primary role is for fault current, not normal operational current.

3-Phase, 3-Wire with Two Parallel Sets (6 Conductors)

This significantly increases the complexity. The inductive reactance will be lower than the values in the NEC table per circuit, but you have two circuits in parallel. You need to account for the mutual inductance between all conductors. Precise calculation is difficult and would likely require specialized software that can model the complex magnetic field interactions. Good practice is to physically install the parallel conductors in a way that minimizes impedance. Using a "grouping method", the parallel set is installed so that the wires from each set alternate through the installed conduit to get optimal impedance. A simple rule of thumb: When running parallel circuits in separate conduits, ensure each conduit contains all the phases to balance the inductive reactance in each.

Key Consideration for PVC

Because PVC is non-magnetic, the inductive reactance is primarily determined by the physical arrangement and spacing of the conductors.

2) Reactance Variation with Steel Conduit and EGC Bonding


Steel conduit's higher reactance compared to PVC arises from eddy currents induced in the steel itself. The changing magnetic field from the conductors induces circulating currents within the steel conduit wall. These eddy currents create their own magnetic fields that oppose the original field, increasing the overall reactance.The bonding of the EGC to the steel conduit drastically affects the behavior:
0 Ends Bonded (NEC Violation)

This is the worst case. The steel conduit forms a long, ungrounded loop. The eddy currents can circulate freely, leading to the highest possible inductive reactance and significant voltage drop. It also creates a hazard since fault current has no low-impedance path back to the source.

1 End Bonded

This provides
some improvement. The bonding allows some fault current to return through the conduit, reducing the circulating eddy currents to some degree. The inductive reactance will be lower than the 0-ends-bonded case, but still higher than the 2-ends-bonded case. This is NOT a code compliant install.

2 Ends Bonded

This is the ideal situation (and NEC requirement). Bonding at both ends provides a low-impedance path for fault current to flow through the conduit, in parallel with the EGC. This significantly reduces the circulating eddy currents in the steel, resulting in the lowest inductive reactance. The magnetic fields from the conductors tend to cancel out more effectively, further minimizing the reactance.

In Summary - Steel Conduit and EGC Bonding

Proper bonding (at both ends) reduces inductive reactance in steel conduit. The conduit and EGC effectively act as parallel conductors for fault current, improving safety and reducing voltage drop during fault conditions.

Important Considerations and Cautions



NEC Tables are Approximations

The values in the NEC tables are
typical values for specific configurations. Actual reactance can vary based on conductor size, spacing, and manufacturing tolerances.

Voltage Drop Calculations

Inductive reactance is crucial for accurate voltage drop calculations, especially in long runs or when using smaller conductors.

Software Tools

For complex circuit configurations or critical applications, use specialized electrical engineering software to accurately model the inductance and reactance.


Impedance vs. Reactance:
Remember that impedance includes both resistance and reactance. Resistance is usually more significant than reactance in shorter runs, but reactance becomes more important in longer runs, especially with larger conductors.Always consult the latest edition of the NEC and consult with a qualified electrical engineer for specific applications. The information here is for educational purposes only and should not be considered a substitute for professional advice. Flag for review

Previous Question Next Question