Topic: Multimotor and 120v OCP sizing

User: Tbatson44, Location: Springfield, MO

Asked on: Wednesday, August 7, 2024 at 4:49 pm EDT
Answered on: Thursday, March 6, 2025 at 12:52 am EST

Question: I have a motor control cabinet fed 240VAC 3phase controlling 6 motors and then 1 - 120VAC (L1 to Neutral) load but I'm not seeing proper calculation for OCP. I am getting caught up with 430.53(B) and it saying this must be sized for the most severe normal conditions. Do I just size this to protect the conductors so 125% of the largest motor plus the sum of all the others? I have 3 - 15hp motors, and 3 - 10hp motors, then L1-N for my 120VAC load.Thank you.

Okay, let's break down the overcurrent protection (OCP) calculation for your motor control cabinet according to the NEC, focusing on 430.53(B) and addressing the "most severe normal conditions" aspect.

Understanding the Code Section - 430.53(B) Several Motors or Motor(s) and Other Load(s).

This section deals with a single overcurrent device protecting multiple motors or a combination of motors and other loads (like your 120V circuit). The key is to size the OCPD so that it can:1. Carry the starting current of the largest motor. This is where the "most severe normal conditions" part comes in. The highest current demand will be when the largest motor starts.2. Carry the full-load current of all the other motors and other loads.3. Protect the conductors from overcurrent.Step-by-Step Calculation1. Determine Full Load Amps (FLA) for each motor

You'll need to look this up in NEC Table 430.250 (Three-Phase AC Motors) and 430.248 for the single phase 120V motor. These tables provide FLA values based on horsepower and voltage.

15 HP @ 230V (Use 230V value, it is close)

Consult Table 430.250. This looks to be roughly 42A each


10 HP @ 230V

Consult Table 430.250. This looks to be roughly 28A each.

Other 120V Loads

I don't know what this value is since I don't know the loads, but the calculation will be (Watts/120V) to get the current draw.2.

Calculate the OCPD Size



Largest Motor Contribution (15 HP)

Take the FLA of the largest motor (42A) and multiply it by the 250% as the standard start up OCP multiplier (NEC 430.52). This gives us 105A.

Sum of Remaining Motor FLAs

Add up the FLA of the remaining motors: (2 x 42A) + (3 x 28A) = 84A + 84A = 168A.


Add the FLA from your 120V load

Let's say you have a 120V load of 1500W this would be 1500W/120V = 12.5A

Total OCPD Size (Initial Calculation)

105A + 168A + 12.5A = 285.5A3.

Conductor Ampacity Check

Before you finalize the OCPD size, you

must
ensure that the conductors feeding the cabinet are adequately sized. Conductor Ampacity Calculation

125% of the largest motor FLA: 1.25 42A = 52.5A Sum of all other motor FLAs: (2 x 42A) + (3 x 28A) = 168A 120V Load: 12.5A Total conductor ampacity required: 52.5A + 168A + 12.5A = 233A

Conductor Sizing

Select conductors based on the ampacity required (233A) from NEC Table 310.16 (or the appropriate table for your conductor type and installation method). Remember to apply any derating factors for ambient temperature, number of conductors in a raceway, etc.
4.


Coordination and Adjustments



Standard OCPD Sizes

The calculated OCPD size (285.5A) is likely not a standard size. You can go up to the
next higher standard size (NEC 240.6) if the calculation doesn't fall exactly on a standard size. So round up to 300A

Exception if the OCPD won't let the motor start

If the 300A OCPD trips during the starting of the largest motor, NEC 430.52(C)(1) Exception No. 1 allows you to increase the OCPD size, BUT ONLY IF it's necessary to allow the motor to start and run normally.

Document this justification carefully.
Important Considerations and Cautions



Motor Nameplate

The actual FLA values on the motor nameplates take precedence over the NEC tables.
Always check the motor nameplates.

Service Factor

If the motors have a service factor greater than 1.15, you may need to adjust the FLA used in the calculations.

Continuous Duty

Motors used for continuous duty need careful consideration of their thermal characteristics.


Other Loads

Be absolutely sure you've accounted for all other loads within the cabinet (e.g., control transformers, lighting, etc.).

Short-Circuit Current Rating (SCCR)

Ensure that the components in the motor control center have an appropriate SCCR to withstand potential fault currents. This is a critical safety aspect. You'll need to do a proper SCCR calculation.

Example Summary (Based on Assumptions)

Largest Motor (15 HP): 42A FLA OCPD Calculation: (42A 250%) + (2 42A) + (3 28A) + 12.5A = 300A (after rounding up) Conductor Ampacity Requirement: 233A Select conductors rated for 233A or higher (after derating). Select a 300A overcurrent protective device. VERIFY ability of components to handle the available fault current (SCCR rating).

Disclaimer:
I am an AI Chatbot. This information is for guidance only and should not be considered a substitute for professional electrical engineering advice. Consult with a qualified electrical engineer for accurate calculations, code compliance, and safe design. Improper electrical design can be dangerous and potentially fatal. Flag for review