User: jot30, Location: Berkeley, CA
Asked on: Wednesday, August 7, 2024 at 4:54 pm EDT
Answered on: Thursday, March 6, 2025 at 12:52 am EST
Question: Trying to understand if code allows you to eliminate one electrode (rod) if you have a UFER installed. Excerpts are from the 2020 NEC...Some background our utility provider requires a rod at the meter. All our water services are copper and all new residential builds require a UFER. So "present - 250 .50" would be Rod, Water, UFER.(underlines by me250.50 Grounding Electrode System.All grounding electrodes as described in 250.52(A)(1) through (A)(7) that are present at each building or structure served shall be bonded together to form the grounding electrode system.250.53 Grounding Electrode System Installation.(2) Supplemental Electrode Required.A single rod, pipe, or plate electrode shall be supplemented by an additional electrode of a type specified in 250.52(A)(2) through (A)(8). The supplemental electrode shall be permitted to be bonded to one of the following:Exception:If a single rod, pipe, or plate grounding electrode has a resistance to earth of 25 ohms or less, the supplemental electrode shall not be required.(D) Metal Underground Water Pipe.If used as a grounding electrode, metal underground water pipe shall meet the requirements of 250.53(D)(1) and (D)(2).(2) Supplemental Electrode Required.A metal underground water pipe shall be supplemented by an additional electrode of a type specified in 250.52(A)(2) through (A)(8). If the supplemental electrode is of the rod, pipe, or plate type, it shall comply with 250.53(A).250.52 Grounding Electrodes.(A) Electrodes Permitted for Grounding.(3) Concrete-Encased Electrode.So as mentioned, our utility requires a rod at the meter and in reading the code both water and rod type electrodes shall be supplemented by an additional electrode. Question - can the UFER be the additional required electrode for both the rod and water present or is an additional supplemental electrode required for each (water and rod).
Okay, let's break down the NEC requirements and address your specific scenario.
The Core Principle: Bonding Together All Available Electrodes
Section 250.50 is the most important starting point. It mandates that all grounding electrodes present at a building must be bonded together to form the grounding electrode system. This means you can't simply pick and choose which electrodes to use and ignore others. If they're there, they must be connected.
Addressing Your Scenario: UFER, Water, and Rod
You have three grounding electrodes present:1. UFER (Concrete-Encased Electrode)
This is defined in 250.52(A)(3).
2.
Metal Underground Water Pipe
This is defined in 250.52(A)(1) (assuming it meets the specific requirements outlined there).
3.
Rod Electrode
This is defined in 250.52(A)(5).Based on 250.50, all three of these must be bonded together. You're correct in assuming "present - 250.50" would be Rod, Water, UFER
Analyzing Supplemental Electrode Requirements
This is where the confusion often arises.
Water Pipe
Section 250.53(D)(2) explicitly requires the water pipe to be supplemented by an additional electrode from 250.52(A)(2) through (A)(8).
Rod Electrode
Section 250.53(A)(2) explicitly requires the rod electrode to be supplemented by an additional electrode from 250.52(A)(2) through (A)(8).
Can the UFER Serve as the Supplemental Electrode for BOTH the Water Pipe and the Rod?Yes, it can. Here's why: The UFER is a permitted electrode type specified in 250.52(A)(3). The UFER, being present, is already part of the grounding electrode system as mandated by 250.50. Since the UFER is present and bonded to both the rod and the water pipe, it fulfills the "supplemental" requirement for both.
Key Takeaway
Because you have all three electrodes present, the UFER acts as the supplemental electrode required for both the water pipe and rod in accordance to the code.
In Summary: Your Installation MUST include
1. A rod electrode at the meter (per utility requirement).
2. A metal underground water pipe connected to the grounding system within the building.3. A UFER electrode installed during construction.
4. A grounding electrode conductor (GEC) connecting all three of these electrodes together to form a single grounding electrode system. This connection will typically be made at the service equipment.
Important Considerations and Best Practices
Continuous Metallic Water Pipe
Make sure the metal water pipe is electrically continuous. Non-conductive couplings or sections can invalidate it as a grounding electrode.
Bonding Jumpers
Consider using bonding jumpers to bypass any potential discontinuities in the water pipe, especially around meters or plastic fittings.
GEC Sizing
Ensure the grounding electrode conductor (GEC) is sized appropriately based on the size of the service entrance conductors, per NEC Table 250.66. The GEC needs to be able to handle fault current.
Utility Requirements
Always confirm your interpretation with your local electrical inspector. Local jurisdictions can sometimes have specific interpretations or amendments to the NEC. The utility requirements also need to be considered.
Resistance to Earth
Even though the exception for the rod is there, you would still need to install a rod in accordance to the utility requirements.
Example:
Imagine your service entrance conductors are sized such that you need a #4 AWG copper GEC. You would run that #4 AWG copper conductor from the service equipment (main panel) to a point where you can bond to: The UFER rebar (using a listed connector) The metal water pipe (within 5 feet of entry into the building, if possible, and before any insulated couplings)* To the grounding bus in the meter enclosure where the rod electrode GEC connects.By following these principles and confirming with your local authorities, you'll have a safe and code-compliant grounding electrode system. Flag for review