Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: 208v lift motor circuit.

User: jklr, Location: Miss

Asked on: Wednesday, August 7, 2024 at 6:11 pm EDT
Answered on: Thursday, March 6, 2025 at 12:52 am EST

Question: Hello,We are on the 2014 NEC and I will be hooking up a lift at a maintenance shop and the specs for the motor are as follows:3HP208-240vFLA 12.9/14.4Rpm 2880/3450SFA 1.1Max Amb °C 40For the OCPD IAW 430.5212.9amps x 300% = 38.7 ampsI plan on installing a 30amp breaker.IAW Table 430.248 and 310.15(b) (16) 75° column208V 3hp motor shows 18.7 amps for the FLC.18.7 X 110% = 20.57amps (I BELIEVE IT WOULD FALL UNDER THE SHORT DUTY)Using 12 awg as the motor feeders and branch circuit conductors.The conduit run is approx 200ft and I plan on installing another 30amp breaker at/near the lift to serve as disco means.The motor does not have overload protection, but looking at 430.33 since it is short duty an overload is not required.I know this is a lot but again I am new to the commercial side of things and trying to figure things out on my own first before I ask for help/corrections.Thanks.

Okay, let's break down your calculations and assumptions under the 2014 NEC for your lift motor installation. I'll highlight areas where adjustments might be needed and explain the reasoning.

Here's a review of your approach, with corrections and considerations



1. Overcurrent Protection (OCPD) - 430.52
Your Calculation

12.9 amps (FLA) x 300% = 38.7 amps. You plan to use a 30A breaker.


Analysis

Your calculation is correct in principle for determining the maximum allowable OCPD size. You are using 300% based on assuming that the motor is not a design E motor and that the code allows for an inverse time breaker. However,

300% is only the MAXIMUM allowed.
You must start with the lowest OCPD that will allow the motor to start, then move up in size only as necessary, based on the specific motor and load. You should check the breaker trip curve to see if you can get the motor started with the 30 amp breaker. Important

You're on the right track considering the
maximum allowed. Code language specifically states "The overcurrent protection shall not exceed the percentage specified in Table 430.52."

Suggestion

Start with a smaller breaker. As long as you have verified the starting/tripping issue with the 30 amp breaker, I would start with a 25 amp breaker.

2. Conductor Sizing - Table 430.248 & 310.15(B)(16) and 430.22
Your Calculation

Using Table 430.248 (FLC for 208V 3HP motor = 18.7 amps). 18.7 amps x 110% = 20.57 amps. You are considering this "short duty". Using 12 AWG conductor.


Analysis

You are correct to reference Table 430.248. Using the FLC from the table is correct for calculating the minimum ampacity of your conductors. 430.22(A).

Short Duty Consideration

Here's where you need to be careful. Assuming short-duty, intermittent, periodic, or varying duty, you need to consult Table 430.22(E) for the multiplier. You need to determine the exact duty cycle to apply the correct percentage factor.


12 AWG ampacity

Per 310.15(B)(16) using the 75°C column, 12 AWG copper is typically rated for 25 amps. If the multiplier from table 430.22(E) is less than 1.0, then you can use the lower ampacity conductor.

Suggestion

You need to know the exact duty cycle to know the multiplier from table 430.22(E).

3. Voltage Drop
The Need

At 200ft, voltage drop is a VERY important consideration. Motors are sensitive to low voltage.

Calculation Required

You need to calculate the expected voltage drop using the 18.7A load (or the duty cycle adjusted load) on the 12 AWG conductor over 200ft. Use a voltage drop calculator (many are available online). Aim for a voltage drop of no more than 3% at the motor terminals under full load.


Consequences of Excessive Voltage Drop

Motor overheating, reduced torque, failure to start, and potential damage.

4. Disconnect
Your Plan

30A breaker at/near the lift as a disconnect.


Analysis

This is generally acceptable if the breaker meets the requirements for a disconnect per 430.109. Critically, it must be lockable in the open position (430.102(B)). Check the breaker manufacturer's specifications.

Ampacity

The disconnect must have an ampacity not less than 115% of the motor's nameplate full-load current rating.


Alternative

A fused disconnect switch is also a valid option.

Suggestion

Ensure the 30A breaker you use is suitable as a disconnect switch, specifically regarding lockability. If the motor is ever to be maintained, it needs a proper disconnect.

5. Motor Overload Protection - 430.33
Your Assumption

Not required due to "short duty."

Analysis

This is potentially incorrect, and the riskiest part of your analysis.

You cannot automatically assume overload protection is not needed solely based on "short duty."
You must meet the conditions of 430.33 exactly. That section only allows you to omit overload protection if the motor cannot be damaged due to overload or failure to start. This is rare! Most lift motors will be damaged if they are overloaded or fail to start. Just because it's "short duty" doesn't inherently mean overload protection is not required. Typical Requirement

Most motors require overload protection per 430.32. This is typically achieved with an overload relay built into the motor starter.

Consideration

If the motor
does require overload protection (highly likely), you need to follow the requirements of 430.32. This involves selecting an overload relay sized appropriately for the motor's FLA.

Suggestion



Assume you need overload protection unless you can prove that the motor is designed to withstand any overload condition and starting failure without damage.
Consult the motor manufacturer's specifications.6. Conduit Fill Consideration

Ensure your conduit fill (number of conductors in the conduit) complies with Chapter 9 and Annex C.

Summary of Key Considerations & Recommendations
1. Voltage Drop

Calculate voltage drop. This is the MOST LIKELY issue with a 200ft run. You may need to increase conductor size.2.

Overload Protection

Assume you need overload protection per 430.32 unless you have documentation from the motor manufacturer stating that the motor cannot be damaged by overload.3.

Duty Cycle

Determine the
exact* duty cycle to use the correct multiplier in Table 430.22(E).
4.


OCPD

You may need to change the overcurrent device so the motor starts, or move down to a lower one like a 25amp breaker so you are not oversizing the protection.5.

Disconnect

Ensure your 30A breaker meets the requirements of a disconnect (lockable open).6.

Local Codes

Always check for any local amendments or requirements that might be stricter than the NEC.

Disclaimer:
I am an AI chatbot and cannot provide official electrical code interpretations or engineering advice. This information is for educational purposes only. A qualified, licensed electrician must be consulted for all electrical work. Flag for review

Previous Question Next Question