User: dissonant, Location: Honolulu, HI
Asked on: Thursday, August 8, 2024 at 6:02 am EDT
Answered on: Thursday, March 6, 2025 at 12:53 am EST
Question: I'm designing a small apartment building with overhead service continuing from the the front of the building to a group metering location by way of the parking garage ceiling. The permitting office reviewer has flagged the design stating it doesn't comply with NEC 230.3. This is one building and not a separate structure, so not sure how it could be read this way. Anyone see any issue with installing the service this way?
You're right to question the reviewer. NEC 230.3 primarily deals with one building or other structure and the requirement of one service. The crux of the issue likely lies in how the reviewer interprets the overhead service run through the parking garage ceiling.Here's a breakdown of why the reviewer might be flagging it, and how to address their concerns
Possible Interpretations Leading to the Flag:
1. "Separate Structure" Argument
Even though it's all one building, the reviewer might be arguing that the parking garage area (especially if it's somewhat isolated or has a different function) constitutes a "separate structure" for the purpose of service location. This is a stretch, but some reviewers are overly cautious.2.
Accessibility and Working Space
The reviewer might be concerned about accessibility and working space around the service conductors and metering equipment located in the parking garage. If the installation doesn't provide adequate clearance and working space per NEC Article 110, that could be a valid concern (although not directly related to 230.3).
3.
Protection from Physical Damage
Running overhead conductors through a parking garage could raise concerns about physical damage from vehicles or other objects. This falls under general wiring methods and protection requirements, not specifically 230.3.
4.
Lack of Service Disconnect Means in an Acceptable Location
While the service conductors are allowed to pass through the building, 230.70(A)(1) requires the service disconnecting means to be installed at a readily accessible location either outside the building or nearest the point of entry of the service conductors. If the service panel with the disconnects is located deep within the building, the reviewer may be concerned that the service disconnects are not near the point of entry.
How to Address the Reviewer's Concerns
Clarify the Scope
The most important step is to talk to the reviewer directly and
understand their specific concern related to NEC 230.3. Don't just guess what they're thinking. Ask for the exact section they believe is being violated and why.
2. Reinforce It's One Building
Emphasize that the parking garage is an integral part of the apartment building, not a separate structure. Provide architectural drawings or other documentation to support your assertion.3.
Addressing Accessibility/Working Space
Demonstrate that the installation meets all accessibility and working space requirements of NEC Article 110. Provide details of clearances around the metering equipment and any disconnects located in the garage.
4.
Addressing Physical Damage
Show how the service conductors will be adequately protected from physical damage in the parking garage. This might involve using rigid conduit, cable trays with covers, or other appropriate methods. Document that the installation meets any applicable requirements for protection against mechanical damage per NEC Article 300.5.
Address location of disconnect means If the service disconnects are located deep in the building, the reviewer may be concerned that the service disconnects are not near the point of entry as described in 230.70(A)(1). Consider including a service disconnect adjacent to the meters in the parking garage to resolve this issue.
6. Provide Detailed Drawings
Submit detailed drawings that clearly show the routing of the service conductors, the location of the metering equipment, the disconnect means (if any), and any protective measures you're taking. Include information on conductor size, conduit type, and other relevant details.7.
Appeal (if Necessary)
If you can't resolve the issue with the reviewer, you have the right to appeal their decision. Be prepared to present your case clearly and concisely, with supporting documentation.
In summary: Talk to the reviewer, understand their specific objections, and provide detailed documentation to address those concerns. It's highly likely the issue isn't directly with 230.3 itself, but rather with interpretations related to separate structures, accessibility, protection from damage, or location of the service disconnect. A proactive and collaborative approach will usually lead to a resolution. Good luck! Flag for review