Topic: Meter / Main combo and no EGC running to sub-panel?

User: Indian_Rdr, Location: St. Louis

Asked on: Thursday, August 8, 2024 at 6:56 am EDT
Answered on: Thursday, March 6, 2025 at 12:53 am EST

Question: The utility around here is telling us we CAN NOT run an EGC from the new meter / main combos to the house panel. This has me confused. Aren't these now feeders going to a sub-panel since the bonding of GEC and neutral is in the combo along with first means of disconnect (200a breaker in combo)? They are telling us to run the EGC to rebar or copper tubing only.So then what happens when rebar is not provided (it's not required here for contractors to do this) and it's plastic coming in from outside for water? Ground rod 6' away?

Okay, let's break this down. What your utility company is telling you is, at face value, contrary to common understanding of the NEC and typical grounding/bonding practices for residential services with a meter-main combo. Let's clarify the situation

Understanding the Setup: Meter-Main Combo as Service Equipment
Service Equipment

The meter-main combo, with its 200A breaker (your "first means of disconnect"),
is considered the service equipment. This is the critical point.

Service Disconnect

The 200A breaker is the service disconnect.

Bonding

By definition, the neutral-to-ground bond
must occur in the service equipment.

Feeders

Any conductors running from the service equipment (meter-main) to your house panel are considered feeders, regardless of distance.

Subpanel

Your house panel is now, effectively, a subpanel.

The Core Issue: EGC Requirement for Feeders
NEC Mandates EGC

The NEC requires an equipment grounding conductor (EGC) to be run with the feeder conductors from the service equipment (meter-main) to the subpanel (house panel). This is essential for safety.

No Neutral-Ground Bond at Subpanel

Because the house panel is now a subpanel, the neutral and ground conductors
must be kept separate, and there must not be a neutral-to-ground bond at the house panel.

Why the EGC is Crucial


The EGC provides a low-impedance path for fault current to return to the source (the transformer), allowing the breaker to trip quickly in the event of a ground fault. This minimizes the risk of electric shock and fire.

What the Utility is Saying is Problematic

The utility's instruction to
not run an EGC and to only connect to rebar or a ground rod is

not code-compliant
for the feeder to the house. Here's why: Ground Rods are Supplemental

Ground rods or rebar are part of the grounding electrode system (GES), which is intended to stabilize voltage to earth. They are not a substitute for the required EGC for clearing faults.

High Impedance

Relying solely on earth as the fault current path creates a high-impedance path, which may not trip the breaker quickly enough.


Safety Hazard

In the event of a ground fault, relying on a high-impedance path can create dangerous voltage on grounded metal parts.

Addressing Specific Scenarios



No Rebar

If rebar is not available, you need to install the code-required grounding electrodes. This can include ground rods, a ground ring, or other methods as specified in NEC Article 250.


Plastic Water Pipe

Plastic water pipe is not a suitable grounding electrode. You cannot rely on it for grounding.

Recommended Actions


Code Requirements

NEC requires the neutral and grounding bars to be separated, and the grounding bars bonded to the panel enclosure with a grounding wire. The ground wire from the meter main combo (feeder) lands here.2.

Document Everything

Make detailed notes of your conversations with the utility, including the date, time, and the name of the person you spoke with. This documentation is essential.3.

Seek Clarification and Documentation from the Utility

Politely but firmly request the specific code section that supports their requirement. Ask for a written statement or policy document outlining their position on EGCs for meter-main combos.4.

Involve the Local Electrical Inspector

This is critical. Explain the situation to the local electrical inspector (the AHJ - Authority Having Jurisdiction). The inspector has the final say on code compliance. Show them the documentation from the utility. They can clarify the requirements and ensure the installation is safe and compliant. The utility cannot override code.5.

Escalate if Necessary

If the utility continues to insist on a non-compliant installation, and the local inspector supports you, you may need to escalate the issue within the utility company. Speak to a supervisor or manager.6.

Do NOT Proceed with a Non-Compliant Installation

Do not proceed with the installation if it violates the NEC and puts you at risk of electrical shock or fire.

In Summary:


The utility's instruction to not run an EGC from the meter-main combo to the house panel is likely incorrect and non-compliant with the NEC. Your house panel is now a subpanel, and the NEC requires an EGC to be run with the feeder conductors. You need to resolve this issue with the utility and the local electrical inspector before proceeding with the installation. Safety should always be the top priority. Flag for review