Topic: CT rated

User: Cstreeper, Location: PA

Asked on: Thursday, August 8, 2024 at 9:59 am EDT
Answered on: Thursday, March 6, 2025 at 12:54 am EST

Question: Is insulation level of CT 720 VAC line/3kVAC suffice for CT used in 15kV SWgr? I have a 15kV SWGR w CT MR 600A/5A CL C200. I don't understand the insulation level, or how it's rated to work with SWGR.

No, a CT with an insulation level designed for a 720VAC line/3kVAC test will not be suitable for use in a 15kV switchgear. Here's why, and a breakdown of the important insulation ratings

Understanding CT Insulation Levels

CT insulation is designed to withstand specific voltage stresses without breakdown. These stresses come from two main sources: System Voltage

The continuous voltage of the power system where the CT is installed (15kV in your case).


Impulse Voltage

Short-duration, high-voltage surges caused by lightning strikes, switching operations, or other transient events.

Key Insulation Ratings for Medium Voltage Equipment (like your SWGR)
1. Nominal Voltage (kV)

This is the system voltage for which the equipment is designed. In your case, it's 15kV.2.

Maximum System Voltage (kV)

This is the highest permissible operating voltage of the system. It's usually slightly higher than the nominal voltage (e.g., 17kV).3.

Impulse Withstand Voltage (kV BIL - Basic Impulse Level)

This is the peak voltage of a standardized impulse waveform (typically 1.2/50 microsecond) that the equipment can withstand without flashover or insulation breakdown.

This is the most critical insulation rating.
For 15kV SWGR, a typical BIL is 95kV or 110kV.4. Power Frequency Withstand Voltage (kV)

Also called a "one-minute withstand" or "high potential (hi-pot) test". This is the AC voltage (at the system's power frequency, like 60Hz) that the equipment can withstand for one minute without breakdown. This is typically around 34-36kV for a 15kV SWGR.

Why Your 720VAC/3kVAC CT is Unsuitable
Voltage Mismatch

The 720VAC/3kVAC rating indicates this CT is designed for
low-voltage applications (like a 480V or 600V system). The 720VAC is likely the continuous voltage rating, and the 3kVAC is probably the one-minute high potential withstand test voltage for the CT's windings relative to ground. It has absolutely nothing to do with the insulation needed for a 15kV environment.

Massive Underrating

The impulse withstand voltage required for a 15kV switchgear (95kV or 110kV BIL) is drastically higher than anything that a 3kVAC rated piece of equipment could handle. Using the wrong CT would create an insulation failure hazard, likely causing a short circuit or arc flash if exposed to a voltage surge.

How to Select the Correct CT for Your 15kV Switchgear
1. Check the Switchgear Nameplate

The switchgear nameplate should specify the rated voltage, maximum system voltage, BIL, and power frequency withstand voltage.2.

Consult the CT Manufacturer

Provide the CT manufacturer with the following information: Switchgear rated voltage (15kV) Switchgear maximum system voltage (likely around 17kV) Switchgear BIL (95kV or 110kV – critical!) Switchgear Power Frequency Withstand Voltage (34kV or 36kV typical) Your desired CT ratio (600A/5A) Required CT accuracy class (C200 in your case)* Mounting requirements3.

Insist on Certified Testing

Ensure the CT manufacturer provides test reports demonstrating that the CT has been tested to meet or exceed the switchgear's insulation requirements according to relevant standards (e.g., IEEE C57.13).

In Summary


A CT with a 720VAC/3kVAC insulation rating is fundamentally unsuitable for use in a 15kV switchgear. Doing so would create a significant safety hazard. Proper CT selection requires careful consideration of the switchgear's insulation requirements, particularly the BIL. Always consult with a qualified electrical engineer and the CT manufacturer to ensure you select a CT that is appropriately rated and tested for your application. Flag for review