Question: I know when using a single cable in a conduit it can be used as a single conductor at 53% fill correct?What about when it’s just two cables? Am I than stuck at 31% for the “two conductor” fill or do I go ahead and figure for more than two conductors at 40%.Anything over two cables I have always used the 40% .

You're asking about conduit fill percentages for conductors, and specifically when dealing with cables, not individual wires. This is a common source of confusion. Here's the breakdown, keeping in mind we're talking about cables, not individual conductors

Key Point:

The NEC (National Electrical Code) refers to conductors when talking about conduit fill calculations. Cables are treated as single conductors for fill calculations, even though they contain multiple current-carrying wires.

Your question is about using cables in conduit, not individual conductors. Therefore, you only count the number of cables.Here's the correct application of NEC table percentages: One Cable

You are technically correct that the NEC allows 53% fill for a single conductor. In our case it would be a single cable in a conduit.


Two Cables

You are also correct! 31% fill is appropriate for two cables in a conduit.

More than Two Cables

You are correct again! You should use 40% fill for three or more cables in a conduit.

How to Apply the Percentages
1. Determine the Inside Area of the Conduit

Use NEC Chapter 9, Table 4 for the trade size of the conduit you are using. This table gives the inside area in square inches.2.

Determine the Outside Area of the Cable(s)

The outside area is not provided in the NEC. You will need to look at the manufacturer's spec sheet for the exact cable you are using. This is the most important step to get correct dimensions.3.

Apply the Fill Percentage

Multiply the conduit's inside area by the appropriate fill percentage (53%, 31%, or 40%). This gives you the maximum allowable area that your cable(s) can occupy inside the conduit.4.

Compare

Make sure the
total area of your cable(s) does not exceed the maximum allowable area calculated in the previous step.

Important Considerations
Type of Conduit

The conduit fill rules vary based on the type of conduit. The fill percentages we've discussed apply primarily to raceways, such as rigid metal conduit (RMC), intermediate metal conduit (IMC), electrical metallic tubing (EMT), and rigid PVC conduit. Other types of raceways, such as flexible metal conduit (FMC) or liquidtight flexible metal conduit (LFMC), may have different rules, particularly about the number of bends allowed. Always refer to the applicable article in the NEC for the specific conduit type.

Ampacity Derating

Filling a conduit too tightly with conductors generates more heat. The NEC requires you to derate the ampacity of the conductors when there are more than three current-carrying conductors in a conduit.


Future Expansion

It's generally a good practice to not completely fill conduits to their maximum allowable fill. This allows for future expansion or changes.

Proper Lubricant

When pulling cables into conduit, always use a listed wire-pulling lubricant to reduce friction and make the job easier.


Local Amendments

Always check with your local authority having jurisdiction (AHJ) for any local amendments or interpretations of the NEC.

In summary:
Your understanding of the fill percentages for cables is correct. Remember to accurately determine the outside diameter of your cables using the manufacturer's specifications and to account for ampacity derating if you have more than three current-carrying conductors in the conduit. Finally, always consult the latest edition of the NEC and your local AHJ for the most accurate and up-to-date information. Flag for review