Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: VFD OCPD and Feeder Size

User: arc_flashed, Location: FL, United States

Asked on: Thursday, August 8, 2024 at 2:45 pm EDT
Answered on: Thursday, March 6, 2025 at 12:55 am EST

Question: I am looking for some help on sizing the cable between my motor controller, a VFD in this case, and the branch OCPD feeding it. Came across a situation at a customer site where they have a 250HP, 480vac motor fed by a VFD. The VFD is fed by a single set of 500mcm cables which meets the 125% of drive rated current (NEC 430 part X). The issue is the branch OCPD is 800amp fuses which I believe violates table 430.52(C)(1) which should be a max of 175% with time delay fuses (approx 525amps). They said they aren't going to pull more cable to the VFD but may look at changing the fuse to a 600amp.My question is how do you properly size the conductors between the OCPD and the motor starter? Is it based on the 125% of the VFD rated input current or the OCPD? I understand thermal protection is provided by the VFD/starter but it feels wrong to have a single set of 500's on a 600amp OCPD.The second question is the max rating of fuse. NEC seems to limit it to the 525amp mentioned above, but an Allen Bradley VFD lists the max dual element fuse for a 250HP as 675amps.

Okay, let's break down the cable sizing and OCPD selection for a VFD-fed motor, and address your specific questions. This is a common area of confusion, so let's get it clear.

Understanding the Rules NEC 430 (Motors, Motor Circuits, and Controllers)

This is your primary guide. Pay special attention to Part A (General), Part B (Conductor Requirements), and Part C (Overload Protection), and of course, Part X for VFDs.


VFD (Variable Frequency Drive) Considerations

VFDs introduce harmonics and non-sinusoidal waveforms, which can affect conductor heating and OCPD selection.

Conductor Sizing (Between OCPD and VFD)


The conductor sizing between the branch circuit OCPD and the VFD is based on 125% of the VFD's rated input current. This is absolutely critical. You are correct about that. Here's why: NEC 430.122(A) (Conductor Sizing)

States that the conductors supplying the VFD from the branch circuit must have an ampacity not less than 125% of the
VFD's rated input current.

Why not the Motor FLA?
You're not directly wiring to the motor; you're wiring to the VFD. The VFD controls the voltage and frequency supplied to the motor. The VFD is the load you're directly connecting to.

Why not based on the OCPD? The OCPD is there to protect the conductors from
overcurrent and short circuits, not to determine their minimum size for normal operation. The conductors must be sized to carry the expected load (125% of VFD input current) continuously.

Steps for Conductor Sizing


Get the VFD Input Current

This is
not the motor's FLA (Full Load Amps). You must find the VFD's nameplate data or manufacturer's specifications for its rated input current at the supply voltage (480V in your case). The output amps to the motor will be higher than the input due to efficiency losses in the VFD.2.

Calculate Minimum Conductor Ampacity

Multiply the VFD input current by 1.25 (125%). This gives you the
minimum ampacity your conductors must have.3.

Select Conductor Size

Use NEC Table 310.16 (or appropriate tables for your installation conditions – temperature rating, conduit type, etc.) to select conductors with an ampacity
equal to or greater than the value you calculated in step 2. You've used 500 kcmil, which likely meets this, but verify based on the VFD input current. Make sure you are using the correct temperature rating of the conductors (75C or 90C) and the proper derating factors based on the number of current carrying conductors in the conduit.4.

Consider Voltage Drop

While not directly related to NEC code compliance, consider voltage drop. Long runs can lead to voltage drop issues, which can negatively impact motor performance.

Your Specific Situation: Is the 500 kcmil Adequate?


You
must find the VFD's rated input current to determine if the 500 kcmil conductors are properly sized. Don't assume. A 250 HP motor can draw a lot of current, and even with a VFD, the input current could be high enough to require larger conductors.

OCPD Sizing (Branch Circuit Protection)



NEC 430.52 (Motor Branch-Circuit Short-Circuit and Ground-Fault Protection)

This section governs the maximum size of the OCPD. It's designed to protect the branch circuit wiring and components from short circuits and ground faults.

Table 430.52(C)(1)

This table provides the
maximum allowable percentages of the motor's FLC (Full-Load Current) for different types of OCPDs.

Important Caveat for VFDs: 430.52(C)(1) Exception.
There's an exception for VFDs that specifically allows the OCPD to be sized according to the VFD manufacturer's instructions. This is key.Steps for OCPD Sizing


Check VFD Manufacturer's Instructions

This is the first and most important step. The VFD manufacturer may provide specific recommendations for the maximum OCPD size. This often overrides Table 430.52(C)(1) if the VFD is listed for such protection. Allen Bradley listing a 675A fuse sounds like their engineering allows it and they have UL tested to this.2.

If No Specific Instructions (Less Common)

Only if the VFD manufacturer doesn't provide specific instructions, then you fall back on Table 430.52(C)(1) using the motor's FLC. For time-delay fuses, that's typically 175% of the motor FLC.3.

Calculate Maximum OCPD Size

Based on either the manufacturer's instructions or Table 430.52(C)(1), calculate the maximum allowable OCPD size.4.

Select OCPD

Choose an OCPD that is less than or equal to the maximum value you calculated in step 3.

Your Specific OCPD Situation (800A Fuses)



Highly Likely Violation

An 800A fuse is
very likely a violation of NEC 430.52(C)(1) unless the VFD manufacturer specifically allows it. The exception would only apply if this VFD has been tested with this large of a fuse.

Allen Bradley Exception?
You mentioned Allen Bradley listing a 675A fuse. If the specific VFD model you are dealing with is covered by that Allen Bradley documentation, then a 600A or 675A fuse might be acceptable (as long as it still meets the VFD manufacturer's recommendations). If the manufacturer lists a 675, this is the highest you can use. 600A Fuse

Changing to a 600A fuse is a good step, but you
must verify that it meets either the VFD manufacturer's instructions or is less than or equal to 175% of the motor FLC (if the manufacturer provides no guidance).

Answering Your Questions Directly


"How do you properly size the conductors between the OCPD and the motor starter? Is it based on the 125% of the VFD rated input current or the OCPD?"
Conductor sizing is based on 125% of the VFD's rated input current (NEC 430.122(A)). The OCPD size is a limit on the protection, not a determinant of the conductor size.2. "The second question is the max rating of fuse. NEC seems to limit it to the 525amp mentioned above, but an Allen Bradley VFD lists the max dual element fuse for a 250HP as 675amps." NEC (Table 430.52(C)(1)) does provide a limit based on the motor's FLC. However, the VFD Exception in 430.52 allows you to use the VFD manufacturer's recommendations if they exist. The Allen Bradley 675A listing is the key. If that listing applies to the specific VFD in question, then you can use it, up to that maximum.

Important Considerations



Harmonics

VFDs generate harmonics, which can increase conductor heating. Consider using conductors rated for harmonic currents (THHN/THWN with suitable de-rating) or specifying conductors with a higher temperature rating. Many manufactures are now listing THHN/THWN-2 for higher temp ratings.

Grounding

Proper grounding is critical for VFD installations. Follow NEC Article 250 and the VFD manufacturer's instructions for grounding conductors and connections.


Coordination Study

For large installations, a coordination study is highly recommended. This ensures that the OCPDs are properly coordinated to minimize downtime in the event of a fault.

Safety First

Work with qualified electricians and engineers who understand VFD installations and NEC requirements.

Action Items


Locate the VFD's Nameplate or Datasheet

Get the
exact model number and find the rated input current at 480V.2.

Verify Conductor Sizing

Calculate 125% of the VFD input current and ensure the 500 kcmil conductors meet or exceed that ampacity based on your installation conditions.3.

Review Allen Bradley Documentation

Confirm that the 675A fuse listing applies to the
specific VFD model at the customer site.4.

Compare with Motor FLC

Calculate 175% of the motor's FLC from NEC Table 430.250. This is your fallback if the manufacturer doesn't give a recommendation.
5.


Determine Correct OCPD

Choose an OCPD that is
less than or equal to either the manufacturer's maximum recommended value or* 175% of the motor's FLC (if the manufacturer provides no guidance).6.

Document Everything:
Keep records of all calculations, VFD specifications, and OCPD selections. This will be helpful for future maintenance and troubleshooting.By following these steps, you can ensure a safe and NEC-compliant installation for your VFD-fed motor. Remember to always prioritize safety and consult with qualified professionals when in doubt. Flag for review

Previous Question Next Question