Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Disconnect

User: mannyb, Location: Florida

Asked on: Thursday, August 8, 2024 at 2:53 pm EDT
Answered on: Thursday, March 6, 2025 at 12:56 am EST

Question: We have a telecom shelter located around 50' from service disconnect. Do I need to add a disconnect at shelter inside or outside. Currently the shelter has no disconnect but the one at load center inside building. We are adding a transfer switch but not clear if a disconnect is needed inside or outside

Okay, let's break down the disconnect requirements for your telecom shelter, considering the distance to the service disconnect and the addition of a transfer switch.

NEC Considerations (Key Sections)



NEC 225.31, 225.32 (Disconnection)

These sections generally require a disconnecting means for each building or structure supplied by a feeder or branch circuit. The purpose is to provide a way to isolate the power at the building for safety during maintenance, repairs, or emergencies.


NEC 225.36 Location

The disconnecting means must be readily accessible and located either inside or outside of the structure.

NEC 225.33. Exception
: Exception No. 1 permits the disconnecting means to be located elsewhere on the premises if the disconnecting means is readily accessible to the occupants of the building or structure and is electrically operated.

Analysis of Your Situation


50' Distance

The fact that the telecom shelter is 50 feet from the service disconnect is significant. Generally, the NEC requires a disconnecting means at the structure.2.

Existing Disconnect at Load Center (Inside Building)

Because the shelter is separate structure with no readily available disconnect. You must install an addition disconnect that meets the guidelines in NEC 225.31 and 225.
323.


Adding a Transfer Switch

The addition of a transfer switch
does not eliminate the requirement for a disconnecting means at the telecom shelter. The transfer switch manages the source of power (utility vs. generator), but it doesn't fulfill the safety function of isolating all power to the shelter.

Conclusion and Recommendation



You almost certainly need to install a disconnecting means (disconnect switch or breaker) either inside or outside the telecom shelter.
Here's the recommended approach


Install a Disconnect

Install a properly sized and rated disconnect switch or breaker at the telecom shelter. This is the safest and most compliant option.


Location



Outside

Mounting the disconnect on the exterior of the shelter is often the most practical and accessible option. Ensure it's weatherproof and readily accessible.


Inside

If you choose to install it inside, it must be readily accessible to the occupants of the shelter.2.

Coordinate with Inspections

Before installing anything, discuss your plans with the local electrical inspector. They have the final say on compliance with local codes and can provide specific guidance for your jurisdiction.

Important Considerations



Disconnect Rating

The disconnect must be rated to interrupt the available fault current at the shelter.


Proper Grounding

Ensure that the grounding system is properly installed and bonded.

Signage

Clearly label the disconnect.

Example Scenario (Recommended Solution)

Install a weatherproof disconnect switch on the outside of the telecom shelter, near the point where the power feeder enters the shelter. Run the feeder from the main building's panel to this disconnect. From the disconnect, run the wiring to your transfer switch inside the shelter.* From the transfer switch, connect to your load center.

Disclaimer:
I am an AI Chatbot and not a qualified electrical engineer or inspector. This information is for general guidance only. You MUST consult with a licensed electrician and local authorities to ensure compliance with all applicable codes and regulations. Failure to do so could result in unsafe conditions, property damage, and legal liabilities. Flag for review

Previous Question Next Question