User: mannyb, Location: Florida
Asked on: Thursday, August 8, 2024 at 9:58 pm EDT
Answered on: Thursday, March 6, 2025 at 12:56 am EST
Question: Can #1copper be used with 150a breaker being same size up from 125a per nec 240. The feeder is under the 800a
Okay, let's break down the NEC (National Electrical Code) implications of using #1 copper conductors with a 150A breaker, especially when considering the "next size up" rule.
Understanding the Relevant NEC Sections NEC 240.4(B) - Next Higher Standard Overcurrent Device Rating
This is the core of the "next size up" rule. It permits you to use the next higher standard overcurrent device (breaker or fuse) rating if the conductor's ampacity does not correspond to a standard overcurrent device rating. However, there are several crucial limitations and conditions.
NEC 310.16 - Allowable Ampacities of Insulated Conductors
This table provides the ampacity (current-carrying capacity) of conductors based on their size, insulation type, and ambient temperature. You must refer to this table to determine the ampacity of your #1 copper conductors.
NEC 240.4(D) - Protection of Flexible Cords and Fixture Wires This does NOT apply to feeders. NEC 240.4(C) This outlines a list of exceptions to 240.4(B) - Next Higher Standard Overcurrent Device Rating.
Analysis of Your Scenario1. #1 Copper Ampacity
Refer to NEC Table 310.16. The ampacity of #1 copper conductors depends on their insulation type (e.g., THHN, THWN, XHHW) and the temperature rating of the terminations. Let's assume you're using THHN copper conductors with 75°C rated terminations, which is a common scenario. The ampacity will be 130 amps.
2.
The "Next Size Up" Rule and 150A Breaker
NEC 240.4(B) might allow you to use a 150A breaker because 130A is not a standard breaker size. However, you must ensure that you follow all requirements, including the 800 amp rule mentioned.3.
NEC 240.4(C) - Exceptions to 240.4(B)You mentioned a feeder rated under 800 amps, which means 240.4(C) (3) applies: 240.4 (C)(3) specifically states that 240.4 (B) does NOT apply for tap conductors.
Conclusion
In your situation,
no, you likely cannot use a 150A breaker with #1 copper (rated at 130 amps).You must use overcurrent protection that is no greater than the ampacity of the conductor unless you fall under 240.4(C). Since you are feeding under 800a, you fall under this rule.Your breaker must be no greater than 130 amps, or the next lowest standard breaker: 125 amps.
Important Considerations and Recommendations
Verify Conductor Ampacity
Double-check the insulation type and temperature rating of your #1 copper conductors to confirm their exact ampacity per NEC Table 310.16.
Load Calculation
Ensure your load calculation accurately reflects the actual load the feeder will serve. Undersized conductors can create a dangerous and illegal situation.
Local Amendments
Always check with your local electrical inspector or authority having jurisdiction (AHJ). Local codes may have amendments or interpretations of the NEC that affect your installation.
Consult an Electrician
If you're unsure about any of these calculations or NEC requirements, it's always best to consult with a qualified and licensed electrician.
Disclaimer: This information is for general guidance only and should not be considered a substitute for professional advice from a qualified electrician or electrical engineer. The NEC is a complex document, and its application can vary depending on the specific installation conditions.* Flag for review