Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Can I jumper the line side feed between multiple motor feeder protective devices?

User: AC/DC-FAN, Location: Austin, TX

Asked on: Thursday, August 8, 2024 at 10:23 pm EDT
Answered on: Thursday, March 6, 2025 at 12:56 am EST

Question: I'm designing a UL-508A 480VAC motor control panel. Are there any limitations per UL 508A or NEC bringing a #8 AWG 480VAC feeder from load side of my main fused disconnect protecting the panel directly down to the line side of my first branch circuit motor feeder breaker and then jumpering #12 AWG 480VAC from that first breaker to multiple other branch circuit motor feeder breakers? The #8 AWG Feeder from the load side of my panel main is sized properly per NEC accounting for 125% of largest OPD + sum of all other motor FLA's. The #12 AWG Feeders jumpering to the other OPD's protecting the smaller motor circuits are sized for the sum of those motor FLA's as well. I know I've seen this type of jumpering done many times in the past but want to be sure I'm doing it correct per code. I'd like to not use a Power Distibution Block.

You're asking about a fairly common practice in motor control panel design, but it's crucial to get it right to ensure safety and code compliance. Let's break down the UL 508A and NEC requirements and considerations

Here's a breakdown of the issues and how to approach them:

1. UL 508A and Component Short Circuit Current Ratings (SCCR)



The biggest concern is the SCCR of the branch circuit breakers.
UL 508A requires you to determine the available fault current at the line terminals of every component in your panel, and the components must have an SCCR equal to or greater than that value. Downstream components have to have an SCCR equal to or higher than the upstream devices protection rating. So, your #12 AWG jumpers and the breakers they feed must be able to withstand the available fault current that the main fused disconnect can provide. If the SCCR of your branch circuit breakers and #12 AWG jumpers is not sufficient, this method will be a code violation. Mitigation



Series Ratings

UL 508A allows for
series ratings of components. This means you can use a combination of overcurrent devices to increase the overall SCCR of the downstream circuit. This requires rigorous testing and listing by the manufacturer. It's unlikely that you will find a series rating that allows a #12 AWG wire to be protected by anything larger than a 20 amp breaker for the purposes of SCCR, but you might.

Current Limiting Fuses

Using current-limiting fuses in the main disconnect can significantly reduce the let-through current during a fault, potentially allowing you to meet the SCCR requirements of downstream breakers. However, you must have documentation from the fuse manufacturer showing the let-through current characteristics of the fuses you're using to properly determine if it reduces the available current to an acceptable level.

Higher SCCR Components

Consider using branch circuit breakers with higher SCCR ratings. This may increase the cost, but it simplifies the design.2.

NEC Wire Sizing



NEC Article 430 (Motors, Motor Circuits, and Controllers)

This article dictates the conductor sizing requirements.

Main Feeder (#8 AWG)

As you've stated, the #8 AWG feeder must be sized according to NEC 430.24: 125% of the largest motor's full-load amps (FLA) + the sum of the other motor FLAs. This is your minimum ampacity.


Branch Circuit Conductors (#12 AWG Jumpers)

The #12 AWG conductors feeding each branch circuit breaker must be sized according to NEC 430.22. Typically, that's 125% of the motor's FLA (for a single motor on that branch). If you have multiple motors on a single branch circuit, you need to follow the rules in 430.24, same as the main feeder, but applied to only the motors on that branch.

Overcurrent Protection

Each motor's branch circuit must have its own overcurrent protection (typically a circuit breaker or fuses) sized according to NEC 430.52. This usually involves looking at the motor's code letter and using the tables in 430.52 to determine the maximum allowable overcurrent protection.
3.


UL 508A Internal Wiring

UL 508A provides specific requirements for internal wiring within the control panel.

Conductor Ampacity

The conductors must have sufficient ampacity for the load they will carry, considering the insulation type and the ambient temperature inside the enclosure. NEC Table 310.16 is often used (with derating factors applied as needed).


Short-Circuit Current Rating (SCCR)

This is a critical point, and it ties into the SCCR of the components, as noted above. The wire and termination methods have to withstand the available fault current.

Mechanical Protection

Conductors must be adequately supported and protected from mechanical damage within the enclosure.4.

Terminations



Proper Terminations are Crucial

Ensure that all terminations are properly sized for the conductors being used and are torqued to the manufacturer's specifications. Loose terminations are a common cause of failures.

UL Listed Lugs/Connectors

Use UL-listed lugs and connectors that are appropriate for the conductor size and the equipment being terminated.


Wire Bending Space

Make sure there is adequate wire bending space within the enclosure to allow for proper installation and maintenance. Consult UL 508A and the NEC for wire bending space requirements.5.

Feeder Taps

While you're essentially creating a "tap" situation with the #12 AWG jumpers, this is generally acceptable within a control panel if done correctly, as long as you meet the following conditions:

Overcurrent Protection

Each tap must be protected by an overcurrent device at its load end (i.e., the branch circuit breaker).

Tap Conductor Ampacity

The tap conductor must have an ampacity sufficient for the load it serves, as discussed above.


Termination Size

The terminations on the main feeder for your taps must be sized properly. This becomes very difficult when dealing with multi-strand conductors.

Splicing

Avoid splicing inside the control panel if possible. If you must splice, use UL-listed splicing connectors that are rated for the voltage and current.6.

Power Distribution Blocks (PDBs)

You mentioned you want to avoid using a PDB. While you can do without one, PDBs often provide a safer, more organized, and code-compliant way to distribute power within a control panel, especially with multiple branch circuits.

Advantages of PDBs



Improved Safety

PDBs provide a secure and insulated method for distributing power, reducing the risk of accidental shorts or contact with live conductors.

Simplified Wiring

PDBs make wiring neater and easier, especially when dealing with multiple branch circuits.


Code Compliance

PDBs are typically UL-listed components and can help you meet code requirements for conductor spacing and termination.

Better SCCR Management

UL Listed PDB's have a documented SCCR allowing you to reduce engineering efforts.


Easier Maintenance

PDBs make it easier to troubleshoot and maintain the control panel.

Reduced Wire Nuts and Splices

PDB's eliminate multiple terminations, reducing the chance of a termination failure and freeing up space.7.

Coordination Study

While not always required for smaller panels, a coordination study can be very beneficial. This study analyzes the overcurrent protection devices in your system (main disconnect and branch circuit breakers) to ensure that they are properly coordinated. This means that the branch circuit breakers should trip before the main disconnect in the event of a fault on a branch circuit, preventing unnecessary shutdowns of the entire panel.

In summary


SCCR is the #1 issue.
Verify that the SCCR of all components (especially branch circuit breakers and the #12 AWG jumpers) is sufficient for the available fault current at their line terminals.2. Wire Sizing

Ensure that all conductors are properly sized according to NEC Article 430 and UL 508A requirements.3.

Terminations

Use proper terminations and torque them to the manufacturer's specifications.4.

Consider a Power Distribution Block

It can simplify wiring, improve safety, and aid in code compliance.5.

Documentation is Key

Keep detailed records of all calculations, component SCCR ratings, and any assumptions made during the design process. This documentation will be essential for inspection and troubleshooting.

Recommendation:


While you can technically do what you're proposing, it's often more practical, safer, and easier to achieve code compliance by using a power distribution block, current-limiting fuses, or branch circuit breakers with higher SCCR ratings. Also, it's prudent to have a qualified electrical engineer review your design to ensure that it meets all applicable codes and standards. Flag for review

Previous Question Next Question