Question: Greetings,I'm an instrumentation technician that has been tasked with installing a differential pressure monitoring system in a commercial environment. Pressure measurement is made using 4-20mA loop powered transmitters. Each transmitter will be powered/connected to a custom communication device that is powered using a wall wort style transformer (I was voluntold to use this device) that has a micro USB connector on the end. So essentially, the device is powered by a usb charger. It was requested that we locate the transmitters in clusters, in boxes above the drop ceiling. This means I will have as many as 12 wall transformers to contend with above a drop ceiling at each transmitter box. Electricians will handle any AC requirements, and I will certainly discuss with them but while searching for solutions/recommendations/code requirements online, I came across this site and figured I would ask. What are the best practices/code requirements/safety considerations when dealing with these types of transformers above a drop ceiling in a commercial environment?Let me add that that whole thing feels "dirty" which is why I'm asking the experts....hoping to find a solution that I can feel ok about.Thank you for your time!Bob

Bob, you're right to feel uneasy. Using wall-wart style USB chargers in this application isn't ideal, and it definitely raises some concerns. Here's a breakdown of the issues and some potential solutions

Key Concerns & Code Issues
Listing & Approval

This is the biggest hurdle. NEC (National Electrical Code) requires electrical equipment installed in commercial spaces to be
listed for its intended use. Wall-wart USB chargers are typically listed for general use, not specifically for permanent installation above a drop ceiling where heat buildup, access limitations, and other environmental factors are present. Using non-listed equipment introduces liability concerns.

Accessibility

While drop ceilings provide some access, they are not considered easily accessible for routine maintenance and repair. Placing power supplies above them complicates troubleshooting and replacement.

Heat Dissipation

USB chargers can generate heat, especially when constantly powering a 4-20mA loop. Confined spaces above ceilings can limit heat dissipation, potentially leading to premature failure or even a fire hazard. Check the temperature rating of the device.


Voltage Drop

Twelve 4-20mA loops powered from USB chargers could potentially strain the power supply and lead to voltage drop, affecting the accuracy of your measurements.

Wire Sizing

You'll need to ensure the wiring to the transmitters is appropriately sized for the current draw and the distances involved.


Professional Installation

Per NEC Section 110.3(B) “Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling” and NEC Section 110.14 “Electrical connections and splices shall be made such that the completed connection is mechanically and electrically sound and made using identified connectors”

Best Practices & Solutions
1. Get the Communication Device Re-Designed (Ideal Solution)

Push back on using wall-wart chargers. The best solution is to have the communication device redesigned with an appropriate, listed, and commercial-grade power supply built-in. This would eliminate the mess of individual chargers and ensure compliance. Explore options like: A single, higher-wattage, listed power supply that can power all communication devices in a box via a properly distributed DC bus. POE (Power Over Ethernet) if your communication devices support it. This would provide both power and data over a single cable.2.

Industrial-Grade Power Supplies (Next Best)

If a redesign is not possible, look for small,
industrial-grade, DIN rail-mountable 24VDC power supplies. These are designed for harsh environments and are typically UL-listed. You could mount these within the junction boxes. Consider single or multiple DIN rail-mountable power supplies depending on how many power supplies can be placed within the junction box while maintaining spacing requirements for proper heat dissipation and cable management.3.

Code-Compliant Enclosures

Regardless of the power supply type, everything must be housed within a suitable enclosure (NEMA-rated if necessary). This provides protection from dust, moisture, and accidental contact.4.

Proper Wiring & Connections

Use appropriately sized and rated wiring for the 24VDC (or whatever DC voltage your transmitters require) power. Use proper terminal blocks or connectors (UL-listed) for all connections. No wire nuts allowed above the ceiling! Label all wires and terminals clearly.5.

Documentation

Create detailed wiring diagrams and documentation for future maintenance.6.

Consider a Centralized Power Source

If you have multiple boxes, you may be able to run a single power feed to a central location above the ceiling and then distribute the DC power to the individual boxes. This reduces the number of AC circuits required.7.

Regular Inspections

Implement a regular inspection schedule to check for loose connections, overheating, or other potential problems.

Specific Code References to Discuss with the Electrician
NEC Article 300: Wiring Methods (general wiring requirements) NEC Article 310: Conductors for General Wiring (wire sizing) NEC Article 400: Flexible Cords and Cables (if used – but try to avoid flexible cords above the ceiling) NEC Article 430: Motors, Motor Circuits, and Controllers (if the power supplies are used for anything that could be considered a motor circuit) NEC Article 645: Information Technology Equipment (if the communication devices fall under this definition) NEC Article 725: Class 1, Class 2, and Class 3 Remote-Control, Signaling, and Power-Limited Circuits (likely applicable for your low-voltage DC wiring)Safety Considerations Lockout/Tagout (LOTO)

Ensure a LOTO procedure is in place before working on any electrical circuits.

Proper PPE

Use appropriate personal protective equipment (PPE), including safety glasses, gloves, and insulated tools.


Qualified Personnel

Only qualified personnel should perform electrical work.

Action Plan
1. Document Your Concerns

Clearly document your concerns about using wall-wart chargers and present them to the project manager and/or the electrician.2.

Consult with the Electrician

Discuss the electrical requirements and code compliance issues with the electrician. Get their input on the best way to provide power to the transmitters.3.

Explore Alternatives

Research alternative power solutions (industrial-grade supplies, POE, etc.) and present them to the team.4.

Get Approval:
Before proceeding with the installation, get written approval for the chosen power solution from the project manager and the electrician.By addressing these concerns and implementing these best practices, you can ensure a safer, more reliable, and code-compliant installation. Good luck! Flag for review