Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Supplementary Grounding Electrodes

User: anbm, Location: TX

Asked on: Friday, August 9, 2024 at 7:14 am EDT
Answered on: Thursday, March 6, 2025 at 12:57 am EST

Question: 1. If the building grounding electrode system already has water metal pipe, building steel, UFER, one ground rod - all bond together....the second ground rod (Supplementary Grounding Electrode) is not required, correct? Because the first ground rod is no longer the sole grounding electrode.2. How or what tool will be used to meter ground resistance?

You are correct on both counts:1. Supplementary Ground Rod Not Required

If the building grounding electrode system already has a water metal pipe, building steel, UFER (concrete-encased electrode), and a ground rod all bonded together, adding a second supplementary ground rod is

not required
by the NEC (National Electrical Code). The interconnected system of electrodes constitutes a robust grounding system. The purpose of the second ground rod (or other supplemental electrode) is primarily to improve grounding in cases where a single rod is the only grounding electrode. If you have multiple electrodes bonded, you have already achieved that improvement.2. Ground Resistance Meter (Ground Tester)

The instrument used to measure ground resistance is typically called a

Ground Resistance Meter
or Ground Tester. There are a few different types, but the most common uses the Fall-of-Potential method: Fall-of-Potential Method

This method requires placing the ground rod you want to test in the earth along with two auxiliary ground rods (probes) at specific distances from the ground rod being tested. The ground tester injects a test current into the earth and measures the voltage drop. By knowing the current and voltage, the tester can calculate the resistance of the earth around the electrode being tested.


Types of Ground Testers



3-Point Tester (Most Common)

Uses the Fall-of-Potential method with two auxiliary ground rods/probes. The standard setup is to place the probes at distances from the electrode under test, usually in a straight line. Proper probe placement is key to obtaining accurate results.


Clamp-On Tester

Measures ground resistance without the need for auxiliary ground rods. The clamp is placed around the ground conductor (e.g., the wire going to the ground rod) and measures the loop resistance of the ground circuit. These are useful for testing multiple grounded systems where the ground rod is part of a larger, connected grounding network. They can't measure the resistance of a single, isolated ground rod.

2-Point Tester

Simpler tester, but less accurate. They need a known good ground for comparison. Not generally recommended for critical grounding system testing.


Important Considerations



Probe Placement

Proper probe placement is crucial for accurate Fall-of-Potential testing. The probes must be far enough away from the electrode under test to be outside its "sphere of influence" (the area of earth immediately around the electrode that significantly contributes to its resistance). Follow the manufacturer's instructions for probe placement distances.


Soil Conditions

Soil moisture, temperature, and composition can all affect ground resistance. Testing during dry periods may result in higher resistance readings.

Interference

Underground utilities or other buried metal objects can influence the readings. Choose a testing location that is free from known sources of interference.


Calibration:
Ensure the ground tester is properly calibrated before use.Therefore, to meter ground resistance, you'll need a Ground Resistance Meter (ground tester), typically a 3-point tester using the Fall-of-Potential method, along with auxiliary ground rods (probes) and connecting test leads. You must understand the proper placement of the probes and interpret the readings correctly. Clamp-on testers are useful in some situations, but not for measuring the resistance of a single, isolated ground electrode. Flag for review

Previous Question Next Question