User: Dsg319, Location: West Virginia
Asked on: Friday, August 9, 2024 at 9:29 am EDT
Answered on: Thursday, March 6, 2025 at 12:57 am EST
Question: I know next to nothing with MV equipment and requirements.But on a job where we pulled 6 parallel 3c750kcmil tray cables with and 1/0 ground in the cable.This is 4160v and coming off of from what I can tell is a 3000amp breaker.How do they get away with not having a 400kcmil EGC ?.Even with utilizing cable tray as an EGC at the expansion joints it as 4/0 jumpers for continuity.I know there has to be more to this than what I know.Just looking to get educated.
You're right to question this, as it sounds like a potential violation of NEC or other applicable standards. Here's a breakdown of why your concerns are valid and what factors might be at play
Why a Large EGC is Typically Required (NEC Perspective, though specifics vary):
Fault Current Clearing
The primary purpose of the Equipment Grounding Conductor (EGC) is to provide a low-impedance path back to the source in case of a ground fault. This low impedance allows a large current to flow, tripping the overcurrent protective device (OCPD, like that 3000A breaker) quickly and safely. With 4160V and a 3000A breaker, the available fault current could be very high.
Voltage Drop Limitation
A small EGC might lead to excessive voltage drop during a fault, which could prevent the OCPD from tripping quickly enough, leading to potential hazards like arc flash or equipment damage.
NEC Requirements (General, refer to your local code)
NEC 250.184(C)
This section addresses grounding for circuits over 1000V. It generally mandates an EGC sized based on the phase conductors, but allows for exceptions.
NEC 250.122
This section deals with EGC sizing in general, for systems under 1000V. While not directly applicable to your 4160V situation, the principles are relevant. The rule of thumb is that the EGC must increase in size proportionally with the increase in ungrounded conductors. Since you have six parallel sets of 750 kcmil conductors, an equivalent single conductor would be massive.
Table 250.122
This table dictates the EGC size based on the OCPD size. For a 3000A breaker (assuming it's rated that high), the table stops at 2000A, requiring a 3/0 AWG copper EGC. However, this is for systems under 1000V.
Possible Explanations/Exceptions to the Standard EGC Sizing
1.
Engineering Study and Calculations (Most Likely Reason)
The most likely explanation is that a qualified electrical engineer performed a detailed fault current study and impedance calculations for the specific installation. This study could have demonstrated that the combination of the cable tray (properly bonded) and the 1/0 ground wire within each cable provides a sufficient low-impedance ground fault path to safely clear faults.
Factors considered in the study might include
Source Impedance
The impedance of the utility transformer and the power distribution system significantly impacts the available fault current. If the source impedance is high, the fault current might be limited.
Cable Length
Longer cable runs increase impedance, reducing fault current.
Cable Tray Material and Construction
The type of metal, dimensions, and bonding of the cable tray all affect its ability to carry fault current.
Protective Relay Settings
The settings on the protective relays associated with the 3000A breaker can be adjusted to provide faster tripping for ground faults.
Engineering Documentation
If this is the case, there must be documented engineering calculations justifying the EGC size and the reliance on the cable tray. This documentation is crucial for safety and compliance. Ask for a copy of the study.2.
Cable Tray as Sole EGC (Highly Unlikely Alone)
The NEC does allow cable tray to be used as an EGC under specific conditions (NEC 392.60). However, these conditions are stringent:
Approved for Grounding
The cable tray must be specifically approved for use as an EGC.
Minimum Cross-Sectional Area
The cable tray must have a minimum cross-sectional area of metal. This varies depending on the type of tray and the application.
Proper Bonding
All sections of the cable tray must be properly bonded together using listed bonding jumpers (likely those 4/0 jumpers you saw) at all joints, including expansion joints, to ensure electrical continuity.
Supplement with Internal EGC
Even when cable tray is approved, it's highly unusual not to supplement it with conductors within the cables. The internal 1/0 wires probably count as this. However, on 4160V, 1/0 seems very undersized without thorough calculations.3.
Other Specific Code Requirements or Local Amendments
Check with the local authority having jurisdiction (AHJ). There might be local amendments to the NEC or other applicable codes that influence EGC sizing in medium-voltage installations.
What to Do
1.
Ask Questions
The most important step is to ask the engineer or contractor responsible for the design and installation to provide the documentation justifying the EGC size. Specifically, request the fault current study and calculations.2.
Review the Engineering
If you have the documentation, carefully review it to understand the assumptions and calculations used. If you are not familiar with electrical engineering principles, consult with a qualified electrical engineer.3.
Contact the AHJ
If you still have concerns after reviewing the documentation, contact the local authority having jurisdiction (AHJ) to get their opinion.4.
Document Everything
Keep a record of all your questions, the responses you receive, and any documentation you review.
Key Takeaways
Medium-voltage systems require careful engineering analysis. Standard rules of thumb for EGC sizing often don't apply. Documentation is critical. There should be documented engineering calculations justifying the design.* Safety is paramount. If you have any doubts about the safety of the installation, raise your concerns immediately.Remember, electricity at 4160V is dangerous, and proper grounding is essential to ensure safety. Don't hesitate to seek clarification and ensure that the installation meets all applicable code requirements and sound engineering practices. Flag for review