Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: voltage drop 3% include transformer or not?

User: binwork91, Location: new york

Asked on: Friday, August 9, 2024 at 11:15 am EDT
Answered on: Thursday, March 6, 2025 at 12:57 am EST

Question: Do you consider the voltage drop in transformers?In my opinion, we need to take the voltage drop in transformers into account.However, I've heard different opinions where people only consider the voltage drop on feeders.What is your opinion, and why?

You are absolutely correct: Voltage drop in transformers should absolutely be considered in overall system voltage drop calculations. Dismissing transformer voltage drop is a significant oversight and can lead to serious performance issues.Here's a breakdown of why you're right and why others might mistakenly exclude it

Why You're Correct (Why Transformer Voltage Drop Matters):
Part of the System

Transformers are
integral components of the electrical power distribution system. They step up or step down voltage to optimize transmission and distribution. Just like feeders, they have impedance. Ignoring their impedance means ignoring a significant source of voltage drop.

Significant Impedance

Transformers, especially larger ones, do have a noticeable impedance (expressed as % impedance or Z%). This impedance causes a voltage drop under load. It's not always negligible. For example, a transformer with 5% impedance will experience approximately a 5% voltage drop at full rated current and rated power factor (PF).

Cumulative Effect

Voltage drop is cumulative throughout the system. The drop in the transformer adds to the drop in the feeders and branch circuits. Ignoring the transformer drop can lead to:


Undervoltage at the load

Equipment may not operate correctly or efficiently. Motors can overheat, lights dim, and electronic equipment can malfunction.

Reduced Efficiency

Lower voltage means higher current for the same power, leading to increased losses in conductors.


Potential Damage

Some equipment is very sensitive to voltage fluctuations and can be damaged by consistently low voltage.

Code Compliance

While electrical codes like the NEC (National Electrical Code) in the US don't
mandate a specific voltage drop calculation method for the entire system, they do set limits for voltage drop in feeders and branch circuits. Ignoring the transformer makes it much harder to ensure the overall system stays within those acceptable limits. You might have a feeder voltage drop that appears fine on paper, but when you add the transformer drop, you exceed the code's recommendations.

Design Considerations

Accurate voltage drop calculations are critical for proper system design. They help in selecting the appropriate transformer size, conductor sizes, and tap settings on transformers to ensure adequate voltage at the load. Underestimating voltage drop can lead to costly rework later.

Why Some Might (Incorrectly) Exclude Transformer Voltage Drop



Simplified Calculations (Convenience)

Sometimes, engineers or technicians might use simplified calculation methods or rules of thumb that don't explicitly include transformer voltage drop for quick estimations. This can be acceptable for very small systems or preliminary design phases,
but it's never a substitute for a thorough calculation.

Assumed Negligible Drop

In some very specific cases, the transformer's impedance might be very low, or the load it supplies might be relatively small. In such cases, the voltage drop might be small enough to be considered negligible. However, this should be verified with calculations, not assumed.

Misunderstanding of Transformer Operation

Some may incorrectly assume that transformers are perfect voltage sources and maintain a constant voltage output regardless of load. This is not true; they have internal impedance that causes voltage regulation (change in output voltage with changes in load).


Focus on Feeder Regulations

Some people may be focused solely on meeting the voltage drop regulations for feeders, without considering the overall system performance. While meeting those regulations is important, it's insufficient without accounting for the transformer drop.

How to Include Transformer Voltage Drop in Calculations

1.

Obtain Transformer Impedance

The transformer impedance is usually provided by the manufacturer as a percentage (e.g., 5% Z). This is a critical piece of information. The impedance is usually given at the transformer's rated kVA.2.

Convert %Z to Ohms

You can calculate the transformer's equivalent series impedance in ohms referred to either the primary or secondary side. The formula for calculating impedance in ohms (Z in ohms) from percentage impedance (%Z) is: Z (ohms) = (%Z / 100) (V^2 / kVA 1000)Where: %Z is the percentage impedance from the transformer nameplate V is the voltage (line-to-line for 3-phase) on the side you're referring the impedance to (primary or secondary). Make sure to use the actual operating voltage, not just the nominal voltage. kVA is the transformer's rated kVA.3.

Calculate Voltage Drop

Use Ohm's Law (V = I * Z) and/or more sophisticated power flow calculations to determine the voltage drop across the transformer impedance at the expected load current. You'll also need to consider the power factor of the load. Since the impedance is generally given at rated kVA, if you are operating at a significantly lower kVA you can adjust the impedance calculation accordingly for a more accurate voltage drop calculation.4.

Add to Feeder Voltage Drop

Add the voltage drop across the transformer to the voltage drop calculated for the feeders and branch circuits.

In summary:


Always include transformer voltage drop in your system voltage drop calculations. It's an essential step in ensuring proper equipment operation, efficiency, and code compliance. Don't rely on simplified assumptions or rules of thumb without verifying their accuracy. Get the transformer impedance data, perform the necessary calculations, and account for it in your system design. Your designs will be better, and your clients will be happier! Flag for review

Previous Question Next Question