Question: Currently troubleshooting a house that when the air conditioning outside unit runs some lights in the house flicker and the dishwasher will beep and the controls will light up. Only does it when the compressor runs. During the winter this does not happen if the auxiliary heat which is propane is used instead of the heat pump. Dishwasher was changed out and Bosch heat pump was replaced.
This is a classic symptom of a voltage drop when the A/C compressor kicks on. Here's a breakdown of the possible causes and how to troubleshoot them
Understanding the Problem
Voltage Drop
When the A/C compressor starts, it requires a large surge of electricity (inrush current). If the electrical system can't supply that current without a significant voltage drop, other appliances will experience a temporary dip in voltage. This dip is what causes the lights to flicker and can disrupt the operation of sensitive electronics like dishwashers.
Why it happens with A/C and not Propane Heat
Your propane heat likely uses much less electricity. The auxiliary heat likely only is energizing a blower motor where as the air conditioning is powering a compressor, blower motor and some electronics.
Why new equipment didn't fix it
Replacing the A/C unit and dishwasher could have helped if the old units were drawing excessive current due to age or malfunction. However, if the underlying electrical infrastructure is the problem, new units won't solve it.
Possible Causes (In order of likelihood)1. Loose/Corroded Connections
This is the MOST common culprit. Check all electrical connections related to the A/C and the main service panel.
A/C Disconnect Switch
This is the switch near the outside A/C unit. Turn the power OFF at the breaker, and then inspect the wiring inside the disconnect switch. Look for loose wires, burned insulation, or corrosion. Tighten all connections securely.
Service Panel (Main Breaker Box)
Turn OFF the main breaker before opening the panel.
If you are not comfortable working with electrical panels, HIRE A QUALIFIED ELECTRICIAN. This is dangerous work. Look for loose or corroded connections on the main breaker, the A/C breaker, and the neutral/ground bus bars. Check for any signs of overheating (discoloration, melting). Tighten all connections to the proper torque specifications (if available on the panel). Wiring at the A/C Unit
Carefully inspect the wiring where it enters the A/C unit.
Wiring at the Dishwasher
Though you replaced the dishwasher, double-check the wiring connections to it.2.
Undersized Wiring
The wire gauge running to the A/C unit might be too small for the distance and the A/C unit's current draw. This causes excessive voltage drop.
How to Check
Find the A/C unit's electrical specifications (usually on a sticker on the unit). Note the Minimum Circuit Ampacity (MCA). This is the minimum size breaker and wire that should be used. Measure the length of the wire run from the breaker panel to the A/C unit. Consult a wire sizing chart (online or in an electrical code book) to determine if the wire gauge is appropriate for the MCA and the distance.
Important
If the wire is undersized, you'll need to have an electrician replace it with the correct gauge. Also check the wire size to the dishwasher, it may be undersized.3.
Weak Neutral Connection
A poor neutral connection can cause voltage imbalances that affect sensitive electronics. This is often difficult to diagnose without specialized equipment.
How to Check
An electrician can perform a neutral-to-ground voltage test. A high voltage reading can indicate a problem with the neutral. Check the neutral connections at the service panel.4.
Shared Neutral
In older homes, it's possible that the A/C circuit and the lights/dishwasher circuit share a neutral wire. This is generally against modern electrical codes and can cause problems.
How to Check
An electrician can trace the wiring to determine if circuits are sharing a neutral.5.
Overloaded Circuit
While less likely since you replaced the A/C unit, the circuit the A/C is on may be overloaded by other appliances. The dishwasher and lights on the same circuit can cause issues.6.
Power Company Issues
In rare cases, the problem could be with the power company's service to your house.
How to Check
If you've ruled out all internal wiring issues, contact your power company. They can check the voltage at the meter and the transformer serving your house.
Troubleshooting Steps
Start with Visual Inspection
Turn OFF the power (main breaker). Carefully inspect all wiring connections at the A/C disconnect, service panel, A/C unit, and dishwasher. Look for loose wires, corrosion, burning, or other damage. Tighten any loose connections.2.
Voltage Drop Test (requires a multimeter and understanding of electrical safety)
Turn ON the A/C. Measure the voltage at the A/C disconnect switch before the compressor starts. Measure the voltage while the compressor is running. If there's a significant voltage drop (more than 5-10%), it confirms a wiring problem. Repeat the voltage drop test at the breaker panel and at the dishwasher outlet to help isolate the problem.3.
Isolate the Dishwasher
Try running the A/C with the dishwasher completely disconnected. If the lights still flicker, the dishwasher isn't the primary cause.4.
Call an Electrician
If you're not comfortable working with electrical wiring, or if you've tried the above steps and the problem persists,
call a qualified electrician. They have the tools and expertise to diagnose and repair complex electrical problems safely.
Important Safety Precautions
Turn OFF the power before working on any electrical wiring. Double-check that the power is off with a voltage tester. Be careful when working around electricity.* If you're not sure what you're doing, call an electrician.
By systematically checking these potential causes, you should be able to pinpoint the source of the voltage drop and get your electrical system working properly. Remember safety first! Flag for review