Topic: No Grounding on Panel, OK with NEC?

User: ponderosa, Location: Oregon, Ohio

Asked on: Friday, August 9, 2024 at 2:13 pm EDT
Answered on: Thursday, March 6, 2025 at 12:58 am EST

Question: Electrical service was installed in 1973. Panels are not grounded, just tied to utility neutral. Owner claims this was up to code when installed. My assumption is that the panels were bonded to water pipes at some point but then removed when water pipes were changed out. Is it accurate to assume the NEC required panels to be grounded in 1973?

You're asking a very common and important question about electrical safety in older homes. Let's break it down: The 1973 NEC and Grounding

Yes, your assumption is accurate. The 1973 National Electrical Code (NEC)

did
require grounding of electrical panels. The core concept of a grounded electrical system has been a requirement in the NEC for many decades prior to 1973.
Why Grounding is Required

The purpose of grounding is to provide a low-impedance path for fault current to flow back to the source (usually the transformer at the utility). This low-impedance path is crucial because it allows a circuit breaker or fuse to quickly trip and de-energize a faulty circuit. Without proper grounding, a fault current can linger, potentially energizing metal parts of appliances or the electrical system itself, creating a shock hazard.

Bonding vs. Grounding

It's important to distinguish between
grounding and bonding.

Grounding

Connecting the neutral conductor to earth.

Bonding

Connecting all non-current-carrying metal parts of the electrical system together to create an electrically continuous path. This includes things like metal conduit, metal enclosures, and appliance frames.The grounding electrode (e.g., ground rod, water pipe) connects to the service neutral and the equipment grounding system. Bonding ensures that if a fault occurs, all metal parts are at the same potential, minimizing the risk of shock.


What Happened in this Case

You're likely correct that at some point there was a grounding connection, probably to a metal water pipe. When the plumbing was updated to PVC or PEX (non-conductive materials), that grounding connection was lost. It's also possible that a ground rod was originally installed, but the connection to it has corroded or been removed.

Is the Owner Correct?
Technically, the owner may be correct that the installation initially met code at the time it was installed. However, electrical codes are not retroactive. That means the owner is grandfathered in. However, once anything changes (like a panel replacement, significant wiring alteration, etc.), the updated portions must comply with the current NEC edition (as adopted by the local jurisdiction). Also, even if the installation was code-compliant at the time, it is NOT considered safe today. The Problem with Relying Only on the Utility Neutral

While the utility neutral is grounded at the transformer, relying solely on it for grounding within the building is dangerous. Here's why:

Longer Fault Path

The fault current has to travel all the way back to the transformer through the neutral conductor. This longer path adds impedance, which can reduce the fault current and prevent the breaker from tripping quickly.


Neutral Conductor Integrity

If the neutral conductor becomes compromised (loose connection, corrosion, etc.), the grounding path is lost, and equipment can become energized.

Voltage Potential

Under fault conditions, the neutral conductor can develop a voltage potential with respect to ground. This can create a shock hazard.

What Needs to Be Done


Consult a Qualified Electrician

The most important step is to have a licensed and experienced electrician evaluate the entire electrical system.2.

Install a Proper Grounding System

The electrician should install a proper grounding system that complies with the current NEC. This typically involves:
Installing one or more ground rods. Connecting the ground rod(s) to the service neutral (at the service entrance). Bonding all metallic parts of the electrical system together (including the metal panels).* Running equipment grounding conductors (wires) to all outlets and appliances.3.

Consider GFCI Protection

In addition to grounding, Ground Fault Circuit Interrupters (GFCIs) provide an extra layer of protection against electric shock. GFCIs should be installed in areas where water is present (bathrooms, kitchens, outdoors, etc.).

In summary, while the original installation may have technically been "up to code" in 1973, it is absolutely essential to upgrade the grounding system to meet modern safety standards. A missing or inadequate grounding system is a serious safety hazard and should be addressed immediately.