User: electro7, Location: Northern CA, US
Asked on: Friday, August 9, 2024 at 2:36 pm EDT
Answered on: Thursday, March 6, 2025 at 12:59 am EST
Question: Hi,I am designing a system and wanted to confirm on some electrical calculations for feeder conductors.inverter max output current 41.6A and 33.3A.2 inverters of the 41.6A and 1 inverter of the 33.3A.41.6 X 1.25 = 52A (OCPD 60A)33.3 X 1.25 = 41.63 (OCPD 50A)Thats easy but I was wondering about the feeders feeding this solar PV panelboard these three inverters are connected to.Can it be:(41.6 X 2) + 33.3 = 116.5A X 1.25 = 145.63AUSE 150A OCPD??Even though the individual inverter output circuit breakers add to 170A can the panelboard feeder still be 150A?
You are correct in calculating the individual inverter output circuit protection device (OCPD) sizes and applying the 1.25 multiplier for continuous operation as per NEC requirements.Let's break down the feeder calculation to ensure accuracy and compliance with the National Electrical Code (NEC)
Understanding the NEC Requirements
The NEC requires that feeders be sized to carry the calculated load. For PV systems, this calculation involves multiplying the inverter's maximum output current by 125% to account for continuous operation (over 3 hours). However, the NEC also allows for the use of diversity factors and demand factors in some situations.
Feeder Calculation
You've correctly calculated the continuous current from each inverter: Inverter 1 (41.6A): 41.6A 1.25 = 52A Inverter 2 (41.6A): 41.6A 1.25 = 52A Inverter 3 (33.3A): 33.3A 1.25 = 41.63ANow, to calculate the total continuous current for the feeder:52A + 52A + 41.63A = 145.63AYour calculation of 145.63A is correct.
Feeder OCPD and Conductor Sizing
You are choosing a 150A OCPD, which would cover the 145.63A continuous load. You are choosing a conductor and you want to confirm the size and is sized to handle 145.63A.
Regarding the Sum of Individual OCPDs Exceeding the Feeder OCPD
Yes, it's common and permissible for the sum of the individual inverter output circuit breakers to be larger than the feeder circuit breaker rating. Here's why: Diversity
It's unlikely that all inverters will be producing their maximum output current simultaneously. Solar irradiance fluctuates throughout the day, and inverter efficiency varies with input power.
Overcurrent Protection
The individual inverter OCPDs protect the inverter output circuits from overcurrent events within those circuits. The feeder OCPD protects the feeder conductors from overcurrent events on the feeder itself.
NEC Allowance
The NEC anticipates this scenario in section
690.9(A) Circuit ampacity and Overcurrent Device Sizing.Important Considerations
Conductor Ampacity
The conductors feeding the panelboard MUST have an ampacity equal to or greater than the calculated continuous current (145.63A). Use the appropriate ampacity tables in the NEC (Table 310.16 or the engineering tables) considering the conductor's insulation type, termination temperature ratings (usually 75°C or 90°C), and any ambient temperature derating factors.
Voltage Drop
Perform a voltage drop calculation to ensure the voltage drop from the inverters to the panelboard is within acceptable limits (typically 3% for feeders and 5% total, including the branch circuits). Longer conductor runs will require larger conductors to minimize voltage drop.
Short-Circuit Current Rating (SCCR)
Ensure the panelboard and all connected equipment have an adequate SCCR to withstand the available fault current at the panelboard location.
Manufacturer's Instructions
Always follow the inverter manufacturer's instructions for wiring and overcurrent protection requirements. They may have specific requirements or recommendations that exceed the minimum NEC requirements.
Example
Let's say you're using THHN conductors with a 75°C termination rating and no other derating factors. Referring to NEC Table 310.16, you would need a 1/0 AWG copper conductor, which has an ampacity of 150A (at 75°C). You would also need to confirm the voltage drop and SCCR are adequate.
In SummaryYour calculations are mostly correct. You can use a 150A OCPD for the feeder if the conductors are sized to handle at least 145.63A and all other relevant NEC requirements are met (voltage drop, SCCR, etc.). The fact that the sum of the individual inverter OCPDs is greater than 150A is acceptable. Remember to consult the latest edition of the NEC and local codes, and always consult with a qualified electrical engineer or contractor for final design and installation.* Flag for review