Topic: Temperature Considerations in PV Design

User: wwhitney, Location: Berkeley, CA

Asked on: Friday, August 9, 2024 at 3:39 pm EDT
Answered on: Thursday, March 6, 2025 at 12:59 am EST

Question: What computations require knowing a maximum and minimum ambient temperature? I'm thinking max Voc on the DC string requires maximum temperature, maximum Isc on the DC string requires minimum temperature, and conductor ampacity requires maximum temperature.If you use ASHRAE historical data for a given location, you can get numbers like the mean 1% high temperature (1% of the time it was hotter, so for 87.6 hours per year), the mean 0.4% high temperature (35 hours per year it was hotter), the mean annual extreme (50% of the years the record high for the year was hotter, 50% of the years it was lower), or you can compute a likelihood of exceedance at any level for any length of time (e.g. a 10% chance that the highest temperature seen over 20 years exceeds the value, and a 90% chance it doesn't).Which of those temperature levels would you use?And lastly, since we've had a warming trend for the last 100+ years, if the ASHRAE data is purely historical (is that right?), when designing a project with an expected lifetime of 20 years, do you make a prediction about how much warmer things will be in 20 years, and use that prediction for determining the maximum temperature to use? If so, what source do you use for the future temperature prediction?Cheers, Wayne

You've hit on some of the key computations that require ambient temperature considerations in electrical and PV design. Let's break down each point and address your questions

Computations Requiring Max/Min Ambient Temperature:

You're correct about the key areas: Maximum Voc Calculation (DC String)

As temperature
decreases, the open-circuit voltage (Voc) of a PV module increases. Designing for the lowest expected ambient temperature is crucial. This prevents over-voltage conditions that can damage inverters or other components.

Maximum Isc Calculation (DC String)

While temperature has less influence on Isc than it does on Voc, it does have an effect. As temperature increases, the short-circuit current (Isc) of a PV module slightly increases. Designing for the highest expected ambient temperature is important for accurate string sizing and overcurrent protection.

Conductor Ampacity

Conductor ampacity is directly related to the conductor's temperature rating. Higher ambient temperatures reduce a conductor's ability to dissipate heat, thus
reducing its ampacity. You must design for the highest expected ambient temperature to avoid exceeding the conductor's temperature rating and potentially causing fires.

Equipment Enclosure Temperature

Temperature inside electrical enclosures rises due to equipment losses and solar radiation. You need to consider the highest expected ambient temperature combined with solar irradiance to ensure equipment within the enclosure operates within its rated temperature range. Cooling solutions (fans, air conditioners) might be necessary.

Battery Storage Systems

Battery performance is heavily influenced by temperature. Both
high and low temperatures can significantly reduce battery capacity, lifespan, and efficiency. BMS (Battery Management System) must consider these variations.

Choosing the Right Temperature Level

This is a crucial question, and there's no single "right" answer. It depends on the specific application, local codes, and the risk tolerance you (or your client) are willing to accept. Here's a breakdown:


Mean 1% High Temperature (87.6 hours/year)

Generally considered too high for continuous use calculations. This is a very infrequent extreme.

Mean 0.4% High Temperature (35 hours/year)

Still likely too high for continuous use, but might be considered for equipment with short-term overload capacity.


Mean Annual Extreme

A good starting point for many designs, offering a balance between cost-effectiveness and reliability. Using the average of the annual extreme high temperatures reduces the risk of under-designing by not being skewed by single-year anomalies, but there's still a 50% chance it will be hotter than that at least once per year.

Likelihood of Exceedance (e.g., 10% chance over 20 years)

This is the
most robust and recommended approach. It allows you to quantitatively assess the risk of exceeding a certain temperature threshold over the design life of the system. This allows you to make an informed decision based on the cost and consequences of a temperature exceedance.

Key Considerations for Choosing a Temperature Level



Component Derating

Many electrical components (inverters, charge controllers, breakers) have derating curves that specify how their performance decreases at higher temperatures. You must ensure that your equipment can handle the chosen design temperature.

Safety Factors

Incorporate safety factors into your calculations, especially for critical components.


Code Requirements

Local electrical codes (NEC in the US) may specify minimum ambient temperature requirements for certain applications.

Client's Risk Tolerance

Discuss the risks and costs associated with different temperature levels with your client.

The Warming Trend and Future Temperature Predictions

You are absolutely correct to be concerned about this. Relying solely on historical ASHRAE data is becoming increasingly inadequate due to climate change. Here's how to address it:1.

Acknowledge and Quantify the Uncertainty

Explicitly state that your design temperature is based on historical data and that future temperature increases are possible.2.

Extend the Historical Data

Look for longer historical datasets. If possible, obtain data covering the longest available period.3.

Incorporate Climate Change Projections

This is where it gets tricky, but essential.


IPCC Reports (Intergovernmental Panel on Climate Change)

These reports provide comprehensive climate models and projections. The CMIP (Coupled Model Intercomparison Project) data within the IPCC framework is used to generate future scenarios. The IPCC provides a summary for policymakers that provides global estimates for several possible scenarios.

National Climate Assessments

Many countries have their own climate assessments that provide more localized projections (e.g., the National Climate Assessment in the US). These assessments can use higher resolution models and tailor the data to local regions. The NCA provides projections out to the end of the century.


Local Climate Data

Some cities or regions may have their own climate studies and projections.

"Climate Change Adjusted Design Values"

This is an evolving area. Some organizations are starting to develop methodologies for adjusting design values (including temperature) based on climate projections.4.

Add a Margin of Safety

Once you have climate projections, add a safety margin to your design temperature. This is a subjective decision, but it should be based on the level of uncertainty and the consequences of exceeding the design temperature.5.

Consider Adaptive Design

Where possible, design systems that can be adapted to future temperature changes. This could involve oversizing components, selecting equipment with higher temperature ratings, or including provisions for future cooling upgrades.6.

Document Your Assumptions

Thoroughly document all of your assumptions, data sources, and calculations. This will allow future engineers to understand your design choices and make adjustments if necessary.

Example Scenario

Let's say you're designing a PV system with a 20-year lifespan in Phoenix, Arizona.1.

Historical Data

You get ASHRAE data showing a mean annual extreme high temperature of 45°C (113°F).2.

Climate Projections

You consult the National Climate Assessment and find that the mean annual extreme high temperature in Phoenix is projected to increase by 2-4°C (3.6-7.2°F) over the next 20 years under a moderate emissions scenario.
3.


Safety Margin

You decide to add a 2°C (3.6°F) safety margin to account for the uncertainty in the climate projections.
4.


Design Temperature

Your design temperature becomes 45°C (historical) + 4°C (projection) + 2°C (safety margin) = 51°C (124°F).

Key Takeaways:
Don't rely solely on historical data in a warming world. Use climate projections to estimate future temperature changes. Add a safety margin to account for uncertainty. Document your assumptions thoroughly. Consider adaptive design strategies.It's important to remember that predicting the future is inherently uncertain. However, by incorporating climate projections into your design process, you can significantly improve the long-term reliability and performance of your electrical systems. Consulting with a qualified climate scientist or environmental engineer can also be beneficial. Flag for review