Topic: Potential electrical power saving by increasing the size of conductors NEC REQUIRED

User: Rjryan, Location: Trophy Club, Texas

Asked on: Friday, August 9, 2024 at 6:03 pm EDT
Answered on: Thursday, March 6, 2025 at 12:59 am EST

Question: I have found a few articles about the electrical use savings by increasing the size of the conduct past NEC requirements.It makes sense to me larger wire has less resistance, will not heat up as much under the same load, because heat causes resistance.I questioned an Electrical Inspector from Fort Worth, Texas several years ago about this. Everything has gone up, but at that time he said a rough calculationis for every size you increase the wire it will pay for itself in 5 years.Besides the resistance of the conductors, I have not found a formula or method to accurately calculate electrical use savings by increasing conductorsize beyond the NEC.Does anyone have a formula or method for these calculations?

You're on the right track! Increasing conductor size beyond NEC minimum requirements can indeed lead to energy savings, primarily due to reduced I²R losses (also known as copper losses or heat losses). Here's a breakdown of the formula, method, and key considerations for calculating those savings

1. Understanding the Core Formula: I²R Losses

The power loss in a conductor due to its resistance is calculated using the following fundamental formula: P = I²R P

Power loss (in Watts) – This is the key value you want to reduce.

I

Current flowing through the conductor (in Amperes) – This is dictated by the load.


R

Resistance of the conductor (in Ohms) – This is where conductor size comes in. Larger conductor = lower resistance.

2. Calculating Conductor Resistance (R)


You need to determine the resistance of the conductors you're comparing: R = (ρ L) / A R

Resistance of the conductor (in Ohms)


ρ

Resistivity of the conductor material (in Ohm-meters or Ohm-circular mils/foot). For copper, you can use approximately 1.724 x 10^-8 Ohm-meters, or 10.4 Ohm-circular mils/foot at 20°C.

L

Length of the conductor (in meters or feet). Important: This is the
one-way length. For a complete circuit, you need to double the one-way distance to account for the return path.

A

Cross-sectional area of the conductor (in square meters or circular mils). This is where the NEC tables are helpful. The NEC provides approximate circular mil areas for different AWG wire sizes. You can also use online calculators for converting AWG size to circular mils.

3. The Complete Calculation Method: A Step-by-Step Approach


Here's the methodical way to calculate the energy savings: Step 1: Define the Scenario. Load

Determine the electrical load (in Amperes or Watts) that the circuit will serve. Use the expected average or typical load if the load varies.

Distance

Measure the one-way distance of the circuit run (from the source to the load).


Voltage

Note the voltage of the circuit (e.g., 120V, 240V, 480V).

Operating Hours

Estimate the number of hours per day/week/year the circuit will be operating under that load.


Step 2: Choose Conductor Sizes.
NEC Minimum

Determine the minimum conductor size required by the NEC for that load, distance, voltage, and installation conditions (e.g., conduit type, ambient temperature). Use NEC tables like 310.15(B)(16) (formerly 310.16) and consider voltage drop requirements (which might necessitate larger conductors even if ampacity doesn't). Don't forget to factor in derating for conduit fill and ambient temperature!


Upsized Conductor

Choose a larger conductor size to compare. Consider a one-size or two-size increase.

Step 3: Calculate Resistance for Each Conductor Size.
Using the formula `R = (ρ L) / A`, calculate the resistance for both the NEC minimum conductor size and the upsized conductor. Remember to double the one-way length (L) to account for the entire circuit. Be consistent with your units (meters vs. feet, square meters vs. circular mils). Step 4: Calculate Power Loss (Watts) for Each Conductor Size. Using the formula `P = I²R`, calculate the power loss in Watts for each conductor size. Use the load current (I) determined in Step 1 and the resistance (R) calculated in Step 3. Step 5: Calculate Energy Loss (kWh) per Year for Each Conductor Size. Energy Loss (kWh) = (Power Loss (Watts) Operating Hours per Year) / 1000 Calculate the annual energy loss in kilowatt-hours (kWh) for both the NEC minimum and the upsized conductor. Step 6: Calculate the Annual Cost Savings. Annual Cost Savings = (Energy Loss (kWh) with NEC Minimum Conductor - Energy Loss (kWh) with Upsized Conductor) Cost per kWh Multiply the difference in annual energy loss (in kWh) by the cost of electricity per kWh in your area. This will give you the annual cost savings from using the larger conductor. Step 7: Calculate Payback Period. Incremental Cost = Cost of Upsized Conductor - Cost of NEC Minimum Conductor (This is the extra you pay for the larger wire.) Include the increased labor costs of pulling larger wire. You may also need to increase the size of the conduit depending on how many current carrying conductors are in the conduit. Payback Period (Years) = Incremental Cost / Annual Cost Savings Divide the incremental cost by the annual cost savings to estimate the payback period in years.

Example (Simplified)

Let's say you have a 20 Amp load, running 100 feet (one-way) at 120V, operating 8 hours per day, 365 days per year. Electricity costs $0.15/kWh. We'll compare using #12 AWG (NEC minimum, assuming no voltage drop issues) versus #10 AWG.
1.


Load

20 Amps2.

Distance

100 feet (one-way) = 200 feet total circuit length3.

Voltage

120V4.

Operating Hours

8 hours/day
365 days/year = 2920 hours/year

#12 AWG (NEC Minimum)

Resistance (approximate): 200 ft 1.98 Ohms/1000 ft = 0.396 Ohms Power Loss: 20² 0.396 = 158.4 Watts Energy Loss: (158.4 Watts 2920 hours) / 1000 = 461.57 kWh/year Cost of Energy Loss: 461.57 kWh/year $0.15/kWh = $69.24/year

#10 AWG (Upsized)

Resistance (approximate): 200 ft 1.24 Ohms/1000 ft = 0.248 Ohms Power Loss: 20² 0.248 = 99.2 Watts Energy Loss: (99.2 Watts 2920 hours) / 1000 = 289.74 kWh/year Cost of Energy Loss: 289.74 kWh/year $0.15/kWh = $43.46/year

Savings

Annual Cost Savings: $69.24 - $43.46 = $25.78/yearLet's say the extra cost of #10 AWG over #12 AWG for this run, including labor, is $75.

Payback Period

$75 / $25.78/year = 2.91 years

Key Considerations and Caveats



Voltage Drop

The NEC specifies voltage drop limits. Even if the ampacity of a conductor is sufficient, voltage drop might necessitate a larger conductor. This is crucial, especially for long runs.

Conduit Fill

Larger conductors require larger conduit. Check NEC Chapter 9, Table 1, and relevant notes for conduit fill limitations. Increasing conduit size adds to the up-front cost.


Ambient Temperature & Derating

The NEC requires derating conductor ampacity based on ambient temperature and the number of current-carrying conductors in a conduit. These derating factors can significantly impact the required conductor size and should always be considered.

Load Profile

The more accurate your estimate of the load profile (how much current the circuit draws and for how long), the more accurate your savings calculation will be. Consider peak demand, average load, and duty cycles.


Future Load Growth

If you anticipate the load on the circuit increasing in the future, upsizing the conductor now might avoid costly upgrades later.

Harmonics

In circuits with significant harmonic distortion, the neutral conductor can carry a substantial amount of current. This can require a larger neutral conductor than the phase conductors.


Power Factor

Low power factor increases the current drawn by a load, which increases I²R losses. Power factor correction can reduce these losses.

Accuracy of Resistance Values

The resistance values used in the calculations should be as accurate as possible. Consult conductor manufacturers' data sheets for specific resistance values at different temperatures. Be aware that the values in NEC Chapter 9 tables are
approximate and are typically at 75°C. The resistance of copper increases with temperature.

Labor Costs

Installing larger conductors and larger conduit can increase labor costs. Be sure to factor these costs into your payback period calculation.

Inflation

Electricity prices tend to increase over time. Consider including a factor for inflation in your long-term savings calculations.

Tools & Resources



NEC (National Electrical Code)

The definitive source for electrical safety requirements.

Electrical Engineering Handbooks

These provide comprehensive information on conductor properties and calculations.


Online Calculators

Many websites offer online calculators for conductor ampacity, voltage drop, and energy savings. However, always verify the assumptions and calculations made by these tools. Some are better than others.

Conductor Manufacturers' Websites

These sites provide detailed specifications for their products.


Spreadsheet Software (Excel, Google Sheets)

Create a spreadsheet to automate the calculations and easily compare different scenarios.

In summary, calculating electrical use savings by increasing conductor size beyond NEC requirements involves determining the I²R losses for different conductor sizes and comparing the costs of those losses to the incremental cost of the larger conductor. A careful analysis of the load profile, operating conditions, and material costs is essential for an accurate assessment.