Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Load Calculation

User: mrcons, Location: Canada

Asked on: Friday, August 9, 2024 at 8:40 pm EDT
Answered on: Thursday, March 6, 2025 at 1:00 am EST

Question: Questions:1. Can we use the optional method load calculation if less 100A service conductor ampacity base on 220.82(A)?2. How do we know the service or feeder conductor with an ampacity of 100 or greater (220.82A)?3. Is it based on calculated value thru standard method or based on total load before the demand factors?

Okay, let's break down these questions regarding optional load calculations per NEC 220.82(A).1. Can we use the optional method load calculation if less 100A service conductor ampacity base on 220.82(A)? Yes, but it's nuanced. NEC 220.82(A) describes the general allowance for using an optional calculation method for dwelling units. The key point is that this section doesn't itself restrict the use of the optional method based on service ampacity. The restriction comes in elsewhere in Article 220, specifically in Section 220.84 220.84 - Optional Method — Additional Loads

This section does impose a condition related to service or feeder size if you're adding significant load to an existing dwelling unit. Specifically, 220.84(B) states that if, after adding the new load, the total load exceeds the ampacity of the existing service or feeder conductors, the load increase shall not exceed 220.84(C). This indirectly influences if you should use the optional calculation method, but it doesn't directly prohibit its use if your service is less than 100A.

Important Consideration

Just because the NEC
allows something doesn't mean it's practical or safe. A very small service (e.g., 60A) might be inadequate even if the calculated load under the optional method appears to be within the service's capacity. Local codes might have more restrictive rules. Safety should always be a primary concern and consider the potential for future load increases.

2. How do we know the service or feeder conductor with an ampacity of 100 or greater (220.82A)?
The ampacity of the conductors is determined by their size and insulation type, based on the applicable ampacity tables in Article 310. This is based on the conductors installed, not the calculated load. How to Determine Ampacity



Identify the conductor size and material (copper or aluminum/copper-clad aluminum).
Identify the insulation type (e.g., THHN, THWN, XHHW). Refer to the appropriate ampacity table in Article 310 (specifically, 310.16) based on the termination temperature rating of the equipment. The 75°C column is commonly used for most breakers and equipment rated over 100A, but always check the equipment markings for the specific temperature limitation. Equipment rated 100A or less will usually have a termination rating of 60 degrees. Read the ampacity value from the table. That value represents the maximum current the conductor can safely carry under the conditions specified in the table.3. Is it based on calculated value thru standard method or based on total load before the demand factors? The 100A threshold (related to 220.84, not 220.82 directly) refers to the ampacity of the existing service or feeder conductors, as described in question 2. This is entirely based on the conductor installed and the values from the ampacity tables in 310.16. It has nothing to do with calculated load by either the standard or optional method. The load calculations (whether standard or optional) are used to determine the minimum required ampacity for the service or feeder. You perform the load calculation to determine the amount of current the service or feeder needs to supply.

In summary

220.82(A) itself doesn't limit the optional method based on service ampacity. 220.84 does impose a consideration related to service/feeder size when adding significant load to an existing dwelling. The 100A reference (in the context of 220.84) refers to the ampacity of the conductors already installed, based on their size, insulation, and the applicable ampacity tables in Article 310. Load calculations (standard or optional) are separate processes to determine the required ampacity to serve the load. Always err on the side of caution. If the service or feeder seems undersized, even if a calculation suggests it's adequate, consider upgrading.

Example


Let's say you have an existing service using #4 AWG copper conductors with THHN insulation, and the equipment is rated for 75C terminations. Table 310.16 would show that #4 AWG THHN copper is rated for 85 amps. In this case, the "service conductor ampacity" is 85A, not* 100A or greater. Thus, the optional calculation is not applicable if you're adding a significant load (as described in 220.84). You would need to upgrade the service conductors if the new load requires a service greater than 85A.I hope this clarifies the use of the optional method and the related requirements. Always consult the latest edition of the NEC and local codes for the most accurate and up-to-date information. When in doubt, consult with a qualified electrical professional. Flag for review

Previous Question Next Question