Topic: Clarification on 680.26

User: augie47, Location: Tennessee

Asked on: Saturday, August 10, 2024 at 10:13 am EDT
Answered on: Thursday, March 6, 2025 at 1:00 am EST

Question: Often this ole boy has problems with Code languageTwo such examples are in the '23 Code on 680.26 .Clarification would be appreciated.680.26(B)(1)(f) in discussing the perimeter bond states "Be installed only in perimeter surfaces not intended to have access to the swimmers" ????and680.26(B)(2)(d) Discussing interconnection of bonded portions of perimeter surfaces states listed splicing devices must be incorporated.When the perimeter surface consists of rebar or mesh in the concrete is a listed device required to connect overlapping sections.

You're right, those sections of the 2023 NEC (NFPA 70) 680.26 can be tricky. Let's break them down

680.26(B)(1)(f) Perimeter Bonding - "Be installed only in perimeter surfaces not intended to have access to the swimmers"
The Issue

This seems counterintuitive at first. Why
not bond the surfaces swimmers touch?

The Reasoning

This section focuses on a specific type of perimeter bonding designed to equalize the potential between the pool water and surfaces around the pool. It's not about bonding everything swimmers might touch. The intention here is to prevent voltage gradients between the water and the surrounding earth/concrete.

Understanding "Perimeter Surfaces Not Intended to Have Access to Swimmers"

Think of this as referring to the
outer edges of the pool deck, or the soil/earth immediately adjacent to the pool's structure, or the surface of an attached spa when the two are separated by a raised bond beam that is intended to prevent access to the other. These are areas a swimmer wouldn't normally walk or stand. If swimmers were to stand on these areas, this creates a gradient between the pool water and earth.

In simpler terms

This rule basically states that you only need to worry about bonding the surrounding surface immediately adjacent to the pool.

680.26(B)(2)(d) Interconnection of Bonded Portions of Perimeter Surfaces - Listed Splicing Devices
The Issue

Does this mean every rebar overlap in the concrete needs a "listed splicing device"?


The Reasoning

This is where the Code is specific and often debated. The key is the phrase "interconnection of bonded portions." The intent of this section is to ensure solid, reliable electrical continuity between different sections of the conductive grid (rebar or mesh) embedded in the concrete.

When a Listed Device is Required



Purpose Built

Splice devices are required when overlapping sections of wire are run solely for the purpose of bonding, as opposed to structural reinforcement.

Concrete Pour Interruptions

If the concrete is poured in stages, creating a "cold joint" that can compromise electrical continuity between rebar sections, a listed device is mandatory.


Material Dissimilarity

If overlapping sections of wire are dissimilar, such as galvanized to copper, a listed splicing device rated to resist galvanic corrosion is required.

When a Listed Device is NOT Required



Continuous Pour with Adequate Overlap

In a single, continuous concrete pour, if the rebar or mesh has sufficient overlap and is securely tied together (as per standard construction practices for structural integrity), most inspectors will accept that as meeting the bonding requirement without the need for a separate listed splicing device. The key is that the overlap and tying must provide good electrical conductivity.

Structural Reinforcement

If overlapping sections of rebar are run solely as structural reinforcement, as opposed to bonding, these sections may be exempt from the code as it would be redundant to run separate sections of wire to achieve bonding.

Important Considerations and Why This is Tricky



AHJ (Authority Having Jurisdiction)

Local interpretations vary wildly. Always check with your local inspector before starting any work. They have the final say.

"Listed Splicing Device"

Ensure the device is specifically listed for grounding and bonding purposes. A standard mechanical rebar splice connector
may not be sufficient.

Documentation

Keep records of your bonding methods and materials. Photos before the concrete is poured are invaluable.

Testing

After completion, a qualified electrician should test the bonding system for continuity and resistance to ensure it meets code requirements.

In summary



680.26(B)(1)(f)

Bond the outer edges of the pool surface to prevent gradients.

680.26(B)(2)(d)

Generally, if you have a solid, continuous concrete pour with good rebar/mesh overlap and proper ties and that is used as a bonding system, you might be okay without a listed splicing device. However, if you're pouring in multiple stages, bonding dissimilar materials, or the rebar is specifically there for bonding (not structural), you almost certainly will* need listed splicing devices.

Always consult with your local electrical inspector and a qualified electrician to ensure your pool bonding meets all applicable codes and safety standards.
They can provide definitive answers based on your specific situation and local regulations. Flag for review

Previous Question Next Question