Question: Their is a bare wire in ac cable it helps to ground the cable , why and how does it work, why not in mc cable ?????????????????????????????????????

Let's break down the purpose of the bare ground wire in AC cable and why it differs from MC cable

Why is there a bare ground wire in AC cable (specifically, Type AC cable, aka BX cable)?
Safety: Fault Current Path

The primary reason for the bare ground wire (technically called the
equipment grounding conductor or EGC) is safety. It provides a low-impedance path back to the electrical panel. Here's how it works: If a hot wire (the black or red wire) accidentally comes into contact with the metal enclosure or other metal parts of an appliance or electrical box, a fault current (short circuit) occurs. The EGC provides a direct path for this large fault current to flow back to the panel's grounding system. This large current triggers the circuit breaker (or fuse) to trip (open), quickly shutting off the power to the circuit. This rapid shutoff is crucial to prevent:

Electrical shock

Without the EGC, the metal enclosure could become energized at a dangerous voltage, creating a shock hazard for anyone who touches it.

Fire

A sustained fault current can generate heat and start a fire.


Bonding

The EGC also bonds together all the metallic parts of the electrical system (metal boxes, conduit, appliance chassis, etc.). This ensures that everything is at the same electrical potential (close to zero volts relative to ground). This reduces the risk of touch voltage.

AC Cable Armor

With the older versions of AC cable (BX), the flexible metal armor itself was used as a grounding path. However, this proved unreliable over time due to corrosion, loose connections, and the relatively high impedance of the armor. The EGC was added to AC cable to provide a dedicated, low-impedance ground path, improving safety.

How does it work?
1. Continuous Path

The EGC is connected to the grounding bus bar in the electrical panel, which is ultimately connected to the grounding electrode system (ground rod or water pipe).2.

Low Impedance

The EGC is sized to have low electrical resistance (impedance). This allows a large fault current to flow easily.3.

Fault Detection

When a fault current flows through the EGC, it creates a voltage drop across the wire, which is detected by the circuit breaker/fuse.4.

Circuit Interruption

The breaker/fuse trips, cutting off the power to the circuit and eliminating the hazard.

Why not in MC cable (Metal-Clad Cable)?


MC cable
does have a grounding system. The outer metallic jacket of MC cable is designed to serve as the primary equipment grounding conductor.Here are the key differences: MC Cable Jacket as Ground

MC cable is constructed with an outer metallic jacket that is specifically designed and tested to provide a reliable, low-impedance ground path. The jacket is typically made of aluminum or steel.

Supplemental Ground Wire

Most modern MC cable also includes an
insulated green or bare grounding conductor inside the cable in addition to the metal jacket. This serves as a supplemental grounding path. This added wire provides an extra measure of safety and redundancy.

Interlocked Armor

The way the MC cable armor is interlocked and constructed allows for a good continuous electrical bond throughout the length of the cable.In short, MC cable relies primarily on its metal jacket for grounding, with a supplemental wire inside for additional safety. AC cable needs the dedicated bare ground wire because its armor is not designed to be the primary grounding path.

In Summary



AC Cable (BX)

Requires a dedicated
bare grounding conductor because its flexible metal conduit is not a reliable grounding path on its own. The grounding conductor must be properly terminated to the box.

MC Cable

The metal jacket is designed to be the primary grounding path. It typically includes a supplemental insulated or bare ground wire for additional safety. The jacket of MC cable is designed for the grounding path, so it is often used in commercial construction.

Important Note:
Electrical work can be dangerous. Always consult with a qualified and licensed electrician for any electrical installations or repairs. Incorrect wiring can lead to electrical shock, fire, or other hazards. Flag for review