Topic: 410.71 - disconnect requirements for 2-ended LED/fluorescent

User: Flicker Index, Location: Pac NW

Asked on: Saturday, August 10, 2024 at 2:23 pm EDT
Answered on: Thursday, March 6, 2025 at 1:01 am EST

Question: "For indoor locations at other than dwellings and associated accessory structures, fluorescent or LED luminaires that use double-ended lamps and are equipped with ballasts or LED drivers that can be serviced in place must have a disconnecting means either internal or external to each luminaire"a screw in light bulb or PL-C lamps are "single ended" and the common fluorescent lamps are double ended, as well as LED drop-ins. Now, when it comes to integral ballast LED lamps in tube shape but wired such that its powered using the two pins on one end, is it still "double ended"? If not, is this the reason one end feeding is a common?

Let's break this down: Double-Ended vs. Single-Ended

The critical distinction is how the lamp receives power.


Double-Ended

Receives power at both ends of the lamp. Each end has pins that connect to the ballast or driver circuitry. Traditional fluorescent tubes and many LED tubes designed as replacements fall into this category.

Single-Ended

Receives power
only from one end of the lamp. Examples are screw-in bulbs and PL-C lamps, which have all their electrical connections at the base.

The NEC Requirement

The quote you provided from the National Electrical Code (NEC) focuses on safety for maintenance. The disconnecting means (switch, pull chain, etc.) is required for luminaires with double-ended lamps and in-place serviceable ballasts/drivers to allow a worker to de-energize the fixture before working on it. This is because with power coming in at both ends, there's a greater potential shock hazard during servicing.

One-End Wired LED Tubes (Integral Ballast)

These LED tubes are designed to mimic the physical shape of a fluorescent tube, but they are fundamentally different electrically. Even though they have pins on both ends,
they are only powered from one end. The pins on the other end are typically just for mechanical support or alignment. They can be considered a single-ended lamp in a double-ended package.

Why One-End Wiring is Common


Simplified Wiring

One-end wiring simplifies the installation and reduces the number of connections required in the fixture.2.

Safety

As only one end has the AC connections, it is deemed to have less shock hazard.3.

Code Compliance

Because these one-end wired LED tubes effectively function as single-ended lamps, they are exempt from the NEC requirement for a disconnecting means at the luminaire if the ballast/driver isn't serviceable in place. If they are designed with a ballast/driver that can be serviced in place, a disconnecting means would still be required.

Regarding your last point
: One-end powering is not solely and exactly to allow them to be exempt from the NEC section stated. It's more correct to say the one-end powering allows such consideration on whether it can be exempt, by deeming the LED as single ended instead of double endedIn summary:

A one-end powered LED tube designed to replace a fluorescent tube, even though it might physically resemble a double-ended lamp, is considered single-ended
electrically. This single-ended design can exempt them from the requirement for a disconnecting means at the luminaire. However, if the LED tube's driver is* serviceable in place, a disconnecting means is still necessary regardless of it being considered single or double ended. Flag for review