Question: Hello,I have an apartment building that basically has small apartment next to each other (separated by a firewall) and a door that leads to an exterior walkway. The owner wants to put the panel behind the main door exterior wall. This isnt my first choice location, but i don't see a problem with it as long as the panel has a 3 feet clearance. Do you see a code issue having the panel on this wall? See attached picture . Thank you
Okay, let's break down the code considerations for locating your electrical panel on the exterior wall of an apartment building, based on the information you've provided and assuming you're in the United States and following the NEC (National Electrical Code).
Based on the NEC, the following factors are most relevant for the exterior location of the panel
Working Space (110.26)
This is your primary concern. You're correct in focusing on the 3-foot clearance.
Depth
You need at least 3 feet of clear working space in front of the panel. This distance is measured from the front of the enclosure. This distance can increase depending on voltage to ground and opposing conditions.
Width
The working space must be at least 30 inches wide or the width of the equipment, whichever is greater. The panel doesn't have to be centered in this 30-inch width, but it must be accessible within that width.
Height
The working space must extend from the floor or platform to a height of at least 6 1/2 feet (78 inches) or the height of the equipment, whichever is greater.
Clear and Unobstructed
The working space must be clear and unobstructed. This means no storage, equipment, or anything else blocking access. Note that doors are allowed to swing into this space.
Environment (110.11)
Because this panel will be outdoors, it needs to be rated for the environment.
NEMA Enclosure Type
You'll need an enclosure rated for outdoor use (NEMA 3R or higher is typical) to protect the panel from rain, snow, and other environmental factors. Check local amendments, as some jurisdictions may require specific NEMA ratings.
Physical Protection (110.27)
The panel needs to be protected from physical damage.
Location
Consider the likelihood of someone bumping into it with carts, equipment, or vehicles. If damage is likely, consider using bollards or other protective measures.
Vandalism
If vandalism is a concern, a more robust enclosure might be needed, or the panel might need to be located in a less exposed area.
Accessibility (230.70(A)(1))
The main service disconnect must be readily accessible. "Readily accessible" means capable of being reached quickly for operation, renewal, or inspections without climbing over or removing obstacles or resorting to portable ladders, etc. The location you describe, as long as it's not locked or obstructed, likely meets this requirement.
Identification (408.4(A))
Each circuit directory must be legibly and clearly labeled to indicate its purpose or use.
Potential Issues to Consider Based on Your Description
Exposure to Weather
While a NEMA 3R (or better) enclosure will protect from rain, consider the long-term effects of sun, temperature extremes, and humidity.
Vandalism/Tampering
Exterior panels are more vulnerable.
Aesthetics
The owner might have concerns about the appearance of the panel on the exterior wall.
Recommendations
Consult with the Local Authority Having Jurisdiction (AHJ)
The most important step is to discuss the proposed location with your local electrical inspector before proceeding. They have the final say on whether it meets local codes and are familiar with any local amendments to the NEC. They may have specific requirements or preferences for outdoor panel installations in your area.2.
Verify NEMA Rating
Make absolutely sure the enclosure you choose is appropriately rated for outdoor use in your specific climate.3.
Plan for Clear Working Space
Ensure the area in front of the panel will remain clear and unobstructed. Consider landscaping or other barriers to prevent storage in front of the panel.4.
Document Everything
Keep records of your discussions with the AHJ, the panel specifications, and the installation details.
In summary, putting the panel on the exterior wall is possible if you address the working space, environmental protection, physical protection, accessibility, and labeling requirements. However, careful planning, proper equipment selection, and communication with the AHJ are crucial for a safe and code-compliant installation.
I strongly advise discussing this with your local electrical inspector. They can provide the definitive answer based on the specific circumstances and local codes. Good luck! Flag for review