Question: I know what many do when coming into the top of a NEMA 3R enclosure: use a conduit hub like a "Myers" hub and screw conduit male adapters into it. So many installations do it. And I personally think it's a better seal than a rain tight EMT fitting screwed directly into the top of the enclosure. However, "myers" hubs (I know myers is just one brand) are only listed for use with RMC. There's very few say raintight EMT to RMC adapters that could be used with an RMC nipple to screw into a hub. What "proper" ways do people see being used here that they might be comfortable with?
You've hit on a common dilemma in the field. Using Myers hubs and EMT fittings directly into the top of a NEMA 3R enclosure seems like a robust solution, but as you've pointed out, it often bends the rules a bit. Here are a few "proper" alternatives, keeping in mind that "proper" means code-compliant and installation instruction-following
1. RMC to the Hub (Most Compliant, Least Convenient):
The Textbook Solution
Use RMC conduit from your source to the hub. This is what the hub is designed for. Use sealing locknuts on both sides of the enclosure wall. If you need to transition from EMT to RMC, do it before you get to the enclosure. Transition outside the enclosure using: A listed EMT to RMC coupling (these exist, though can be harder to find. Look for weatherproof options.) A junction box (NEMA 3R rated) with proper fittings for both EMT and RMC. This box acts as the transition point.
2. Using a Listed Rain Tight EMT Connector with Sealing Locknut
Direct Entry
Use a listed rain-tight EMT connector (the kind with the rubber gasket) directly into the top of the enclosure. Use a sealing locknut on the inside of the enclosure. The key here is to
follow the manufacturer's instructions for torqueing the connector and the locknut. Some inspectors are particular about seeing the sealing locknut used in conjunction with the rain tight connector. This is a widely accepted solution.3. Chase Nipples and a Coupling (Common But Potentially Problematic)
The "Nipple and Coupling Dance"
Use a short RMC nipple screwed into the hub with sealing locknuts. On the other end of the RMC nipple, use an RMC to EMT coupling (or a reducing coupling if needed) to connect to the EMT run.
Why it's potentially problematic
Coupling Rating
You need to ensure the RMC to EMT coupling is also rated for wet locations and properly sealed. Many standard couplings aren't.
Nipple Length
The nipple has to be long enough to provide adequate thread engagement in both the hub and the coupling.
Accessibility
Tightening the coupling inside the enclosure can be difficult.
4. Using a NEMA 3R Conduit Body (LB, LL, LR, or T)
Indirect Entry
Mount a NEMA 3R-rated conduit body (like an LB) to the top of the enclosure using a short nipple into the hub. Use EMT fittings into the conduit body to continue your run.
Advantages
Easier to pull wires, provides a degree of separation from the inside of the enclosure.
Disadvantages
More expensive, adds more components.
Important Considerations for ANY Solution
Manufacturer's Instructions
Always follow the manufacturer's instructions for the fittings, hubs, and enclosures. This is critical for maintaining the NEMA 3R rating.
Thread Sealant
Using a listed thread sealant appropriate for the fitting materials is good practice, especially in wet environments.
Enclosure Knockouts
Ensure the knockout size in the enclosure matches the hub/fitting size correctly. Using reducer washers defeats the purpose of the 3R rating.
Sealing Locknuts
A sealing locknut MUST be used in conjunction with the hub.
Torque
Adhere to specified torque settings. Under-tightening can compromise the seal; over-tightening can damage the fitting.
Local AHJ
The final authority is always your local Authority Having Jurisdiction (AHJ). Their interpretation of the code is what matters. Discuss your approach with them if you have any doubts.
Why The First Option Is Preferred
The first option - RMC straight into the hub - is the most compliant because it uses the hub as intended. The other solutions involve a degree of "jury-rigging" and relying on the ratings of multiple components to create a weatherproof seal.
In summary: While EMT directly into a 3R enclosure with a sealing locknut is a common and often accepted practice (if using a proper rain tight connector), the "textbook" solution of using RMC and a hub is the most reliable and code-compliant. If you're deviating from that, be sure to use listed components, follow manufacturer's instructions, and consult with your AHJ if necessary. Flag for review