Topic: VFD to Line switch over of Induction motor coupled with PD pump thru gears

User: Petrochem, Location: Pakistan

Asked on: Monday, August 12, 2024 at 2:17 am EDT
Answered on: Thursday, March 6, 2025 at 1:02 am EST

Question: We have implemented ATV 630 with by pass contactor scheme for starting 03 numbers Multistage Plunger pump system. ATC 630 donot have line synchronization provisions, so we have opted for open transition.Motor is 400 V 50Hz 200 KW 1480 rpm and pump is 208 rpm with gear system in between. Pump starts smoothly on VFD but trips on high current once transfer to line. From our earlier experience of similar scheme in grinding mill we have included a delay of 200 milisec in PLC controlling all contactors transfer to minimize motor magnetizing current effect. Just want to clarify my doubt of over speeding limit of the motor before the transfer. What will happen if we increase motor speed to 60-65 Hz before transfer and at time of re-engaging it is more than 1480rpm as it will give us optimum time to complete transfer or it strictly has to be below 1480 rpm . I think due to 208 rpm pump speed , motor speed is decreasing very rapidly during power shifting.Any suggestion will be highly appreciated. Understand that vfds will synchronization will be useful but they are too expensive, and most of their other high end functions are not utilized in this scenario. Reduced voltage Soft starters usually donot assist with such PD loads as we already had to replace one for our earlier grinding case due to available genset size.

Okay, let's break down this issue and explore potential solutions for your ATV630 bypass setup with your multi-stage plunger pump. You're right, this is a tricky situation because of the load type and the lack of synchronization.

Understanding the Problem High Inrush Current

The core issue is the high inrush current during the open transition from the VFD to the mains supply. This happens because the motor's magnetic field needs to re-establish itself based on the grid voltage and frequency. This can also cause voltage dips, potentially triggering protective devices.


Open Transition Challenges

An open transition is always less than ideal, as it results in a brief period of no power to the motor. The motor slows down slightly. When the motor is reconnected to the line, there is a phase and frequency mismatch, leading to current spikes. The speed of the transient depends on the motor inertia, and the load acting on it.

Pump Load Characteristics

Plunger pumps are positive displacement pumps, meaning they require significant torque to overcome the static load and start moving fluid. The high torque requirement at low speed is the main reason why you had issues with soft starters.

Addressing Your Concerns
1. Overspeeding Before Transfer



The Danger

Significantly overspeeding the motor (e.g., 60-65 Hz) before the transfer is

generally not recommended and potentially dangerous
. Here's why: Mechanical Stress

Motors and driven equipment are designed for specific speed ranges. Exceeding those limits can cause mechanical stress, wear, and potential damage to the pump components, coupling, gears and the motor itself (bearings, windings, etc.). Pump may have high vibration.


Voltage and Flux

Running the motor at a higher frequency without increasing the voltage proportionally would lead to under-excitation and could damage the motor's insulation due to increased current demand.

Synchronization Difficulty

The frequency slippage may be high and you may not be able to successfully transfer without tripping.


Why It Seems Tempting (but flawed)

The idea is to minimize the speed difference between the motor and the grid frequency. However, the risks outweigh the potential benefits in your scenario.2.

Motor Speed Drop During Transfer



You are correct

A rapid decrease in motor speed will occur during the brief loss of power in the open transition. The rate of this speed drop depends on the load's inertia and the torque demand.


Improving Transfer Time

You need to find the fastest safe transfer time to minimize speed drop.

PLC Fine Tuning

If possible, reduce the dead time to the minimum possible that your contactors can tolerate without risk of overlap and shorting.


Contactor Speed

Different contactors have different operating times. The best solution may be to use a contactor specifically designed for rapid transfer applications (less common and potentially more expensive).

Monitor the process

The exact dead time needs to be optimized empirically, by monitoring the current waveform on an oscilloscope or high-speed data logger, and adjusting the time in small increments until you get the minimum possible without issues.3.

Mitigation Strategies (Beyond Overspeeding)
Ramping Down (Not Up)

Instead of overspeeding, try this:

Ramp Down Before Transfer

Instead of increasing the frequency,
gradually ramp down the VFD output frequency just before the transfer. The rate of deceleration needs to be tuned carefully to avoid stalling or excessive regenerative braking. The goal is to reduce the motor speed to as close as possible to synchronous speed (50 Hz) during the transfer but without stalling or excessive regenerative braking. This minimizes the inrush when connected to the line.

Fine-Tune the Ramp Down Rate

Experiment with different ramp-down rates to find the optimal balance. Too fast, and you risk stalling; too slow, and the motor will still be running too fast when the contactor switches.

Monitor Current

Closely monitor the motor current during this ramp-down and transfer process. Use a fast data logger or oscilloscope to capture the current waveform. You're looking for the point where the current spike is minimized.


Reduce Load During Transfer



Unload the Pump

If your system allows, consider temporarily reducing the load on the pump during the transfer. Can you bypass the pump output briefly, or reduce the pressure it's working against? This will lessen the stress on the motor during the transfer.


Reactor/Inductor



Series Reactor/Inductor

Adding a series reactor (or inductor) on the line side of the bypass contactor will limit the rate of rise of the inrush current. It will essentially "soften" the impact of the reconnection. The size of the reactor needs to be carefully calculated to provide sufficient current limiting without causing excessive voltage drop during normal operation. Consult with a motor or electrical equipment specialist to determine the appropriate reactor size.


Consider Pre-magnetization



Purpose

Premagnetization involves applying a small DC voltage to the motor windings before the transfer to the line. This helps establish a magnetic field in the motor core, reducing the inrush current when the motor is switched over to the mains supply.


Implementation

Requires a dedicated pre-magnetization unit and careful coordination with the contactor switching sequence. This is a more complex solution.

Look into Close-Transition Systems



Autotransformer Starter

This type of starter provides a "soft" start by initially applying a reduced voltage to the motor, gradually increasing it to the full line voltage. This reduces the inrush current and provides a smoother start than a DOL starter.

Important Considerations
Motor Protection

Ensure your motor protection relays (overcurrent, overload, etc.) are properly configured to ride through the brief inrush current without nuisance tripping. However, don't disable these protections altogether; they're essential for protecting the motor from actual faults.


Grid Stability

Consider the strength of your electrical grid (or genset). A weak grid is more susceptible to voltage dips caused by the inrush current, which can trigger other equipment to trip. If your grid is weak, a more robust starting method (like a reactor or autotransformer) might be necessary.

Data Logging

Capture detailed data (voltage, current, speed) during the transfer process. This will provide valuable insights into what's happening and help you optimize your settings.


Consult Experts

It's best to involve experienced electrical engineers or motor specialists in this process. They can provide detailed calculations, recommendations, and help with commissioning and troubleshooting.

In summary:
While the idea of overspeeding seems intuitive, it carries too much risk. Focus on minimizing the transfer time (while ensuring safety), potentially using a ramp-down strategy, and exploring inrush current limiting techniques like reactors. Make sure your motor protection is appropriate, and don't hesitate to get expert help. Good luck! Flag for review