User: Jimmy7, Location: Boston, MA
Asked on: Monday, August 12, 2024 at 7:23 am EDT
Answered on: Thursday, March 6, 2025 at 1:02 am EST
Question: Hello,I have a customer who has geothermal equipment in his single family house. The house has a 400 amp service with two 200 amp panels side by side. The customer is concerned that when the geothermal equipment turns on the lights flicker, I’m guessing it’s the in-rush current. It appears that most of the geothermal equipment is in one of the 200 amp panels. As a result, the customer would like to remove and relocate any lighting circuit that is located in the panel where the geothermal is fed from to the other panel. This is an effort to stop the lights from flickering upon the start up of the geothermal system. Would this even work, or does the in-rush affect the entire 400 amp service? FYI - Prior to the geothermal install the entire house was fed from a 200 amp service.
You've got a good understanding of the issue. Let's break down whether relocating the lighting circuits will work and other factors to consider.
Will Relocating Lighting Circuits to the Other Panel Help?
Maybe, but it's not a guaranteed fix. Here's why: The Goal
The idea is to isolate the sensitive lighting circuits from the voltage sag caused by the geothermal system's inrush current. By moving the lights to a different panel, you're hoping to spread the load and minimize the voltage drop on that particular circuit.
Shared Neutral and Ground
Both panels share a common neutral and ground back at the main service entrance. While the current flow will be different in each panel, a voltage sag on the neutral can still affect circuits in both panels to some degree.
Magnitude of Inrush
If the inrush current is very large compared to the overall service capacity, even moving the lights might not completely eliminate the flicker. The sag could be occurring at the service entrance level, affecting the entire 400A service.
Panel Load Balance
Ideally, the load across both panels should be reasonably balanced. If one panel is heavily loaded (even without the geothermal running), moving more circuits to the already less-loaded panel might not be the best long-term solution.
In Conclusion: It's worth trying, but don't expect miracles. Moving the lighting circuits is a relatively simple and inexpensive thing to try. If it significantly reduces the flicker, great! But be prepared for the possibility that it won't be a complete solution.
Other Potential Solutions and Things to Investigate
Before doing any rewiring, definitely investigate the following:1.
Verify Proper Geothermal Installation
Correct Wiring
Make sure the geothermal system is wired according to the manufacturer's specifications and local codes. Undersized wiring can exacerbate voltage drop issues.
Proper Grounding
Verify that the grounding system is robust and meets code requirements. Improper grounding can contribute to voltage fluctuations.
Starting Capacitors
Geothermal systems often use starting capacitors to reduce inrush current. Confirm that these capacitors are functioning correctly. Have a qualified HVAC technician inspect the geothermal unit.2.
Check for Loose Connections
Loose connections anywhere in the electrical system (from the utility connection to the panel to the branch circuits) can create resistance and worsen voltage sag. Carefully inspect all connections for tightness and signs of corrosion. Use a thermal imager to detect hot spots (a sign of loose connections).3.
Voltage at the Service Entrance
With the geothermal system running, measure the voltage at the service entrance (where the utility connects to the meter). If the voltage is significantly low at this point, the problem might be with the utility supply. Contact the utility company to investigate.4.
Load Balancing
Load Calculation
Perform a thorough load calculation for the entire house to ensure that the 400A service is adequate. It's possible that the added geothermal load has pushed the service to its limit.
Load Balancing Between Panels
Check the current draw on each panel with the geothermal system running. If one panel is significantly more loaded than the other, consider moving some of the non-essential loads (e.g., electric water heater, electric dryer) to the other panel to achieve better balance.5.
Consider a Soft Starter
For the Geothermal System
A "soft starter" (also known as a reduced voltage starter) can significantly reduce the inrush current of the geothermal system's compressor. This is often the most effective solution for eliminating voltage sag. This is the preferred method and what I would recommend.6.
Dedicated Circuit for Lights (Less Likely to Help but Possible)
Run a new, dedicated circuit from the less loaded panel for lighting in the rooms most affected by the flicker. This further isolates those lights, but remember the shared neutral limitation.
Important Safety Considerations
Work within Your Qualifications
Only perform electrical work that you are qualified and licensed to do.
Turn Off Power
Always de-energize circuits before working on them. Use a voltage tester to verify that the circuit is dead.
Follow Codes
Adhere to all applicable electrical codes (NEC and local codes).
Steps to Take
Diagnose
Start with a thorough diagnosis. Measure voltages and currents, check connections, and perform load calculations.2.
Inspect the Geothermal System
Have a qualified HVAC technician inspect the geothermal unit for proper operation and wiring.3.
Try Moving Lighting Circuits
If the diagnosis doesn't reveal any major issues, try moving the lighting circuits to the other panel.4.
Consider a Soft Starter
If the flicker persists, strongly consider installing a soft starter for the geothermal system.5.
Consult an Electrician: If you're unsure about any of these steps, consult a licensed electrician.Good luck! Let me know if you have any other questions. Flag for review