Question: Hello!I have been tasked with converting an entire factory from a solidly grounded to high resistive grounded 480V system (HRG).We will be utilizing a Post Glover SmartPulse system and have already evaluated the existing distribution to be a 3P/3W with no L-N (277V) loads.My question concerns MOVs.Rockwell VFDs and Servo drives (PowerFlex 40, 525, 535, 700, 700S, 753, 755 and Kinetix 6000, 5700) instruction manuals for all of these drives state that if connected to an ungrounded system, the MOVs must all be disconnected. This is a considerable task since the production line has over a hundred devices, but we are scheduling and budgeting for it.Other than 480V VFD and servos - can anyone think of other 480V equipment which would have a sensitivity to HRG?
You're right to be thorough and plan for this. Disconnecting MOVs in VFDs and servo drives in an HRG system is crucial to prevent premature failure. Here's a breakdown of other 480V equipment that might have MOV sensitivities in an HRG system, and why
Equipment Likely to Have MOV Issues in an HRG System:
Surge Protective Devices (SPDs) / Transient Voltage Surge Suppressors (TVSSs)
This is the most obvious one, outside of the VFDs and servo drives you already know about. 480V SPDs are designed to clamp voltage to ground, just like the MOVs inside the VFDs. Connecting them to an HRG system can lead to MOV failure because of elevated phase to ground voltages.
Where to look
Distribution panels, sub-panels, motor control centers (MCCs), lighting panels, and potentially even built into some individual pieces of equipment.
Solution
Replace SPDs with models specifically designed for HRG systems or, in some cases, remove them entirely. Make sure any replacement SPDs are rated for the higher phase-to-ground voltage that can occur in an HRG system.
Solid-State Relays (SSRs)
Some SSRs, especially those with built-in overvoltage protection, might use MOVs or other voltage clamping devices.
Where to look
Control panels, temperature controllers, motor starters (sometimes used in place of mechanical contacts).
Solution
Check the SSR datasheets. If MOVs are present and they are connected from line to ground, they should be removed or the SSR replaced with one rated for HRG systems.
Electronic Power Supplies (EPS)
480VAC to 24VDC (or other low voltage DC) power supplies may have MOVs at their input stages.
Where to look
Control panels, PLCs, HMIs, and other control equipment.
Solution
Review EPS documentation for the presence of MOVs. Check if EPSs are rated for floating power networks (which are effectively what HRG systems are, since fault current is limited). If not rated, consider replacing the EPS with a suitable alternative.
Lighting Ballasts (Electronic Ballasts for Fluorescent, LED, HID)
Some electronic ballasts for 480V lighting systems may incorporate surge suppression components.
Where to look
Lighting fixtures throughout the factory.
Solution
Check the ballast specifications. If surge suppression is present and it's line-to-ground, either disconnect the MOVs (if accessible and safe) or replace the ballasts with HRG-compatible versions.
Older Equipment with Basic Surge Protection
Older equipment might have rudimentary surge protection implemented using MOVs directly across the line to ground. This is less common now, but worth investigating in older installations.
Where to look
Inside junction boxes, at the input terminals of older motors (less likely for 480V, but possible), and within older control panels.
Solution
Remove the MOVs.
Power Conditioners and UPS Units
Some power conditioners and Uninterruptible Power Supplies (UPS) that operate on 480V may include MOVs for surge protection.
Where to look
Electrical rooms, server rooms, or locations where critical equipment is powered.
Solution
Inspect the unit's documentation or contact the manufacturer to determine if MOVs are present and if they need to be disconnected for an HRG system.
Why MOVs Cause Problems in HRG Systems
Elevated Phase-to-Ground Voltage
In a solidly grounded system, the phase-to-ground voltage is relatively stable. In an HRG system, during a ground fault, the unfaulted phases can see a voltage rise to near the phase-to-phase voltage (480V in your case). This higher voltage can exceed the MOV's voltage rating, causing it to conduct continuously and eventually fail (often short-circuiting).2.
Continuous Leakage Current
Even without a fault, the line-to-ground capacitance to ground will be constantly charging and discharging through the MOV, reducing its service life.
Important Considerations
Documentation, Documentation, Documentation
Meticulously document every piece of equipment you inspect, what you find (MOV presence, part numbers, ratings), and the actions you take (MOV removal, component replacement). This is crucial for future troubleshooting and maintenance.
Manufacturer Consultation
When in doubt, contact the equipment manufacturer directly. They can provide specific guidance on HRG compatibility and any necessary modifications.
Personnel Safety
Disconnecting or replacing components requires proper electrical safety procedures. De-energize circuits, use appropriate PPE, and follow lockout/tagout procedures.
System Grounding Resistor Monitoring
Ensure your Post Glover SmartPulse system is properly configured and monitored. It should alarm on ground faults and provide information to help locate the fault quickly. This minimizes the time that equipment is subjected to elevated phase-to-ground voltages.*
Training: Train maintenance personnel on the differences between solidly grounded and HRG systems, the implications for equipment, and proper troubleshooting procedures.By being proactive and considering these factors, you can minimize the risk of equipment failures and ensure a smooth transition to your HRG system. Good luck! Flag for review