Topic: Single phase load 120 / 208V power question

User: cppoly, Location: New York

Asked on: Monday, August 12, 2024 at 9:49 am EDT
Answered on: Thursday, March 6, 2025 at 1:03 am EST

Question: A 60/60/2 fused disconnect serves a UPS which has and 208V/120V, 1 phase, 3 wire output.The UPS serves three separate 120V, 12A loads.Is the total power consumed at the UPS: 120V x 12A = 1,440 VA x 3 = 4,320 VA?Is the amps seen at the line side of the UPS 4,320 / 208V = 20.7 amps?

Yes, your calculations are correct. Let's break it down: Individual Load Power

120V
12A = 1440 VA

Total Load Power

1440 VA
3 loads = 4320 VA

Line Side Current

4320 VA / 208V = 20.77 ampsTherefore:


The total power consumed at the UPS is 4,320 VA.
* The current seen at the line side (208V input) of the UPS is approximately 20.7 amps.

Given that a 60/60/60 fused disconnect can handle more amperage then the total load of 20.77 amps, the disconnect is adequately sized. Flag for review