User: Timona, Location: Houston, Texas
Asked on: Monday, August 12, 2024 at 12:03 pm EDT
Answered on: Thursday, March 6, 2025 at 1:03 am EST
Question: I am doing total load calculation of a building in Excel.I am using the numbers from the panel schedules.Now, what should I be using from the panel schedules? The demand load or the connected load?
You should be using the Demand Load from the panel schedules for your total building load calculation. Here's why: Connected Load
This is the sum of the nameplate ratings of all the equipment connected to the panel. It represents the maximum possible load if everything operated at its rated capacity simultaneously. This is highly unlikely and doesn't reflect real-world usage.
Demand Load
This is the load after applying demand factors to account for the fact that not all equipment will be operating at its full capacity at the same time. It's a more realistic estimate of the actual load the panel (and the building as a whole) will experience.
Why Demand Load is Crucial
Accurate Sizing
Using the connected load will lead to oversizing your electrical service equipment (transformers, switchgear, conductors, etc.), which is wasteful and expensive.
Code Compliance
Electrical codes (like the NEC in the US) require the use of demand factors when calculating the total load.
Realistic Assessment
Demand load provides a more accurate representation of the actual power consumption, which is important for energy management and cost analysis.
How to Use Demand Load
Collect Panel Schedules
Gather all panel schedules for the building.2.
Identify Demand Load
Locate the demand load (also sometimes called "calculated load" or "estimated load") for each panel.3.
Sum Demand Loads
Add the demand loads of all the panels together.4.
Apply Diversity Factor (if applicable)
In some cases, you might need to apply a diversity factor to the sum of the panel demand loads. A diversity factor accounts for the fact that the peak loads of different panels may not occur simultaneously. This is less common but may be applicable for very large buildings or specific types of occupancies. Consult with an electrical engineer or relevant codes for guidance on using diversity factors.
Important Considerations
Code Requirements
Always adhere to the local and national electrical codes (e.g., NEC, IEC) for load calculation procedures and demand factors.
Specific Equipment
Certain equipment types (e.g., HVAC, motors) may require specific demand factors or load calculation methods as defined in the code.
Panel Schedule Accuracy
Ensure that the panel schedules are accurate and up-to-date. Inaccurate panel schedules will lead to inaccurate load calculations.*
Professional Advice
For complex projects or critical applications, it's always recommended to consult with a qualified electrical engineer.
In summary, use the Demand Load from the panel schedules as the basis for your total building load calculation. This will result in a more accurate, cost-effective, and code-compliant design. Flag for review