User: DSrader, Location: Hutchinson, KS
Asked on: Monday, August 12, 2024 at 1:03 pm EDT
Answered on: Thursday, March 6, 2025 at 1:03 am EST
Question: I have an RTU rated for 208 V 3 phase being fed 240 V 3 phase with 2 compressors, both are showing unbalanced current draw. One is reading 30-31 amps on L1 and L3, 41 amps on L2, the other is 51 amps on L1 and L3, 71 amps on L2. My first thought was motor windings, but highly unlikely that both would have the same problem. I've never had issues this severe before, and I know there would be no wild leg on a Y wound transformer, which I think is common for 208V, but even on a delta wound transformer I've never seen where a wild leg causes current unbalance. The voltage reads 241V to 243V across on all 3 legs. Is there something I'm missing here?One more thing, this Mfr. makes distinct units for either 208V or 240V, not both.
Okay, this is a tricky situation. You're right to be concerned about the significant current unbalance, especially with both compressors showing the same pattern. Let's break down the potential causes and how to approach troubleshooting
1. Overvoltage and Underrated Motor Concerns:
Critical Issue
Your primary concern is the motor voltage rating. Running a 208V motor continuously on 240V can and WILL cause damage, potentially shortening its lifespan significantly.
Heat Generation
Overvoltage causes increased core losses in the motor, leading to overheating. This is a major stressor on the windings.
Winding Stress
The higher voltage can stress the insulation of the motor windings, leading to premature failure.
2. Potential Causes and Considerations
Overvoltage
Even though it's the most obvious, confirm that the 240V is consistently stable. Check during peak load times (like when both compressors are running) to ensure the voltage isn't spiking even higher. Measure voltage
at the RTU disconnect and at the compressor terminals themselves to rule out voltage drop within the unit. Compensating Motor Starters
Check for the presence of any compensating motor starters (auto-transformers or reactors). If installed, confirm they are set for the correct voltage tap (208V).
Capacitors in the Circuit
Some RTUs have power factor correction capacitors. Check their health. A failing or incorrectly sized capacitor on one phase could cause current imbalance.
CAUTION: DISCHARGE CAPACITORS BEFORE WORKING ON THEM! Transformer Issues
You're probably right about no wild leg on a Y-wound transformer, but it's worth verifying the transformer feeding the RTU is indeed a standard 208V or 240V source. Check the transformer nameplate for its voltage configuration and kVA rating. Ensure it's adequately sized for the RTU and any other loads it serves.
Verify transformer tap settings. Some transformers have adjustable taps to compensate for voltage variations. Ensure the taps are set correctly for the incoming voltage. Internal Unit Wiring
Inspect the wiring within the RTU itself. Look for loose connections, damaged insulation, or signs of overheating.
Refrigerant Issues
Although less likely to cause this specific pattern of current unbalance, refrigerant issues can put strain on the compressors. Check refrigerant charge levels and operating pressures. A restriction in the refrigerant circuit could cause one compressor to work harder.
Compressor Mechanical Problems
Again, less likely to be identical across two compressors, but consider the possibility. Check for signs of bearing wear, valve problems, or other mechanical issues.
Wiring
Check wiring for tightness, damage, and proper gauge.
3. Troubleshooting Steps
Immediate Action: Mitigate Overvoltage
The priority is to protect the compressors. If possible, address the overvoltage. This might involve adjusting transformer taps (if available) or consulting with the power company to address voltage issues on their side.
DO NOT continue to run the units with this significant overvoltage for extended periods. You're risking permanent damage.2. Voltage Measurements
As mentioned above, take very accurate voltage measurements at the RTU disconnect, at the compressor terminals, and at the transformer supplying the unit. Record these measurements under load.3.
Current Measurements
Use a high-quality clamp meter. Double-check your current readings. Even a slight inaccuracy can throw off your analysis. Record currents on each phase for both compressors simultaneously, if possible.4.
Capacitor Testing
If the RTU has capacitors, isolate them (with power off and capacitors discharged!) and test their capacitance and ESR (Equivalent Series Resistance) with a capacitor meter. Replace any that are out of spec.5.
Motor Winding Testing (with caution)
As a last resort, you could perform a motor winding resistance test with a megohmmeter to check for shorts. However, given the overvoltage situation, this is risky. It might reveal existing damage but also could further stress already compromised insulation.
Weigh the risks carefully before proceeding.6. Contact the Manufacturer
Given that the manufacturer makes distinct units for 208V and 240V, contact their technical support. Explain the situation in detail. They may have seen similar issues before and can provide specific guidance.
Important Considerations
Safety First
Work on electrical equipment only if you are qualified and understand the safety procedures. Disconnect power before working on any components.
Documentation
Carefully document all your measurements and observations. This will be invaluable for troubleshooting and for communicating with the manufacturer or other experts.*
Professional Help
If you are not comfortable with any of these troubleshooting steps, consult a qualified electrician or HVAC technician experienced with commercial equipment.
Why the Unbalance Pattern?
The consistent unbalance pattern (L2 higher than L1 and L3) is unusual. The consistent pattern makes me more suspicious of capacitors, internal unit wiring issues, or some type of control device that is wired incorrectly or has failed than the compressors themselves. While the overvoltage exacerbates the situation and is a serious problem, it should effect all three legs, not just one.Good luck with the troubleshooting! Addressing the overvoltage is paramount, then carefully working through the other potential causes will hopefully lead you to the root of the problem. Flag for review