Topic: Power Dips and Surges!

User: Coachmike, Location: Morris County, NJ

Asked on: Monday, August 12, 2024 at 2:03 pm EDT
Answered on: Thursday, March 6, 2025 at 1:04 am EST

Question: Card dealership is experiencing an intermittent power dip on the B phase of a 3 phase 480 volt 800 amp service. This phase loss is causing an HVAC unit's VFD to trip and show an overvoltage fault. Of course, the utility is saying it is not their issue and neighbors do not have the problem. Any insight is appreciated. TIA

Okay, let's troubleshoot this intermittent B-phase power dip causing your HVAC VFD to trip. This is a frustrating situation, but here's a structured approach to diagnosing and potentially resolving the issue

1. Verify & Document the Problem:
Precise Data Logging

You
must capture the voltage dip on the B-phase when the VFD trips. A simple voltmeter won't cut it. Use a data logging meter or power quality analyzer that can record voltage, current, frequency, harmonics, and potentially transient events over time (at least a week). Set the logging interval to something reasonably short (e.g., 1 second or less) to catch transient dips. Record all three phases.

VFD Trip Log

Carefully examine the VFD's trip log. Note the exact error code, the time of the trip, and any pre-fault values the VFD provides (voltage, current, frequency, DC bus voltage). This is crucial for understanding the nature of the fault.

Correlation

The key is correlating the recorded voltage dip (specifically on the B-phase) with the VFD trip event. The logs need to match up in time.


Document Everything

Keep a detailed log of dates, times, events, readings, actions taken, and communications with the utility.

Photograph Evidence

If possible, capture screenshots or photos of the data logging meter or power quality analyzer readings
during the dip and VFD trip.

2. Detailed On-Site Investigation (Electrical System)



Internal Load Audit

Conduct a load audit within the dealership. Note the types of equipment operating and their potential impact on the electrical system. Pay special attention to:

Large motors

Air compressors, car lifts, welders, paint booth equipment, etc. These can cause voltage dips during startup. Are any of these operating coincidentally with the VFD trips?


Lighting

Especially if you have a large amount of fluorescent or LED lighting. Poorly designed or maintained lighting ballasts can inject harmonics into the system.

Other HVAC equipment

Multiple HVAC units cycling on/off simultaneously can stress the system.


EV Chargers

A dealership is likely to have these. Load balance is important.

Connection Integrity

Check every connection in the B-phase circuit, from the service entrance to the VFD:


Service Entrance

Inspect the main disconnect for any signs of corrosion, looseness, or overheating on the B-phase lugs and conductors. Thermographic (infrared) scanning can be invaluable here.

Metering

Verify the utility's metering equipment is properly connected and functioning.


Distribution Panels

Check all connections in the main distribution panel and any sub-panels feeding the HVAC unit. Look for signs of loose connections (discoloration, burning, melting). Torque all connections to the manufacturer's specifications.

Wiring

Inspect the wiring from the distribution panel to the VFD. Look for damaged insulation, pinched wires, or improper terminations.


Grounding

Verify the integrity of the grounding system. A poor ground can exacerbate voltage fluctuations. Check ground connections at the service entrance, distribution panels, and the VFD. Use a ground resistance meter to verify a low ground resistance.

Neutral

Verify the neutral conductor is properly sized and connected. An undersized neutral can cause voltage imbalances.


Transformer Inspection

If you have a step-down transformer feeding the HVAC unit or the entire building, inspect it carefully:

Voltage Ratios

Verify the transformer's primary and secondary voltages are correct and balanced.


Load Balance

Check the current on each phase of the transformer. Significant imbalances can indicate a problem.

Temperature

Use an infrared thermometer to check the transformer's temperature. Overheating can indicate overload or a winding fault.


Noise

Listen for unusual buzzing or humming sounds from the transformer, which could indicate a problem.

Capacitor Bank

Check the capacitor bank for issues. Any bulges or leaking on the capacitors.


Conductor Sizing

Verify that all conductors are properly sized for the load they are carrying. Undersized conductors can cause voltage drop.

Harmonic Analysis

Use a power quality analyzer to measure harmonic distortion in the system. Excessive harmonics can cause voltage fluctuations and VFD trips.


Neutral-to-Ground Voltage

Measure the voltage between neutral and ground at various points in the system. Excessive voltage can indicate a grounding problem.

Surge Protection

Evaluate your surge protection. Poor or missing surge protection can allow voltage spikes to damage equipment or cause nuisance trips.

3. Possible Internal Causes (Dealership)



Specific Equipment Interaction

Could a specific piece of equipment cycling on/off be causing the dip? Try to identify any correlations. This could be another large motor starting, a welding machine being used, or even a high-demand appliance.

Power Factor Correction

Does the facility have power factor correction capacitors? If so, check their condition and operation. A failing capacitor can cause voltage instability.


Load Imbalance

A significant load imbalance across the three phases can cause voltage drops, especially on the most heavily loaded phase.

4. VFD-Specific Checks



VFD Settings

Review the VFD's parameters. Are the voltage settings correct? Is the overvoltage trip point set appropriately? Is the VFD's input voltage tolerance within the expected range of the incoming power?


Input Reactors/Chokes

Some VFDs have input reactors or chokes to reduce harmonics and protect the VFD. Ensure these are properly sized and connected.

DC Bus Capacitors

Check the DC bus capacitors in the VFD. Failing capacitors can cause overvoltage faults.


VFD Firmware

Check if there are any firmware updates available for the VFD. Sometimes updates address voltage sensitivity issues.

Isolate the VFD

Temporarily (for testing purposes only) connect the VFD to a temporary, isolated power source (generator or UPS) to see if the problem persists. If the problem disappears, it confirms that the issue is with the main electrical system.

Important: Ensure proper grounding and isolation procedures are followed when using a temporary power source.
5. Utility Interaction (Continued)



Escalate

If the problem persists and you suspect the utility, escalate the issue. Talk to a supervisor or engineer at the utility. Politely but firmly present your documented evidence.

Demand a Power Quality Investigation

Request that the utility conduct a power quality investigation at the service entrance to your building and at the transformer feeding your building. They have specialized equipment to detect voltage sags, swells, and other power quality issues.


Transformer Tap Settings

Ask the utility to check the tap settings on their transformer feeding your building. Incorrect tap settings can result in voltage fluctuations.

Neighbor Comparison

Gather more data from your neighbors. Even if they aren't experiencing the same VFD trips, ask them to monitor their voltage (especially during the times your VFD trips). If they are also seeing voltage dips, it strengthens your case with the utility.

6. Diagnostic Steps



Isolate the HVAC Unit

If possible, temporarily disconnect the HVAC unit (and its VFD) from the main electrical system. Monitor the B-phase voltage without the HVAC load. If the voltage dips disappear, it strongly suggests the problem is related to the HVAC unit or its VFD.

Turn Off Suspect Equipment

Systematically turn off potentially problematic equipment (large motors, welders, etc.) one at a time and monitor the B-phase voltage. If the voltage dips stop when a particular piece of equipment is turned off, you've identified a likely culprit.


B Phase Load Swap

As an extreme test, swap the B Phase and C Phase at the Main Disconnect. Monitor if the issue follows the B Phase or stays with the existing connection.

Neutral Monitoring

Attach a meter to the neutral bar in the main panel and monitor for voltage fluctuations. This can indicate grounding problems.

Important Considerations



Safety First

Work on electrical systems only if you are qualified and have the necessary safety training and equipment. When in doubt, hire a qualified electrician.

Documentation

Keep meticulous records of all readings, tests, and actions taken.


Professional Help

If you're unable to resolve the issue yourself, consult with a qualified electrical engineer or a power quality expert. They have the expertise and equipment to diagnose complex power problems.*

VFD Manufacturer:
Contact the VFD manufacturer for troubleshooting advice specific to their product. They may have seen similar issues before and can provide guidance.By systematically following these steps, you should be able to identify the source of the intermittent voltage dip and take appropriate corrective action. Good luck! Flag for review